User: xguard, Location: Baton Rouge, LA
Asked on: Wednesday, September 18, 2024 at 5:58 pm EDT
Answered on: Thursday, March 6, 2025 at 2:38 am EST
Question: I don't recall seeing a circuit breaker before with a 60C/70C rating before. This circuit breaker is on a generator. I've seen them marked with the ambient temperature rating for the circuit breaker trip curve but this looks like it's referring to the lug temperature rating. I'd assume I'm limited to the 60C ampacity column. Thoughts? Any information would be appreciated, thanks.
You're right to be cautious and thoughtful about that 60C/70C rating. You're also likely correct in that it refers to the terminal/lug temperature rating. Here's a breakdown of what it means and how to interpret it
Understanding the 60C/70C Rating on a Circuit Breaker
Terminal Temperature Rating
This marking on a circuit breaker indicates the maximum allowable temperature of the wire termination point (where the wires connect to the breaker) under continuous load. It's related to preventing overheating and potential fire hazards at the connection.
Relationship to Wire Ampacity
This temperature rating directly affects the allowable ampacity (current-carrying capacity) of the conductors you connect to the breaker.
Why 60C/70C? Common Standards
These are two of the most common temperature ratings for electrical equipment terminations in North America, based on UL standards and the NEC (National Electrical Code).
Material Compatibility
The temperature rating reflects the materials used in the breaker's terminals and the insulation of the conductors. Exceeding the temperature rating can degrade these materials over time, leading to failure.
How to Interpret the Rating and Select Conductors1. Default to the Lower Rating (60°C)
Unless the circuit breaker and all other equipment in the circuit are specifically listed and marked for 75°C or 90°C terminations (and the conductors themselves are rated for at least that temperature), you must use the 60°C ampacity column in NEC Table 310.16. This is the most conservative and safest approach.
2.
Read the Fine Print (Equipment Listings)
Circuit Breaker Listing
The circuit breaker's listing information (typically found on the breaker itself or in its documentation) will sometimes state the acceptable temperature rating for terminations. Pay very close attention to this. If it says "Suitable for use with 60°C or 75°C conductors," you can use the 75°C column if all other conditions are met. If it only mentions 60°C, you're limited to that.
Generator Listing
Also, carefully review the generator's documentation. It might have specific wiring requirements that override general NEC rules.3.
Check Equipment Terminations
Look at the terminals where the conductors connect at both ends of the circuit. For example, if this is the generator's output breaker and you're connecting to a transfer switch, check the temperature rating of the transfer switch terminations as well. The lowest rated termination point in the circuit dictates the ampacity of the conductors.4.
Conductor Insulation
The conductors themselves must be rated for at least the temperature you're using for ampacity calculations (60°C, 75°C, or 90°C). Common insulation types are THHN, THWN, THW, XHHW, etc. Look for the temperature rating printed on the conductor's insulation.
Example
Let's say you have a 60A circuit breaker with a 60°C/70°C rating.
If the breaker listing or generator documentation doesn't explicitly allow 75°C terminations
You must use the 60°C column in NEC Table 310.16. For copper conductors, you'd need at least #4 AWG wire (which is typically rated THHN/THWN-2 90C, but you are still limited to the 60C ampacity).
If the breaker and the generator are both listed for 75°C terminations, and the conductors are rated for at least 75°C (e.g., THHN/THWN-2)
You could use the 75°C ampacity column. For a 60A circuit, that would allow you to use a smaller conductor gauge if desired (though #4 would likely still be sufficient).
Important Considerations
Upgrading from 60°C to 75°C or 90°C
While it might seem appealing to use a smaller gauge conductor by using a higher temperature rating, ensure that doing so doesn't create other problems, such as increased voltage drop over long runs.
Derating for Ambient Temperature
The ambient temperature around the conductors and equipment can affect their ampacity. If the ambient temperature is higher than the standard 30°C (86°F) assumed in NEC Table 310.16, you'll need to derate the conductor's ampacity based on the correction factors provided in the table. This is crucial for generator installations that might be in enclosed spaces.
Professional Advice
When in doubt, always consult with a qualified electrician. They can properly assess the installation, interpret the equipment listings, and ensure that the wiring complies with the NEC and local codes. A mistake could be costly and dangerous.
In summary, yes, you are correct to be conservative and assume you are limited to the 60°C ampacity column unless* you have clear and specific documentation that all components of the circuit (breaker, generator terminations, conductors, and all downstream terminations) are rated and suitable for higher temperatures. Always err on the side of caution and safety! Flag for review