Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Two feeders supplying a single control panel

User: Juls, Location: Ohio

Asked on: Tuesday, September 17, 2024 at 5:36 pm EDT
Answered on: Thursday, March 6, 2025 at 2:35 am EST

Question: Am I not violating any code rules if I have to design two separate power feed to a single control panel. Both power feeders will be 120V 1P from two separate customer Power panel. The intention was one feed will be the main supply and the other feed is a secondary supply to the control panel. Any thought?

You're right to ask about this. Running two separate 120V 1-phase feeds from two separate customer power panels to a single control panel requires careful consideration and adherence to the National Electrical Code (NEC) and possibly local codes. Here's a breakdown of the concerns and what you need to do to ensure compliance

Key Concerns and NEC Considerations:

1. Overcurrent Protection



NEC Article 240

Each ungrounded conductor (hot wire) MUST have overcurrent protection at the point where it receives its supply. This means circuit breakers or fuses in BOTH panels feeding the control panel. These must be appropriately sized for the conductors and the load.


Feeder Tap Rules (NEC 240.21)

If the conductors from the customer panel to your control panel are considered "taps" (i.e., shorter conductors from a larger feeder), then the tap rules must be strictly followed. These rules dictate maximum tap lengths and overcurrent protection requirements. This usually is not the case for a main feeder.2.

Neutral/Grounded Conductor Sharing (NEC 250.30)



Separate Derived Systems

The NEC generally discourages sharing neutral conductors between separately derived systems (like those from different panels). The reason is that fault currents from one system could return on the neutral of the other, creating potentially dangerous conditions.


Specific Exception

NEC 250.30(A)(5)(b) does allow for the use of a common neutral under specific conditions, particularly if you are using a separately derived system such as a transformer, generator, or inverter. If your control panel contains one of these sources the common neutral is not only permissible but recommended.

The best practice is to run separate neutrals from EACH source to the control panel's neutral terminal.
Connect the equipment grounding conductor to the control panel and bond that to the neutral terminal.3. Grounding (NEC Article 250)



Equipment Grounding Conductor (EGC)

You MUST run an equipment grounding conductor (EGC) from each of the customer panels to the control panel. This is usually a green insulated wire, or can be metal conduit. This conductor provides a low-impedance path for fault current to return to the source, facilitating the operation of the overcurrent protection device.

Bonding

Within the control panel, all non-current-carrying metallic parts (enclosure, etc.) must be bonded together and to the EGC.4.

Disconnecting Means (NEC Article 430, 440, 670)



Multiple Sources

Because you have two separate power sources, you need a way to simultaneously disconnect ALL ungrounded conductors at the control panel.

Main Disconnect

A single main disconnect switch within the control panel that is rated to interrupt the total available fault current and connected to BOTH power feeds is essential. It must clearly disconnect ALL power to the control panel.


Marking (NEC 110.22)

The disconnect switch must be clearly and permanently marked to indicate that it disconnects ALL power to the control panel.5.

Lockout/Tagout (OSHA 1910.147)

Even with a main disconnect, you need a procedure for safely isolating both power sources for maintenance or troubleshooting. Lockout/tagout procedures are crucial to prevent accidental re-energization. The procedure should consider the location of both circuit breakers supplying the control panel.6.

Wiring Methods (NEC Chapter 3)

The wiring methods used (conduit type, wire type, etc.) must be suitable for the environment and comply with the NEC.7.

Voltage Ratings

All components within the control panel must be rated for the applied voltage (120V).8.

Short-Circuit Current Rating (SCCR) (NEC 409.22)

This is a critical and often overlooked requirement. The control panel MUST have a short-circuit current rating (SCCR) that is equal to or greater than the available fault current at its terminals. This means you need to know the fault current that the customer's electrical system can deliver to the control panel. The SCCR rating must be tested and certified to show the control panel's equipment can withstand the tested fault rating. Determining the SCCR can be complex and may require an engineering study. You need to know the utility's available fault current, the transformer size and impedance feeding the customer's panels, and the length and size of the conductors to the control panel. If the control panel SCCR is too low, you might need to use current-limiting fuses or other protective devices to reduce the available fault current.9.

Redundancy and Safety

The intent of a redundant power supply is to increase the control panel's reliability and ensure uninterrupted operation. However, it is crucial to consider the safety implications of having two separate power sources and ensure that the design minimizes the risk of electrical hazards.10.

Coordination with customer
You must coordinate with the customer to see the specific limitations in place with their electrical system and specific regulations they need to follow.

Why the Code is Concerned

The NEC is primarily concerned with safety. Having two separate power sources feeding a single panel creates the potential for:

Backfeed

One power source could energize the other source's circuit if not properly isolated, potentially endangering personnel working on the supposedly "dead" circuit.


Overloading

Without proper coordination, it's possible to overload one circuit while the other is lightly loaded, potentially causing overheating and fire.

Voltage Imbalance

If the voltage levels on the two sources are slightly different, it can cause problems with sensitive equipment.


Unexpected Energization

Someone working on the control panel might disconnect one source, assuming the panel is de-energized, but the other source could still be supplying power.

Recommendations and Steps to Take


Consult with a Licensed Electrical Engineer

This is highly recommended. A qualified engineer can perform a proper analysis, determine the available fault current, select appropriate components, and ensure compliance with all applicable codes.2.

Detailed Documentation

Create detailed electrical schematics and wiring diagrams showing how the two power feeds are connected, the locations of all overcurrent protection devices, the grounding system, and the main disconnect.3.

Secure Necessary Permits and Inspections

Before starting any work, obtain the required electrical permits from your local authority. Arrange for inspections to ensure the installation meets code requirements.4.

Careful Wiring and Labeling

Use proper wiring methods and clearly label all conductors and components. Label the disconnect switch to indicate that it disconnects ALL power sources.5.

Develop a Lockout/Tagout Procedure

Create a written lockout/tagout procedure specific to this control panel. Train all personnel who will be working on or near the panel on the procedure.6.

Consider a Power Transfer Switch

Depending on the criticality of the control panel, a transfer switch may be beneficial. An Automatic Transfer Switch (ATS) will automatically switch between the primary and secondary power sources in the event of a power outage.

In summary, while it's possible to implement two separate feeds to a control panel, it requires meticulous planning, adherence to the NEC, and potentially the involvement of a qualified electrical engineer. Don't take shortcuts – safety should always be the top priority.
Flag for review

Previous Question Next Question