Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Temperature rating of conductors vs terminal temperature

User: Dennis Alwon, Location: Chapel Hill, NC

Asked on: Wednesday, September 18, 2024 at 4:41 pm EDT
Answered on: Thursday, March 6, 2025 at 2:37 am EST

Question: I found this in a 2009 article from the IAEI. I don't understand why one cannot use 60C or 75C insulation on a 90C terminal if the ampacity is rated to the conductor temp.Same is true for 75C terminal and 60C wireCan anyone clarify why this is so.

You're right to question this, as it can be a confusing topic! Here's a breakdown of why you can't always just use the conductor's ampacity even if it's within the temperature rating of the termination

The Core Principle: Heat Dissipation and Termination Temperature Limits

The primary reason behind these limitations is about managing heat. Electrical terminations (like breakers, lugs, and devices) have a maximum operating temperature rating (e.g., 60°C, 75°C, 90°C). This rating is determined by the materials used in the termination and the potential for them to degrade or fail if overheated.Here's the issue: Heat Generation

Conductors carrying current generate heat due to resistance (I²R losses). The amount of heat generated depends on the current (I), the conductor's resistance (R), and the length of the conductor.


Heat Transfer

That heat needs to dissipate away from the conductor. The termination acts as a "heat sink," conducting heat from the conductor into the surrounding environment.

Termination Temperature

The temperature of the termination
itself is critical. If the termination gets too hot, it can: Degrade the insulation of the conductor. Loosen connections (thermal expansion and contraction). Damage the device it's connected to. In extreme cases, cause a fire.

Why the Restrictions Exist
1. 60°C or 75°C Terminal, 90°C Wire



Problem

While the 90°C wire can handle a higher temperature, the 60°C or 75°C terminal cannot. The terminal is designed to effectively dissipate only a certain amount of heat. If you run the 90°C wire at its 90°C ampacity, it will generate more heat, which will conduct into the terminal. This could cause the terminal to exceed its 60°C or 75°C rating, leading to problems as described above.

Solution

You
can use the 90°C wire, but you must use the ampacity from the 60°C or 75°C column of the ampacity tables (NEC Table 310.16/310.15(B)(16)), depending on the terminal rating. This effectively limits the current flowing through the wire and therefore reduces the heat generated, ensuring the terminal stays within its temperature rating.
2.


75°C Terminal, 60°C Wire



Problem

The 60°C wire has a lower temperature rating. While the 75°C termination can handle more heat, the wire will overheat if you run too much current through it. Even though the terminal can withstand a higher temperature, the weak link is now the conductor's insulation.

Solution

You must use the ampacity from the 60°C column of the ampacity tables. This ensures that the wire insulation is not subjected to temperatures exceeding its rating. The terminal will be operating well below its maximum temperature, which is fine.

NEC 110.14(C) and Small Conductors

The NEC (National Electrical Code) addresses this specifically in 110.14(C). The 2009 version states something to the effect that:
"Terminations for conductors rated 100 amperes or less, and marked for not more than 75°C... shall be used with conductors rated not more than 75°C." "Terminations for conductors rated over 100 amperes shall be used with conductors rated not more than 75°C."In essence, most terminations are rated for 75°C. For smaller conductors (100A or less), you are usually required to use the 75°C ampacity column. The exception is if the equipment is specifically marked to allow for higher temperature terminations (which is rare for smaller equipment). This means that even if you use 90°C rated wire, you still have to use the lower 75°C ampacity because of the termination limitations.

Exceptions and Considerations



Equipment Marking

If equipment is specifically marked to allow for 90°C terminations, you can use the 90°C ampacity of the conductor (assuming all other conditions are met). This is relatively rare, especially in residential and smaller commercial installations. Look for markings like "Suitable for use with 90°C conductors."

Derating and Adjustment Factors

Even if you
can use the 90°C ampacity based on equipment markings, you still need to apply any derating or adjustment factors as required by the NEC (e.g., for ambient temperature, conduit fill). The starting point for those derating calculations is always the ampacity of the conductor at its rated temperature (e.g., 90°C), but then you must adjust it downwards.

Free Air

If a conductor is run in free air (not in conduit or cable), the heat dissipation is much better. In some cases, the NEC allows higher ampacities in free air than in conduit.*

Engineering Judgment

In complex situations or for large installations, it may be necessary to perform calculations and/or consult with a qualified electrical engineer to ensure proper conductor sizing and temperature management.

In summary, while a conductor may have a 90°C insulation rating, the overall system's ampacity is limited by the weakest link – the temperature rating of the termination or the wire insulation itself.
Always follow the equipment markings and the requirements of the NEC to ensure a safe and code-compliant installation. When in doubt, use the 75°C ampacity column. It is the most commonly used and safest choice in most circumstances. Flag for review

Previous Question Next Question