User: WCEI, Location: Central Virginia
Asked on: Wednesday, September 18, 2024 at 7:38 am EDT
Answered on: Thursday, March 6, 2025 at 2:36 am EST
Question: Dennis, I briefly checked FAQ’s before I posted this, but did not see it addressed. If I missed it in my haste, you can slap my hand.We have had inspectors require that both a ufer and driven ground rods be used, and we have had inspectors make us remove the connection to the ground rods because a ufer was used.Which is correct, and why and where is this referenced in the code?
Okay, let's break down the Ufer ground and ground rod situation, and I'll try to clear up the conflicting interpretations you're seeing. No hand-slapping necessary – it's a common point of confusion!The Short Answer
Generally, you need both a Ufer ground (concrete-encased electrode) and supplemental grounding electrodes (like ground rods) unless the Ufer ground alone meets specific low-resistance criteria.
The Code References and Explanation
The primary code section dealing with this is
NEC 250.50 - Grounding Electrode System. It requires that all grounding electrodes that are present must be bonded together to form the grounding electrode system. This means if you have a Ufer ground, it must be used. This is a common interpretation issue. Some inspectors are under the mistaken impression that a Ufer eliminates the requirement for supplemental electrodes. It does not.Here's a more detailed look: 250.50 - Grounding Electrode System. All grounding electrodes as described in 250.52 that are present at each building or structure served shall be bonded together to form the grounding electrode system. This means if you have a Ufer, it's part of the grounding electrode system. You can't just ignore it or remove its connection. You must use it. 250.52 - Grounding Electrodes. This section lists acceptable grounding electrodes. It includes: (A)(3) Concrete-Encased Electrode (Ufer Ground)
Defined as at least 20 feet of bare or zinc galvanized or other electrically conductive coated steel reinforcing bar or rod of not less than 1/2 inch (12.7 mm) in diameter, encased by at least 2 inches (50 mm) of concrete and located within a concrete foundation or footing that is in direct contact with the earth. The rebar can be near the bottom, or within the middle of the concrete foundation or footing.
(A)(5) Ground Rods and Pipes
These are also acceptable grounding electrodes.
250.53(A) - Grounding Electrode System Installation Requires that systems with ground rods and other electrodes be bonded together. 250.53(A)(3) Supplemental Electrode Required. A single rod, pipe or plate electrode shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). The supplemental electrode shall be bonded to one of the following:1. Grounding electrode conductor2. Grounded conductor3. Equipment grounding conductor4. The metal enclosure that contains the grounding electrode conductor connection to grounding electrode5. The metal enclosure that contains the grounding electrode conductor connection to grounding electrodeThe supplemental electrode shall be permitted to be installed at the same location as the rod, pipe, or plate electrode. Exception to 250.53(A)(3)
If a single rod, pipe, or plate grounding electrode has a resistance to earth of 25 ohms or less, the supplemental electrode shall not be required. This is the key! If you can demonstrate that the Ufer ground has a resistance to earth of 25 ohms or less (using a proper ground resistance meter and testing method), then you technically don't need the supplemental electrodes. However, this test is rarely performed, and documentation is needed to prove compliance.
Why the Confusion and Conflicting Interpretations? Misunderstanding of "Supplemental"
Some inspectors incorrectly assume that if you have a Ufer, you don't need any other electrodes. The code doesn't say that. It only offers an exception to the supplemental electrode requirement if the Ufer meets the 25-ohm resistance threshold.
Local Amendments
While rare, some jurisdictions might have local amendments to the NEC that alter these requirements. Always check for local variations.
Habit and Tradition
Some inspectors might have always done it a certain way and are resistant to change or don't keep up with code updates.
Lack of Testing
Few installations actually test the Ufer ground to verify its resistance. Without that test, the supplemental electrodes are required by default.
In Practical Terms
Install the Ufer Ground
Make sure it meets the specifications in 250.52(A)(3).
2.
Install Supplemental Electrodes
Usually this means two ground rods (spaced at least 6 feet apart, as per 250.53(B)).
3.
Bond Everything Together
Connect the Ufer ground, the ground rods, and the service equipment to the grounding electrode conductor, forming a complete grounding electrode system.
Addressing the Inspector
If you encounter an inspector who insists on removing the ground rod connection when a Ufer is present, politely point out: NEC 250.50 requires all present grounding electrodes to be bonded together. The Ufer is a grounding electrode. NEC 250.53(A)(3) generally requires supplemental electrodes (like ground rods). The exception to that requirement only applies if you can demonstrate the Ufer's resistance to earth is 25 ohms or less (and you'd need to have that documented).If the inspector remains insistent, ask for a written code reference for their interpretation or ask to speak to their supervisor.
In Summary:
Err on the side of compliance. Unless you specifically test the Ufer and prove it meets the 25-ohm resistance requirement, install the Ufer ground and supplemental grounding electrodes and bond them all together. This is the safest and most defensible approach. It avoids arguments with inspectors and ensures a robust grounding system. Flag for review