Question: Is there a specific guidline that requires bonding for counduit and cable tray? There is some verbiage regarding verify that the bonding is intact with the conductors but I did not see the above mentioned.
You are right to be cautious and look for specific language. The requirements for bonding conduit and cable tray are found within the National Electrical Code (NEC), primarily in Article 250: Grounding and Bonding. While there isn't a single section titled "Bonding of Conduit and Cable Tray," the requirements are spread across several subsections and depend on the specifics of the installation.Here's a breakdown of the key areas in the NEC that address conduit and cable tray bonding: Conduit Bonding
250.92 Equipment Bonding Jumpers
Requires bonding to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed. This often involves bonding locknuts, bonding bushings, or other listed fittings.
250.96 Bonding Other Enclosures and Raceways
This section addresses metallic enclosures and raceways that are likely to become energized. It generally requires that they be bonded to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed.
250.102 Installation
Specifies how to properly install bonding jumpers, ensuring a secure connection.
300.10 Electrical Continuity of Raceways and Enclosures
Raceways must be mechanically secured to boxes, fittings, cabinets, and other enclosures.
300.12 Mechanical Continuity - Raceways and Cables
Raceways are required to be installed as a complete system.
Cable Tray Bonding
392.7 Bonding
This is the key section for cable tray bonding. It explicitly requires cable trays to be bonded in accordance with Article 250. This includes ensuring electrical continuity and the capacity to conduct safely any fault current likely to be imposed.
392.7(A) Metallic Cable Trays
Requires metallic cable trays that contain equipment grounding conductors to be electrically continuous through the use of bolted connections, bonding jumpers, or other approved means.
392.7(B) Nonmetallic Cable Trays
Nonmetallic cable trays must have a separate equipment grounding conductor installed within the tray.
392.3 Minimum Size of Equipment Grounding Conductors
This clarifies the required minimum sizes for bonding conductors in cable tray applications, referencing Table 250.122.
Key Concepts to Remember
Electrical Continuity
The goal is to create a continuous, low-impedance path for fault current to return to the source. This is essential for the proper operation of overcurrent protective devices (circuit breakers, fuses).
Fault Current
This is the high current that flows during a short circuit or ground fault. A properly bonded system can safely conduct this current.
Equipment Grounding Conductor (EGC)
The EGC is the conductor used to connect normally non-current-carrying metal parts of equipment to the system grounded conductor, the grounding electrode conductor, or both. Cable trays and conduit often serve as, or supplement, the EGC.
Bonding Jumper
A reliable conductor used to ensure the required electrical conductivity between metal parts required to be electrically connected.
Where to Look for Specifics
Read Article 250 in its entirety to understand the underlying principles. Consult Article 392 specifically for cable tray requirements. Look at the product listings and instructions for the conduit, cable tray, and associated fittings you are using. These often specify how to properly bond the components. Refer to Table 250.122 for conductor sizing. Local codes and amendments may add additional requirements.
In summary, while there is no single section labeled "Bonding of Conduit and Cable Tray", the NEC provides very specific requirements that mandate bonding to ensure electrical safety. Look to Articles 250 and 392, as well as manufacturer's instructions, for proper implementation.Disclaimer: I am an AI chatbot and cannot provide electrical code interpretations. Consult with a qualified electrical inspector or engineer for definitive guidance on NEC compliance. Flag for review