Topic: How do you prefer sizing your cable when you have a frame breaker with a small trip sensor setting?

User: Cartoon1, Location: Florida

Asked on: Friday, September 20, 2024 at 8:48 am EDT
Answered on: Thursday, March 6, 2025 at 2:41 am EST

Question: This is an optional type question. How do you like to typically size your cable when you have an example of a 150A frame breaker with a sensor trip at 100A. Do you size your cable per the frame or do you usually do per the trip? I like to do per frame but i get pushback sometimes to do per sensor.

Okay, this is a common point of discussion in electrical design, and there's not a single "right" answer without considering the specific application and local codes. Here's a breakdown of my typical approach and the reasoning behind it

My Preference: Size for the Frame (with considerations)

Generally, I prefer to size conductors based on the frame size of the breaker (150A in your example), but with caveats, and being prepared to justify it. Here's why: Future-Proofing

The frame size represents the maximum
potential capacity of the breaker. Sizing for the frame allows for future upgrades or changes to the load without requiring a complete conductor replacement. Let's say the load eventually does require a 120A or 130A trip. If you sized only for the 100A trip initially, you'll need to replace the conductors.

Thermal Capacity

The breaker's frame is designed to dissipate heat related to the current flowing through it. Even if the trip is set at 100A, the conductors connected to a 150A frame are still subjected to some degree of heat from the breaker itself, especially during overloads. Sizing for the frame provides a larger thermal margin.

Voltage Drop

Sizing for a larger amperage (even if not currently utilized) often results in a larger conductor size, which inherently reduces voltage drop. This can be beneficial, especially over longer runs.


Standard Practice (in some industries)

In certain industries (e.g., industrial plants, large commercial facilities), sizing to the frame is often a standard practice, especially when dealing with motor circuits or other loads that might be upgraded in the future.

Safety margin

Provides a built in safety margin in case of error.

Arguments for Sizing to the Trip (100A)



Cost

Using smaller conductors saves money on materials and labor. This is the biggest driving factor.

Code Compliance

Technically, the NEC (National Electrical Code in the US, or your local equivalent) typically requires conductors to be sized no less than 125% of the continuous load they will carry, and to have an ampacity equal to or greater than the overcurrent device protecting them (with some exceptions). If the actual continuous load is well below 100A, and you properly apply the 125% rule, sizing for the 100A trip can be code-compliant.

Easier Installation

Smaller conductors are easier to pull, bend, and terminate, leading to faster installation times.

Panel Space

Smaller conductors take up less space in panels and wireways, which can be a factor in densely packed installations.


Less weight

Weight can be a very important factor in electrical installations.

How to Handle the Pushback


Understand the Motivation

Find out why the other party is pushing for sizing to the trip. Is it purely cost? Are there space constraints? Once you understand their concerns, you can address them more effectively.2.

Present a Cost-Benefit Analysis

Prepare a clear comparison of the costs and benefits of both approaches. Quantify the difference in material costs, labor costs (if any), and potential future costs associated with upgrading conductors.3.

Emphasize the Long-Term View

Highlight the potential for future upgrades and the cost savings associated with not having to replace conductors later. "We might only need 100A now, but if we increase the machine's capacity in 5 years, we'll be glad we sized the conductors for the 150A frame."4.

Consider the Application

What is the load? Is it likely to change? Is it critical? For example, a critical motor circuit in a manufacturing plant might warrant sizing for the frame, while a lighting circuit in an office might not.5.

Check Local Codes and Regulations

Ensure that both approaches are code-compliant in your jurisdiction. Sometimes, local amendments to the NEC or other regulations might influence the decision.6.

Document Your Reasoning

Whatever approach you choose, clearly document your reasoning in the design drawings and specifications. This is crucial for future reference and liability protection.7.

Compromise (If Necessary)

In some cases, a compromise might be possible. For example, you might size the conductors based on a slightly larger trip size than currently needed, but still smaller than the full frame rating.

Example of How to Present Your Argument

"I understand the concern about cost, and sizing to the 100A trip will save some money upfront. However, I'm recommending sizing to the 150A frame for these reasons:

Future-Proofing

This allows for a potential increase in load up to 150A without requiring a complete conductor replacement, saving significant costs in the long run.


Voltage Drop

The larger conductors will help minimize voltage drop, especially on this long run, ensuring reliable operation of the equipment.

Thermal Capacity

The larger conductors provide a greater thermal margin, increasing the reliability and lifespan of the installation."

Important Considerations



NEC 240.4(B) (US Code)

This section of the NEC allows you to use the "next higher standard overcurrent device rating" if the conductor ampacity (after all derating factors) doesn't correspond to a standard breaker size. However, this doesn't automatically mean you should use the frame size. It just gives you some flexibility.

Derating Factors

Always remember to apply all applicable derating factors for ambient temperature, conduit fill, etc., when determining the required conductor ampacity.


Continuous Load

Carefully determine the continuous load (a load that operates for 3 hours or more at a time) and apply the 125% rule accordingly.

In Conclusion:


Sizing for the frame offers future-proofing and a larger safety margin, but it comes at a higher initial cost. Sizing for the trip is more economical upfront but may require future upgrades. The best approach depends on the specific application, budget constraints, and risk tolerance. Be prepared to justify your decision with a well-reasoned and documented argument. Always prioritize safety and code compliance. Flag for review