Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: *Commercial Lease Space Grounding*

User: Jdoyle, Location: Sugar Land

Asked on: Tuesday, September 17, 2024 at 3:00 pm EDT
Answered on: Thursday, March 6, 2025 at 2:34 am EST

Question: We have a lease space, with a 10ft gutter with tap box. When the shell was built, the concrete encased electrode and ground rod were connected to a grounding busbar in the tap box. Now we have multiple tenants installing their services, and the utility provider wont let them connect their grounds for each service to the grounding busbar in the tap box. We are not getting clarification from the utility provider as to why, and we are looking for answers as to where each service should be pulling their service grounding conductors from.

This is a common, and sometimes frustrating, situation in multi-tenant buildings. Let's break down the likely reasons for the utility's refusal and possible solutions.

Understanding the Issue: Why the Utility Might Say No

The utility's objection likely stems from a combination of factors related to grounding and bonding practices, and the potential for creating unwanted circulating currents: NEC Article 250.24(A)(5)

This section covers the connection of the neutral conductor to the grounding electrode system at the service equipment. The main point is that the grounded (neutral) conductor is only connected to the grounding electrode system
at the service disconnect.



Single Point Grounding

Utilities often prefer (and sometimes require) a single, effective ground point for their service. Multiple connections to the same grounding electrode system, especially if those connections are not done properly, can create ground loops. These loops can introduce noise, create voltage imbalances, and potentially compromise safety.

Impedance Concerns

Long runs of grounding electrode conductors (GECs) can have significant impedance at higher frequencies. Multiple tenants connecting to the same GEC can exacerbate this issue, potentially impacting the effectiveness of the grounding system during fault conditions.


Load Diversity

In a multi-tenant building, the loads are diverse and change frequently. The utility wants to ensure the grounding system remains reliable regardless of the tenant loads.

Liability

The utility doesn't want to be held responsible for the grounding practices inside your building. By dictating the single-point ground, they maintain control over the primary connection.


Local Utility Rules

Utility requirements often go beyond the NEC and are specific to the local power company. This is why getting clarification from them is crucial, even if difficult.

Building Steel

Building steel is often used as the grounding electrode. Connecting directly to the steel, may be required or prohibited by local utility.

Possible Solutions (In Order of Preference - Best to Worst)1.

Get Clarification from the Utility - Persistently and in Writing! This is the
most important step. Don't give up. Request a meeting with a utility engineer or inspector. Ask these specific questions, and document their answers in writing (email is acceptable): "Can you explain in detail why we cannot connect the Service Grounding Conductors (SGCs) for each tenant's service to the existing grounding busbar in the tap box?" "What grounding method do you require for each tenant's service? Be specific. Do we need to install new concrete-encased electrodes for each tenant?" "Will a single, properly sized Grounding Electrode Conductor (GEC) from the tap box to the building steel, with each tenant connecting their Service Grounding Conductor (SGC) to that GEC, be acceptable?" (This is a common compromise – see option 3). "Can you provide us with a diagram or written specifications outlining your grounding requirements for multi-tenant services?" "Are there any specific utility standards or regulations that dictate the grounding method in this situation?" "Can you clarify what type of grounding electrode the utility requires/suggests in this scenario?"Without this clear guidance, you're guessing. You need to understand their reasoning to design a compliant and safe system.2.

Dedicated Grounding Electrode for Each Tenant (Ideal, but Expensive)



Description

The most robust solution is for each tenant to have their own, dedicated grounding electrode system (typically a concrete-encased electrode and/or ground rods).

Installation

Each tenant's service would have a GEC running to
their own grounding electrode(s).

Advantages

Provides the most isolation between tenant systems, minimizing the potential for ground loops and circulating currents. Highest level of safety.

Disadvantages

Most expensive and labor-intensive solution. May require significant excavation and concrete work. May not be practical depending on site conditions.3.

Shared Grounding Electrode Conductor with Tap Box Connections (Possible Compromise)



Description

Run a single, properly sized Grounding Electrode Conductor (GEC) from the existing grounding busbar in the tap box to a supplemental grounding electrode (likely building steel or additional ground rods). Then, each tenant connects their Service Grounding Conductor (SGC) to that single, larger GEC near their service disconnect. Essentially, you're creating a very short, shared grounding path.

Installation

A main GEC is connected to the existing electrode, and then a properly sized GEC is tapped to that original conductor for each service.


Advantages

Reduces the likelihood of circulating currents. Simpler than individual electrodes. Still provides a reliable path to ground for each service.

Disadvantages

Requires careful sizing of the common GEC to handle the combined fault current of all services. Requires meticulous installation to ensure solid, low-impedance connections. May not be acceptable to the utility in all cases. Requires very close coordination with the electrical engineer.4.

Supplemental Grounding Electrode System



Description

Install one or more additional grounding electrodes (rods, plates, or concrete-encased electrode) and connect them to the existing grounding electrode system. This can reduce the overall impedance of the grounding system and improve its effectiveness.

Installation

Drive additional ground rods in accessible areas and connect them to the existing grounding electrode conductor.


Advantages

Relatively simple to install. Enhances the overall grounding system.

Disadvantages

May not be sufficient if the existing grounding electrode system is inadequate.5.

Bonding to Building Steel (Check Utility and Local Codes)



Description

If the building steel is reliably grounded (and the utility allows it), you might be able to use it as the primary grounding electrode. Bond the grounding busbar in the tap box directly to the building steel.

Installation

Use heavy-duty bonding jumpers to connect the grounding busbar to a structural steel member.


Advantages

Often a readily available and effective grounding electrode.

Disadvantages

Depends on the building construction. Requires verification that the steel is adequately grounded. Can be difficult to access suitable bonding points.


IMPORTANT

The building steel must be verified as being part of a properly engineered grounding system, not just assumed.

Important Considerations

NEC Compliance

All grounding and bonding must comply with the latest edition of the National Electrical Code (NEC) and any applicable local amendments.


Licensed Electrical Engineer

You must involve a qualified and licensed electrical engineer to design the grounding system. They can perform calculations, ensure compliance, and provide stamped drawings for permitting.

Permitting and Inspections

Obtain all necessary permits and inspections from your local electrical authority.


Service Size

The size of the Service Grounding Conductor (SGC) and Grounding Electrode Conductor (GEC) depends on the size of the service entrance conductors. Consult the NEC tables for proper sizing (NEC 250.66, 250.122).

Connections

Use only approved grounding and bonding connectors. Ensure all connections are clean, tight, and corrosion-resistant.


Documentation

Keep detailed records of all grounding and bonding work, including drawings, calculations, and inspection reports.

Coordination

Coordinate all grounding and bonding work with the utility, the electrical contractor, and the building owner.

In summary, you must obtain clear guidance from the utility regarding their specific grounding requirements for your situation. Armed with that information, engage a qualified electrical engineer to design a compliant and safe grounding system for your multi-tenant building.
* Flag for review

Previous Question Next Question