Topic: Grounded outlets near water

User: Stellar, Location: Michigan

Asked on: Tuesday, September 17, 2024 at 8:09 pm EDT
Answered on: Thursday, March 6, 2025 at 2:35 am EST

Question: Where does it say an outlet next to a sink has to be GROUNDED in a kitchen, bathroom & laundry. Code section in national electrical code

The National Electrical Code (NEC) doesn't just require grounding for outlets near sinks in kitchens, bathrooms, and laundry areas. It requires ground-fault circuit interrupter (GFCI) protection. GFCI protection works by detecting very small current leakages to ground and immediately shutting off the power. A properly grounded receptacle is essential for a GFCI to function correctly, but the protection requirement goes beyond simply being grounded.Here are the relevant NEC sections, along with explanations: NEC 210.8(A) Bathrooms

"All 125-volt through 250-volt receptacles installed in bathrooms shall have GFCI protection for personnel." (This means any receptacle within a bathroom, regardless of proximity to a sink, must be GFCI protected.)


NEC 210.8(B)(1) Kitchens

"All receptacles serving countertop surfaces in kitchens shall have GFCI protection for personnel." (This covers countertop receptacles, and often includes those near sinks).*

NEC 210.8(C)(1) Laundry Areas:
"All receptacles installed in laundry areas shall have GFCI protection for personnel." (This covers all receptacles in the laundry area, regardless of proximity to a sink).Therefore, grounding is part of the requirement for the GFCI to function, but GFCI protection itself is the primary requirement. You need both a properly grounded circuit AND a GFCI device (either a GFCI receptacle or a GFCI circuit breaker) to meet code. Flag for review