Topic: 3ph 240V 3W Inverter to replace a Solectria PVI 75kW

User: solarken, Location: Hudson, OH, USA

Asked on: Tuesday, September 17, 2024 at 7:11 pm EDT
Answered on: Thursday, March 6, 2025 at 2:35 am EST

Question: Has anyone dealt with replacing an old failed 3ph Solectria PVI 75kW Inverter with a 600V array, DC combiners, etc and 240V 3-Wire delta output wiring? I'm trying to think of an option besides reconfiguring the array, adding a transformer, and redoing a lot of wiring. There doesn't seem to be a lot of 240V delta inverters out there. Would appreciate any ideas.

You're right, finding a direct replacement for a 240V Delta Solectria PVI 75kW is tough these days. Most new inverters are designed for higher voltage systems. Here's a breakdown of the challenges and potential solutions, along with their pros and cons

Understanding the Challenges
Limited 240V Delta Inverter Options

The market has largely shifted away from 240V Delta inverters for large commercial systems. Higher voltage systems (480V, 600V) are more efficient for power transmission and are the current industry standard.


Array Voltage Mismatch

Your 600V array is likely wired for a higher DC voltage range than what a 240V inverter would typically handle.

Code Compliance

Any changes you make need to comply with local and national electrical codes (NEC in the US).

Potential Solutions and their Trade-offs
1. Reconfiguring the PV Array



How it works

Rewire the series strings in your array to lower the DC voltage and increase the parallel strings to maintain power. This would theoretically allow you to use a string inverter designed for a lower DC voltage range, and then step up the AC with a transformer.

Pros

Potentially cheapest option (if you can use existing mounting hardware). Could allow for use of more readily available inverters.

Cons

Labor intensive and time consuming. May require longer wire runs to the combiner boxes. Changes the performance characteristics of the PV array. May impact your module warranties. May not be feasible depending on array layout, module type, and available space. Requires careful engineering to ensure proper voltage and current matching with the new inverter.2.

Using a Transformer with a Higher Voltage Inverter



How it works

Replace the Solectria with a modern 480V or 600V inverter and use a step-down transformer to convert the output to 240V Delta.


Pros

Access to a wide range of modern, efficient inverters (e.g., SMA Sunny Tripower CORE1, Sungrow SG75CX-US, Fronius Eco). Monitoring and control features are typically superior to older inverters. Often higher efficiency and longer lifespan.

Cons

Increased cost due to the transformer (significant expense). Transformer adds to the overall system losses. Transformer requires space and proper ventilation. Transformer adds weight and complexity.3.

Central Inverter with String Combiners and Transformer



How it works

Use a central inverter designed for your existing DC voltage (600V) and then use a step-down transformer to get the 240V Delta output. Central inverters are usually larger and more robust.


Pros

Handles the existing DC voltage well. May be more rugged and reliable than string inverters in some applications.

Cons

Higher upfront cost compared to string inverters. Less redundancy – if the central inverter fails, the entire system is down. May have higher cooling requirements. Transformer still needed.4.

DC-DC Optimization and Inverter Replacement



How it Works

Implement DC-DC optimizers (e.g., Tigo, SolarEdge, APsystems) on each module or pair of modules. These optimizers allow you to standardize the DC voltage presented to a central inverter. This could potentially allow you to use a higher voltage inverter (480V or 600V) and then a transformer to step down to 240V Delta.

Pros

Module-level monitoring and optimization. Potential for increased energy harvest, especially in shaded conditions. Some optimizers offer rapid shutdown capabilities. Could potentially simplify the DC string wiring.

Cons

Significant upfront cost for the optimizers. Adds complexity to the system. Increases the number of components that could fail. Transformer still needed.5.

Consider Replacing the Entire System



How it works

This might seem extreme, but if the modules are nearing end-of-life or performing poorly, it might be more economical in the long run to replace everything.


Pros

Full optimization with modern components. Higher efficiency and performance. New warranties. Potential for increased system size due to improved module efficiency.

Cons

Highest upfront cost. Requires more permitting and design work.

Recommendation and Steps to Take
1. Get a Professional Assessment



The BEST course of action is to consult with a qualified solar installer or electrical engineer.
They can assess your specific site conditions, array configuration, electrical infrastructure, and local code requirements. They can also provide a detailed cost analysis of each option.2. Load Analysis

Before choosing an inverter size, perform a load analysis of the equipment that will be powered by the 240V Delta system. Make sure you select an inverter that can adequately handle the demand.3.

Cost Analysis

Gather quotes for each solution, including equipment, labor, and permitting costs. Factor in the long-term operational costs, such as efficiency losses, maintenance, and potential replacements.4.

Evaluate Warranties

Carefully review the warranties offered by the inverter and transformer manufacturers.5.

Consider Future Expansion

If you anticipate expanding the system in the future, choose a solution that is scalable and flexible.

Specific Inverter Brands to Investigate (if going the transformer route)



SMA

Sunny Tripower CORE1 (excellent reputation for reliability)

Sungrow

SG75CX-US (competitive pricing, good performance)


Fronius

Eco Series (well-regarded for efficiency and monitoring)

Yaskawa Solectria

Still around but focused on larger grid-scale systems. You
might find a used 240V inverter, but that's risky.

Important Considerations



NEC Code Compliance

Pay close attention to Article 690 of the NEC for solar photovoltaic systems. Ensure that all wiring, overcurrent protection, and grounding requirements are met.

Rapid Shutdown

Many jurisdictions now require rapid shutdown systems for PV arrays. Make sure your chosen solution is compliant.


Grid Interconnection:
Work closely with your utility company to ensure that the new system meets their interconnection requirements.Good luck! It's a challenging situation, but with careful planning and professional guidance, you can find a suitable solution. Remember to prioritize safety and code compliance. Flag for review