Topic: LFMC into a RGS coupling under 2”?

User: Isaiah, Location: Baton Rouge

Asked on: Friday, September 20, 2024 at 9:31 am EDT
Answered on: Thursday, March 6, 2025 at 2:41 am EST

Question: Our inspector is telling us you can’t connect LFMC directly into a rigid galvanized steel coupling unless it’s 2” or larger. Has anyone heard of this?

Your inspector's statement is incorrect based on the NEC (National Electrical Code). There is no size restriction regarding connecting LFMC (Liquidtight Flexible Metal Conduit) directly into a rigid galvanized steel (RGS) coupling.Here's a breakdown of why the inspector is wrong and what the NEC actually says: NEC Doesn't Restrict by Size

The NEC doesn't place restrictions on connecting LFMC to RGS couplings based on size. The primary concerns are proper installation and the use of listed fittings.


Proper Fittings are Key

The most important aspect is using the correct, listed fittings designed for the specific purpose. You need to use a fitting that is specifically listed to connect LFMC to RGS. These fittings typically have: A thread to screw into the RGS coupling. A compression or other mechanism to securely grip and seal the LFMC.

Listing & Labeling

The fittings
must be listed and labeled for the application. The listing will indicate that the fitting is suitable for connecting LFMC to rigid conduit.

Installation Instructions

Always follow the manufacturer's installation instructions for the fitting. Proper tightening is essential for a watertight connection.

Common Practices

It's very common and acceptable to connect LFMC to RGS couplings in various sizes (less than 2", 2", or larger) as long as the correct listed fitting is used and installed properly.

Why the Inspector Might Think That

It's possible the inspector is confusing this with a different situation, or perhaps misinterpreting a specific local code or specification. Here are some possibilities:


Confusion with Other Conduit Types

They might be thinking of a restriction that applies to other types of conduit, like EMT (Electrical Metallic Tubing), or specific applications.

Local Amendments

While rare, some local jurisdictions might have amendments to the NEC. It's worth checking for local code variations.


Misunderstanding of the Code

Inspectors are human and can sometimes make mistakes or have differing interpretations.*

Specific Project Specifications

There might be project-specific requirements that are more stringent than the NEC. Review the project drawings and specifications carefully.

What You Should Do


Politely Challenge the Inspector

Ask the inspector to provide the specific NEC code section or local amendment that supports their claim. Document this conversation.2.

Show the Listed Fitting

Present the listed fitting you are using and point out its listing information (UL, ETL, etc.) that indicates it is suitable for connecting LFMC to rigid conduit.3.

Consult with the Authority Having Jurisdiction (AHJ)

If the inspector remains unconvinced, escalate the issue to a higher-level authority within the inspection department (AHJ). They can provide a definitive interpretation of the code.4.

Get a Second Opinion

Consult with another licensed electrician or electrical engineer who is familiar with the NEC and local codes. They can provide an expert opinion to support your case.5.

Document Everything

Keep detailed records of all conversations, inspections, and findings. This documentation can be helpful if you need to appeal a decision.

In conclusion, you are likely correct that there is no size limitation in the NEC on connecting LFMC directly into a rigid galvanized steel coupling, as long as you use the appropriate, listed fittings and follow the manufacturer's instructions.