Topic: Copper clad ground rod is that considered non-ferrous?

User: zappy, Location: CA.

Asked on: Wednesday, September 18, 2024 at 7:09 pm EDT
Answered on: Thursday, March 6, 2025 at 2:38 am EST

Question: I'm looking at the code. It says non-ferrous can be half-inch diameter. Iron and or steel has to be 5/8 in diameter. Is a copper clad ground rod considered non-Ferrous? Thank you for your help.

No, a copper-clad steel ground rod is NOT considered non-ferrous. It's a composite material with a steel core. The steel core is the structural component providing the necessary strength for driving the rod into the ground.Since it contains steel (or iron), it falls under the requirement for the larger 5/8 inch diameter in your scenario.Here's why: Ferrous vs. Non-Ferrous

Ferrous materials contain iron. Non-ferrous materials do not. Steel is an iron alloy.


Copper Cladding

The copper cladding is for corrosion resistance and conductivity. It doesn't change the fact that the core is steel. The strength of the ground rod comes from its steel core. The sizing rules generally apply to the material providing the structural strength.

Therefore, in your situation, a copper-clad steel ground rod would need to be 5/8 inch in diameter.


It is important to consult the specific code or standard that your code refers to, since they vary by jurisdiction. If the code only uses the terms "ferrous" and "non-ferrous" then the steel core is ferrous, so it must comply with the rules for ferrous materials. If the relevant regulation specifies the diameter of grounding electrode conductors by material, then the cladding might be relevant. Also, keep in mind that grounding and bonding requirements are very safety-critical, so it's always best to check with a qualified electrical inspector or engineer to confirm proper installation and code compliance in your specific area. Flag for review