User: DC_Brad, Location: California
Asked on: Thursday, September 19, 2024 at 8:10 pm EDT
Answered on: Thursday, March 6, 2025 at 2:40 am EST
Question: My client has a 20kW UPS (208/120V, 3 phase) currently installed. The recommended overcurrent protection for the 20kW UPS is a 90A breaker. My client would like to upsize the UPS to 40kW (recommended input breaker for the 40kW UPS is 175A), but he wants to run the new 40kW UPS with the existing 90A feeder. The wire connected to the 90A breaker is properly sized per the NEC. My client will upgrade the input breaker and wire to 175A sometime next year once he has the budget. The UPS can be set to alert my client when is starts to approached the rating of the 90A breaker. If the UPS were to be overload the input breaker would trip. Is their any reason (per the NEC) my client cannot run his 40kW UPS on the 90A breaker? Again, the wire is properly sized for the 90A breaker per the NEC. Any NEC sections that show this is allowed would be appreciated.
Okay, let's break down the NEC implications of running a 40kW UPS (requiring a 175A breaker) on an existing 90A circuit. The short answer is, this is generally not permitted by the NEC. Here's why, along with the relevant NEC sections
NEC Concerns & Why It's Problematic
1. Overcurrent Protection Mismatch
The primary function of overcurrent protection (circuit breakers) is to protect the conductors (wires) and the equipment connected to them. Your client is proposing to connect equipment rated for 175A to a circuit protected at 90A. This creates a situation where the UPS can draw more current than the circuit is designed to safely handle for extended periods.
NEC 110.3(B) Installation and Use
"Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling." The UPS manufacturer requires a 175A breaker. Using a 90A breaker violates this fundamental rule.
NEC 240.3 Protection of Conductors
"Conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities as specified in 310.15, unless otherwise permitted or required in 240.4(A) through (G)." You've stated the wire is sized for 90A, which is good for the wire, but it doesn't address the issue of the UPS needing 175A protection.
NEC 240.4 Protection of Equipment
This section requires that equipment be protected against overcurrent. While you could argue that the 90A breaker provides some protection, it's not the correct level of protection as specified by the UPS manufacturer's listing and instructions. If the UPS has an internal fault and draws, say, 150A, the 90A breaker might not trip quickly enough to prevent damage to the UPS. More importantly, you'd be operating the UPS in a manner it wasn't designed for, potentially causing internal stress and reducing its lifespan.2.
Potential for Undetected Overloads
While the UPS can alert your client to approaching the 90A limit, relying solely on this is risky. What if the alarm fails? What if someone ignores it? What if there's a sudden transient overload that doesn't trigger the alarm fast enough? The primary protection must be the overcurrent device (the breaker).3.
Nuisance Tripping
Even if the UPS never intentionally draws more than 90A under normal operation, the inrush current when the UPS switches to battery during a power outage, or other transient events, can easily cause the 90A breaker to trip unnecessarily. This defeats the purpose of having a UPS in the first place. You may be okay for months but there could be one little spike or inrush that pushes the 90A breaker over it limit and cause it to trip.
Why This Is NOT Like Motor Protection
Someone might try to argue that this is similar to motor protection, where the breaker is sometimes oversized to handle inrush current. However, this isn't a motor. The UPS manufacturer has specifically stated the required breaker size. You can't override that requirement based on a general understanding of electrical principles.
Why Waiting for the Upgrade Is the ONLY Safe and Code-Compliant Solution
The proper and NEC-compliant approach is to wait until the 175A breaker and appropriately sized conductors are installed before energizing the 40kW UPS. This is the only way to ensure the system is safe and meets code requirements.
In summary: You are asking to operate a 40kW UPS outside of its designed specification. This can damage the UPS and is a code violation. Flag for review