User: mcsolar, Location: San Diego, CA, USA
Asked on: Thursday, September 19, 2024 at 3:36 pm EDT
Answered on: Thursday, March 6, 2025 at 2:40 am EST
Question: Greetings,Ugghh, I just completed my first main panel replacement - it's outdoors, on the side of a house, and required splicing to extend conductors to the new main panel that was placed 3' from the original location ...inspector came out and didn't like that I spliced conductors inside of wall (conductors required to be in raceway and splices need to be accessible) and I thought he suggested that I chip out the stucco (to access some of the conductors that will then enter the box from the rear), place a 12x12" box and splice inside of the box and then run Romex in the wall and into MSP ...so I installed 3 outdoor NEMA 3R metal surface mount junction boxes, kind of semi-flushed them (chipped away stucco, brought conductors in from the back, and mounted boxes through the back of the box straight to the studs), made all splices inside, and ran the romex to the MSP. 3 boxes in 3 different locations with a total of 20 circuits..Obviously, I mis-understood his instructions - Inspector came back out and left a note "surface mount type cannot be flanged properly to insure no water intrusion into structure"Searching for outdoor junction boxes w/flange and coming up empty .. any ideas on what I was supposed to do in the first place, and what I can do about it now?
Okay, this sounds frustrating! Let's break down the issues and figure out some solutions.
Understanding the Inspector's Concerns (and Why You're Having Trouble Finding Flanged Boxes) In-Wall Splices are a No-Go
You correctly identified this as the core issue. The NEC (National Electrical Code) mandates that splices must be accessible for inspection and maintenance. This means they can't be buried behind walls without access.
Raceway Requirement Inside the Wall (Likely)
Depending on your local codes and what's behind that stucco, you may need to protect the wires inside the wall. This generally means running them through conduit (EMT, PVC, etc.).
Water Intrusion is the Killer
This is the crux of the current rejection. Outdoor installations are all about preventing water from getting into the electrical system and, critically, into the building structure itself. Water in the walls leads to mold, rot, and potential structural damage.
Why No Flanged Boxes? You're not finding "flanged outdoor junction boxes" because that's not generally the right approach for this situation. The problem isn't the box itself, but how it's sealed to the building surface especially when surface is not smooth.
Mismatched Instructions (Most Likely)
It sounds like you interpreted the inspector's verbal feedback, and that the interpretation wasn't quite right. This is extremely common, especially when dealing with complex electrical work.
What You Likely Should Have Done (Based on the Inspector's Initial Suggestion)
Here's what the inspector probably intended (and what is generally considered best practice):1.
Access the Wires
Chip away enough stucco around the existing wire entry points to work comfortably.2.
Mount a Suitable Outdoor Junction Box
Use a NEMA 3R or 4 (weatherproof or watertight) surface-mount junction box. Important features:
Size
Big enough to accommodate all the splices with proper wire bending space. Use wire fill tables to get the proper dimensions for the box. (wire fill tables are available at your local electrical supply store or online).
Material
Metal (steel, aluminum, or stainless steel) or non-metallic (PVC, fiberglass). Metal boxes must be grounded.
Hubs/Connectors
Use appropriate NEMA 3R rated conduit hubs or connectors to enter the box.3.
Seal the Box Properly to the Wall
This is the KEY to the inspector's current rejection.
Backer Board
Attach a backer board (plywood or composite material) to the stucco around each location using construction adhesive and screws. Be sure the fasteners are suitable for going into the studs.
Seal Backer Board
Caulk or otherwise seal the edges of the backer board to the stucco to prevent water intrusion behind the board.
Mount J-Box to Backer Board
Attach the j-box to the backer board.
Caulk J-Box
Caulk the perimeter of the j-box where it meets the backer board.4.
Splice Inside the Box
Make all your wire splices within the junction box using approved methods (wire nuts, crimp connectors, etc.). Make sure the splices are neat and organized.5.
Conduit to Main Panel
Run conduit (EMT or PVC, as required by local code and aesthetic preference) from the junction box to the main panel.
Conduit Connectors
Use appropriate NEMA 3R rated conduit connectors to enter both the junction box and the main panel.6.
Romex is Not Allowed
Romex, aka NM-B cable, is not rated for exterior use and cannot be exposed to the elements.
What to Do Now to Pass Inspection (The Most Likely Solution)
STOP
Don't do any more work without talking to the inspector again. Call them and explain that you misunderstood the initial instructions and want to clarify the correct approach. A little humility goes a long way.2.
Get Specific Guidance
Ask the inspector specifically what they want to see in terms of sealing the boxes to the stucco. What type of sealant and flashing is required?3.
Implement the "Properly Sealed Box with Conduit" Method
Follow the steps I outlined above: Remove the boxes you installed. Repair the stucco, or cover with a backer board. Install properly sized j-boxes, mounting to backer board as described above. Seal the boxes to the wall properly. Run conduit from the boxes to the MSP.4.
Document Everything
Take photos of each step of the process. This can be helpful if you need to show the inspector what you've done.
Important Considerations
Local Codes
Always defer to local codes and the inspector's interpretation. They have the final say.
Bonding/Grounding
Make sure all metal boxes, conduit, and the main panel are properly bonded/grounded according to code.
Wire Fill
Be meticulous about wire fill calculations for the junction boxes. Overcrowding is a common violation.
Professional Help
If you're feeling overwhelmed, don't hesitate to consult with a licensed electrician. It might be worth the cost to have them review your work or even take over the project.
In summary, your biggest issue is preventing water intrusion. Focus on creating a watertight seal between the junction boxes and the wall using backer board and caulk, and run conduit to the main panel. Talk to the inspector to get specific guidance on their requirements.Good luck! Flag for review