Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: GEC in Parallel Raceways

User: pvgreeze, Location: Philadelphia

Asked on: Wednesday, September 18, 2024 at 11:03 am EDT
Answered on: Thursday, March 6, 2025 at 2:36 am EST

Question: Hi everyone, I've been looking through threads for a discussion on this topic, and I cannot find anything specific to the issue I'm facing. The AHJ in question uses the 2017 NEC, so all references will be to that, though I think the language of the code is consistent in later versions...I have a PV Disconnect outside of a building, line side interconnection, that is a separate service disconnect [230.2(A)(5)]. In this disconnect, I am bonding the ground (grounding) and the neutral (grounded) with a main bonding jumper sized off Table 250.102(C)(1) [250.24(B) & 250.28]. Now, I need to connect the ground in PV Disconnect to the building grounding electrode system [250.58 and 690.47(A)]. This connection will be achieved with a grounding electrode conductor (GEC), which is sized off of Table 250.66 for this building, which now has multiple [service] disconnecting means in separate enclosures [250.64(D)(2)].My grounding electrode conductor is sized off of NEC 250.66. For this PV system, the OCPD is a 1000A fuse, with three parallel sets of service entrance conductors off the line side of the existing main circuit breaker, in parallel ferrous raceways.Here is where I am confused. Table 250.66 requires me to only have a single 3/0 Cu GEC. A conventional service would have this GEC connected between the grounding busbar in the main switchboard and the building grounding electrode system (GES) - building steel, pipes, ground rods, etc. However, my PV Disconnect is outside of the building, and I need to tie this PV Disconnect GES to the building GES, as outlined above, with a single 3/0 Cu GEC. The easiest method to do this would be to run this GEC with the parallel ungrounded conductors & neutrals to the existing main circuit breaker and connect within the existing switchboard.My questions are:Can I run a single GEC in the same raceway as phase and neutral (grounded) conductors to the point of inteconnection/the most practical tie in point to connect to the existing GESCan I run a single GEC in one raceway when there are multiple parallel raceways, several of which would not contain GECsWould love to know thoughts and comments. I've read through several related threads, and didn't see anything that addressed this specific concern. I'll link below for reference:GEC for PV DisconnectsFor a supply side connection, do I really need a GEC? Some AHJ's require it, some don't care and some won't accept it because they're saying it creates a parallel pathway for a ground fault (which kinda makes sense to me). Honestly, I don't think it's needed as long as the N-G are bonded in the...

Okay, let's break down your PV system grounding question according to the 2017 NEC, addressing your specific concerns

Understanding the Context
Supply-Side Interconnection

You're connecting to the line side of the service, making this a
separately derived system in many ways, despite not being a transformer.

Separate Service Disconnect

The PV disconnect is considered a separate service disconnect per 230.2(A)(5), necessitating its own grounding and bonding requirements.

Parallel Conductors

You have three sets of parallel service-entrance conductors.

Answering Your Questions
1. Can I run a single GEC in the same raceway as phase and neutral (grounded) conductors to the point of interconnection/the most practical tie in point to connect to the existing GES? Yes, with caveats. The NEC doesn't explicitly prohibit running the GEC within the same raceway as the ungrounded and grounded conductors to the point of interconnection (the main switchboard). However, the key consideration is induced currents. This is where the ferrous raceway comes into play. NEC 250.64(E) addresses this

This section deals with grounding electrode conductors in aluminum or copper clad aluminum where they are not protected from physical damage, so the metal raceway protects them.


Minimizing Impedance & Induced Currents (Important)

While you can run the GEC in the same raceway, it's highly advisable to run it

bonded to the raceway
at both ends if you choose this route, to minimize inductive reactance. This would follow the rules from 250.92(B)(4) and 300.3(B), which deal with bonding metal raceways to ensure fault current return paths have low impedance. The purpose of this is to prevent circulating currents. Alternative: Run GEC Outside the Raceway

A
better practice, and often the preferred practice, is to run the GEC outside the raceway altogether. This eliminates the potential for inductive heating of the raceway and minimizes impedance in the ground-fault return path. If you choose this route, the GEC must be protected from physical damage per 250.64(B), which could be with conduit, but it does not need to be metallic.
2.


Can I run a single GEC in one raceway when there are multiple parallel raceways, several of which would not contain GECs?
This is problematic and generally not allowed without proper bonding. If you run the single GEC in only one of the parallel raceways, you create a significant imbalance in the ground-fault return path. This can lead to: Increased Impedance

The ground-fault current will have a higher impedance path back to the source, potentially slowing down the OCPD tripping time.


Unequal Current Sharing

The fault current won't be equally distributed among the parallel raceways.

Potential Overheating

The raceway containing the GEC could overheat under fault conditions due to carrying a disproportionate amount of fault current.


NEC 300.3(B) is relevant here.
This section emphasizes the need to run all circuit conductors (including the grounding conductor) together in the same raceway or cable. While you don't technically have to run a GEC in each raceway, the effect of not doing so requires careful consideration. If you absolutely must do this... (but I strongly advise against it): You would need to thoroughly bond all the parallel raceways together at both ends to ensure an effective ground-fault current path. This means using bonding jumpers sized per 250.102(C) and securely connecting them to each raceway. Even with this, the impedance of the ground-fault path is likely to be higher than if you had run the GEC outside the raceways.

Recommendations
Ideal

Run the 3/0 Cu GEC outside the parallel raceways, protected from physical damage, directly to the building grounding electrode system. This eliminates induced currents and provides a low-impedance ground-fault path.

Acceptable (with caution)

Run the 3/0 Cu GEC
inside one of the parallel raceways, but only if the raceway is bonded to the GEC at both ends to minimize inductive reactance. Ensure all parallel raceways are also bonded together.

Avoid

Running the GEC in only one of the parallel raceways without adequate bonding of all the raceways.

Important Considerations
Local AHJ Interpretation

Always consult with your local AHJ. They may have specific requirements or preferences regarding GEC routing.


Engineering Judgement

Use your engineering judgement to determine the best approach based on the specific site conditions and constraints. Consider factors such as the length of the raceways, the size of the conductors, and the available space for running the GEC.

Example Scenario


Let's say you have three parallel 4" EMT conduits carrying the service-entrance conductors. Option 1 (Preferred)

Run the 3/0 Cu GEC outside of all three conduits, secured to the building structure and protected from physical damage. Connect it directly to the building grounding electrode system.


Option 2 (Less Preferred)

Run the 3/0 Cu GEC inside one of the 4" EMT conduits. Bond the GEC to the conduit at the PV disconnect enclosure and at the main switchboard. Also, bond all three 4" EMT conduits together at both ends with bonding jumpers sized per 250.102(C).

In summary, while the NEC might allow you to run the GEC in the same raceway as the service-entrance conductors, or in only one of multiple parallel raceways, it's not always the best practice. The key is to ensure a low-impedance ground-fault path and minimize the potential for induced currents and overheating.
Flag for review

Previous Question Next Question