Topic: Solar Photovoltaic (PV) Systems 690.31 (B) Identification and Grouping

User: marcelo, Location: Port Chester, NY

Asked on: Thursday, September 19, 2024 at 1:22 pm EDT
Answered on: Thursday, March 6, 2025 at 2:39 am EST

Question: Hello Fellow Electricians,I have a situation where I want to use an existing PVC conduit that feeds a 100A sub-panel located in the garage, (where the solar panels will be installed), to run the phase combiner output back to the main house, where it will be connected to the main electrical panel.690.31 (B) describes the grouping of "DC" circuits and other non PV systems, in my case here, it is NOT "DC", the solar panels are fitted with micro-inverters that will be grouped in three branches in #12NM cable coming down from the roof into a phase combiner where the output will be carried by a set of #6 THHN back to the main panel with all the proper protection/equipment.Question:Am I aloud to run the phase combiner (solar output) on the same raceway as the garage feeder?I'd appreciate your comments...TIAMarcelo

Okay, Marcelo, let's break down this situation. You're essentially asking if you can run the AC output from your microinverter system in the same conduit as the feeder supplying your garage subpanel. Here's the analysis

Key Code Sections & Considerations
690.31(B) Use of non-PV system raceways. This is the section you're looking at, and it specifically addresses DC PV circuits. You are correct in that this section directly doesn't apply because you're dealing with AC output from microinverters, not DC. 300.3 (C) Conductors of Different Systems. This is the more relevant section. It generally prohibits conductors of different systems from occupying the same raceway, cable, or enclosure unless specifically permitted elsewhere in the Code. 300.3(C)(1) Voltage Considerations When you consider running AC from the microinverters in the same raceway as the garage sub panel feeder, you will also need to consider voltage. if the the Garage sub panel is being fed with a 120V/240V and the microinverters are wired for 208V, for example, this will be a violation. 230.7 External Conductors This section addresses service-entrance conductors, and it only applies if the garage is considered a separate building (detached garage). 310.15(B)(3) Adjustment Factors This is IMPORTANT. If you run additional conductors in the conduit, you have to consider ampacity derating due to conductor fill. Adding more current-carrying conductors to the conduit will require you to reduce the allowable ampacity of all conductors in the conduit. You may need to upsize your conductors for BOTH the garage feeder AND the solar output. Physical Space

Can you physically fit the additional conductors within the conduit, adhering to conduit fill limitations (Chapter 9, Table 1)?

Local AHJ Interpretation

This is always the biggest wildcard. Some inspectors are very strict about separation of systems, even when the NEC technically allows it. A preemptive discussion with your local electrical inspector can save you a lot of headaches.

Analysis and Answer


Based on the above considerations, here's a structured response:1. 690.31(B) is
not the governing section here. Because you're using microinverters, your PV system output is AC, not DC.2. 300.3(C) IS the governing section. This means you can only mix conductors in raceways if it is specifically permitted within NEC.3. It may be technically permissible, but possibly impractical. Technically, if all the AC output is in same voltage and phase, AND you can adhere to all derating and fill requirements, AND the AHJ allows it, it might be permissible. HOWEVER, the likelihood of the AHJ accepting this is very minimal.4. Best Practice: Separate Raceways. The safest and most code-compliant approach is to run a completely separate conduit for the solar AC output. This avoids any ambiguity, simplifies inspection, and eliminates potential derating issues.5. 230.7 External Conductors

This addresses situations where you have conductors run across the
exterior of a building.

Recommendation
Strongly consider running a dedicated conduit for your solar AC output. This is the simplest, safest, and most likely to be approved solution. It avoids all ambiguity and potential conflicts. If you are insistent on using the existing conduit, have a very detailed discussion with your local electrical inspector before starting any work. Present your plan, explain your reasoning, and be prepared to justify your approach with the relevant code sections. Get their approval in writing, if possible. Be ready to upsize the conductors. Calculate the conductor fill and ampacity derating meticulously. Document your calculations to show compliance. Consider the future. Are there plans to expand the PV system or the garage load? A dedicated conduit provides more flexibility for future expansion.In summary, while it's theoretically possible to use the existing conduit, it's likely more trouble than it's worth. Separate raceways offer a cleaner, simpler, and more easily approved solution.

Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. Always consult with a licensed electrician for any electrical work.* Flag for review