User: WCEI, Location: Central Virginia
Asked on: Wednesday, September 18, 2024 at 7:50 am EDT
Answered on: Thursday, March 6, 2025 at 2:36 am EST
Question: On a set of drawings we are working from, the engineer stated to install the MC in PVC. We assume for support?If you only sleeve it through PVC without connecting the PVC on either in, is it legal? The MC will be properly connected with approved MC connectors.IF permitted, and two or more MC cables are installed in the same PVC sleeve, without the ends sealed, is de-rating required?Just as important as your answer, please let me know what Article you are referencing.Thank you everyone.
Okay, let's break down the engineer's direction to install MC cable in PVC and address the legality and potential derating requirements.1. Legality of MC Cable in PVC Sleeve (Without Connection) Yes, it is generally permitted, provided the MC cable is properly supported and secured according to code. NEC References
NEC 330.30 Securing and Supporting
This section mandates how MC cable must be supported and secured. Sleeving it through PVC can be a method to provide physical protection, but the MC cable itself must still be supported at appropriate intervals as outlined in 330.30(A) through (E). The PVC sleeve itself does not relieve you of the obligation to support the MC cable properly.
NEC 300.11 Securing and Supporting
This section states that raceways (which would include PVC conduit, even if used as a sleeve) must be securely fastened in place. If the PVC sleeve isn't secured, it could create a hazardous situation.
NEC 300.12 Mechanical Continuity - Raceways and Cables
This section calls for raceways and cable sheaths to be mechanically continuous between boxes, cabinets, or other equipment. Using a short PVC sleeve does not create a continuous raceway system.
Explanation
The NEC doesn't prohibit running MC cable through a short section of PVC for physical protection or support. The key is that the MC cable itself must meet the requirements of Article 330. This includes proper support, protection from physical damage, and acceptable bending radii. The PVC is essentially acting as a sleeve, providing localized protection. It is
not acting as a raceway system in the traditional sense. The NEC mandates that the cables need to be supported (and not rest on the conduits if in a ceiling for example).2. Derating Requirements for Multiple MC Cables in a PVC Sleeve Yes, derating may be required, depending on the length of the sleeve and the number of current-carrying conductors within the cables. NEC References
NEC 310.15(B)(3) Adjustment Factors
This section deals with adjustment factors for ambient temperature and the number of current-carrying conductors in a raceway or cable.
NEC 310.15(A)(3): Ampacities for Cables Installed in Cable Trays and Direct Buried Cables
The amount of heat produced by the cable may be insufficient to warrant derating if the cable is not bundled for more than 24"
Explanation
If the PVC sleeve is considered a raceway or cable tray (as defined by the NEC), and it contains more than three current-carrying conductors (from all the MC cables combined), then you must apply the adjustment factors in NEC 310.15(B)(3). If the PVC sleeve is longer than 24 inches, then it may be considered to be a raceway. If the PVC sleeve is very short (say, just a few inches) and serves only to protect the MC cable as it passes through a wall, it's less likely that derating would be required. The key is whether the grouping of conductors in the sleeve creates a significant heat buildup. The closer the conductors are, and the longer they are together, the more the heat builds up and derating must be applied. Consider also whether the ends are sealed or not. With an unsealed sleeve, the air flows through it, which can help with derating.
Important Considerations
Engineer's Intent
Clarify with the engineer why they specified MC in PVC. Understanding their reasoning will help you implement the installation correctly and safely. There might be specific environmental or physical protection concerns.
AHJ Approval
Always check with the local Authority Having Jurisdiction (AHJ) for their interpretation and specific requirements. The AHJ has the final say.
Physical Protection
Ensure the PVC adequately protects the MC cable from physical damage, as that may be the primary reason for the engineer's specification.
Proper Connectors
Use the correct MC cable connectors at both ends of the cable run to ensure a proper and safe connection.
Support
The most important reason to sleeve the MC cable is because the support system does not meet code. Ensure you install a proper support system.
In summary:
Installing MC cable through a short PVC sleeve can be acceptable, but the MC cable must still be properly supported and secured according to the NEC. Derating may be required if the PVC sleeve contains multiple current-carrying conductors and is of sufficient length to cause heat buildup. Always clarify the engineer's intent and consult with the local AHJ. Flag for review