Topic: Jeez, simple help on KVA calc

User: fastline, Location: midwest usa

Asked on: Wednesday, September 18, 2024 at 1:20 am EDT
Answered on: Thursday, March 6, 2025 at 2:35 am EST

Question: Maybe I need sleep but here is the simple deal. 150kva Xfrmr. 208/120 sec. What are the available amps at 120? I have 1250A. basically on single phase, you don't divide by sq3. It just seems really high but it does make sense as the 3P side is 416.37 and that *3 is about the 1250A. It's late and I haven't done this in a few.

You are correct! Here's the breakdown: Transformer KVA to VA

150 kVA
1000 VA/kVA = 150,000 VA

Single-Phase Calculation

VA / Voltage = Amps
150,000 VA / 120 V =

1250 Amps


So, yes, you have 1250 Amps available at 120V. Your logic and math are spot on, even if you are tired!It does seem like a lot of amps, because it is a lot of amps. 150kVA is a significant amount of power. Just make sure whatever you're connecting to that 120V circuit is appropriately sized to handle that kind of current. Flag for review