Question: Two large AHU units are being replaced, moving from a single fan unit to quad fans. Two VFDs will control two each of the four fans, each fan having a disconnect at the unit. VFDs are being provided by HVAC contractor, I don’t have any specs yet. I am assuming that the two fans controlled by a single VFD will be controlled identically? I’ve never seen it set up this way. If that is the case, would it be acceptable to run both feeders from the VFD in the same pipe and then split before the disconnects at the fans? I assume if they are controlled seperately then they should be run separate as well, due to the frequency differences?
Okay, let's break down the situation and address your concerns. This is a common setup for larger AHUs and provides redundancy and turndown capabilities.
Understanding the Setup Quad Fans
Four fans provide flexibility. At low loads, only one or two fans might run. At peak load, all four are used. This increases efficiency over a single large fan that runs inefficiently at low speeds.
Two VFDs
Each VFD controls two fans. This allows for some staged control and redundancy. If one VFD fails, the other can keep at least some airflow going.
Identical Control (Assumption)
You are correct in questioning this assumption. While it's likely the two fans connected to each VFD will run identically most of the time, it's CRUCIAL to confirm this with the HVAC contractor and review the control sequence. There could be scenarios where they are slightly offset for balancing or vibration management. Even more unlikely, but the VFD could handle separate current limits for the fans.
Acceptability of Running Feeders in the Same Conduit
This is the core question, and the answer depends on the control scheme and electrical code (NEC). Here's a detailed breakdown: If the fans connected to a single VFD are ALWAYS intended to operate identically
NEC Perspective
Yes, it is generally acceptable to run the conductors for both fans controlled by the same VFD in a single conduit. Since the current, voltage, and frequency will be identical at all times for both conductors, it's not a parallel conductor configuration (which would have more stringent rules) and the rules for harmonic currents still apply. Remember to size the conduit appropriately for the total conductor fill and heat dissipation.
Practical Considerations
This simplifies wiring and reduces material costs. Make sure the conductors are sized for the combined load of both fans connected to that VFD, plus any applicable overcurrent protection requirements (see NEC article 430).
If there's ANY POSSIBILITY of the fans connected to a single VFD operating DIFFERENTLY (even slightly)
NEC Perspective
This becomes much more complicated. If the drives can be controlled to run separate frequencies, this is not acceptable, and if they are connected in parallel, the drives must have special features and comply with NEC 310.10(H) rules. Also consider NEC article 300.3(B) regarding parallel runs of conductors. You would be running unbalanced or parallel loads in the same conduit. This will cause an imbalance of inductive reactance across the conductors, and may not be acceptable. This can create significant inductive heating and other problems.
Practical Considerations
Running them separately ensures that the cable and conduit are sized appropriately for each motor and that you do not cause a condition of parallel or imbalanced operation.
Harmonic Currents and Shielded Cables
VFDs generate harmonic currents that can interfere with other equipment and cause overheating in conductors and transformers.
Shielded Cables
It's almost universally recommended to use shielded VFD cables. These cables contain a ground/bonding conductor and a shield that helps contain the electromagnetic interference (EMI) and radio frequency interference (RFI) generated by the VFD.
Grounding
Proper grounding is essential. Follow the VFD manufacturer's instructions for grounding the cable shield. Typically, it's grounded at the VFD end only.
Recommendations1. CLARIFY CONTROL SCHEME
This is the most important step. Get a detailed control sequence from the HVAC contractor and the VFD manufacturer's documentation. Ask specifically: "Will the two fans connected to each VFD always run at the exact same speed and load?" "Is there any possibility of slight speed adjustments or current limiting to one fan independently of the other?" "What happens if one fan connected to a VFD fails mechanically?"2.
SPECIFY SHIELDED VFD CABLES
Make this a requirement in your specifications. This is critical for reducing interference and ensuring reliable operation.3.
SIZING
Size conductors, conduit, and overcurrent protection based on the combined full-load amps (FLA) of both fans connected to each VFD (if running in the same conduit). If not, size appropriately for each individual motor, and each run.4.
DISCONNECTS
Ensure the disconnects are horsepower rated for the motor being disconnected.5.
GROUNDING
Strictly adhere to the VFD manufacturer's grounding instructions.6.
CONDUIT
Select a conduit type appropriate for the environment (wet, corrosive, etc.). Consider using rigid metal conduit (RMC) for its shielding properties.7.
SEPARATE CONDUITS (Conservative Approach)
If there is any doubt about the control scheme or if you want the most robust and future-proof installation, running separate conduits for each fan is the safest option. This eliminates any potential issues related to parallel operation and simplifies troubleshooting.
In Summary
While running both feeders from a single VFD in the same conduit might be acceptable if the fans always* operate identically, the safest and most recommended approach is to run them in separate conduits, especially if there is any possibility of independent control. Prioritize clarity on the control scheme, use shielded VFD cables, and follow all applicable NEC and manufacturer's recommendations. Flag for review