Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Class 1 Division 2 control panel 120VAC supply feed

User: Moistness, Location: PA

Asked on: Thursday, September 19, 2024 at 3:57 pm EDT
Answered on: Thursday, March 6, 2025 at 2:40 am EST

Question: I've been researching the use of fuses in a C1D2 area and concluded that you can use current-limiting class CC fuses among other current-limiting fuses but for the sake of this question, let's stick with class CC fuse in a non-indicating fuse holder, like the Allen Bradley FB series.I found this link that talks about the fuses: http://www.littelfuse.com/~/media/f...littelfuse-fuses-nec-class-1-division-2-c.pdf.Also for the sake of this question, this panel is fed from a 20A circuit from a lighting panel in a safe area, and all of the proper installation guidelines for a C1D2 area are met, and I have a C1D2 rated enclosure, (NEMA4X Stainless Steel).My question is, can I have the line side of the fuse holder with a 20A Class CC current-limiting fuse be the landing point of the "hot" conductor?Also, this 20A fuse will distribute 120V to other lower ampacity fuses that will protect equipment like 24VDC and PLC power supplies.Hopefully, this makes sense.I appreciate the advice.

Yes, you can use the line side of a Class CC fuse holder (like the Allen-Bradley FB series) with a 20A Class CC current-limiting fuse as the landing point for the "hot" conductor coming from your 20A circuit in the safe area, provided all conditions are met for Class I, Division 2 locations and specifically for the chosen equipment.

Here's a breakdown of why, and important considerations: Fuse Suitability

Class CC fuses
are recognized for use in Class I, Division 2 locations under specific conditions. The Littelfuse document you linked to confirms this, as do other fuse manufacturers. However, the entire assembly (fuse and fuse holder) must be suitable for the environment.

Fuse Holder Suitability

This is the crucial part. While the fuse itself might meet the performance requirements for a C1D2 area (current limiting being a key factor in reducing spark potential), the fuse holder is equally important. The Allen-Bradley FB series fuse holders are general purpose fuse blocks. Unless the fuse holder is explicitly marked and rated for use in Class I Division 2 environments, it's

not
considered intrinsically safe or non-incendive. The concern is with potential arcing during fuse replacement. Wiring Methods

The wiring methods used to connect to the fuse block
must comply with NEC Article 501.10(B), which covers wiring in Class I, Division 2 locations. This usually means using rigid metal conduit (RMC), intermediate metal conduit (IMC), or Type TC-ER cable with suitable fittings. Ensure proper sealing and termination.

Enclosure Type

The NEMA 4X stainless steel enclosure is a good starting point, but ensure its suitability for the specific flammable gas or vapor present in your Division 2 location. Check the enclosure's markings and certifications carefully.

Downstream Fuses

Protecting lower-amperage circuits (24VDC and PLC power supplies) with properly sized Class CC fuses is a standard and acceptable practice. Ensure these fuses are also appropriately rated for the equipment they protect and are housed within the same C1D2 rated enclosure.


Documentation is critical

You need to have documentation proving that the chosen fuse and fuse holder is suitable for the Class I Division 2 environment. This documentation is typically provided by the manufacturer. Make sure to keep this documentation readily available for inspection.

Important Considerations and Next Steps


Consult the Fuse Holder Manufacturer

The definitive answer on whether the Allen-Bradley FB series fuse holder is suitable for your specific C1D2 application can only come from Allen-Bradley (or your specific manufacturer of the fuse holder). Contact their technical support or engineering department and provide them with your Class I, Division 2 area details (specific gas or vapor present) to get a definitive answer on the suitability of the FB series. Do not assume it's acceptable without confirmation. Look for marking on the component that indicates it has been tested and approved for use in a Class 1 Division 2 environment.2.

Review NEC Article 501

Carefully review NEC Article 501 (specifically 501.10(B) for wiring methods, and the rest of the article as it relates to equipment in Class I, Division 2 locations).
3.


Consider Alternatives

If the Allen-Bradley FB series is not rated for C1D2, investigate fuse holders that are specifically designed and rated for hazardous locations. These may be more expensive, but are necessary for code compliance and safety. Look for fuse holders that are intrinsically safe or non-incendive.4.

Seek Expert Consultation

It's highly recommended to consult with a qualified electrical engineer with expertise in hazardous location electrical design. They can review your design, ensure compliance with all applicable codes and standards, and provide valuable insights. A PE stamp is necessary.5.

Labeling

Ensure that all equipment within the C1D2 enclosure is clearly labeled to indicate its suitability for the hazardous location.

In summary, while Class CC fuses can be used in Class I, Division 2 locations under certain conditions, the biggest uncertainty lies in the suitability of the fuse holder. You MUST verify the fuse holder's rating with the manufacturer or replace it with one specifically designed and approved for C1D2 applications.
Flag for review

Previous Question Next Question