Topic: Al Feeders

User: Alwayslearningelec, Location: NJ

Asked on: Friday, September 20, 2024 at 10:41 am EDT
Answered on: Thursday, March 6, 2025 at 2:41 am EST

Question: First time I have comoe across this in spec. I think I'm going to price the AL conductors but the conduits/conductor sizes on the riser are based on Cu.I know I will now have ot upsize the wire and conduit and keep in mind VD. Any suggestion for best way to go about this? I assume there could be a decent saving that could win me the job. Below is the extent of the feeder work. Maybe it won;t make that much of a diffference and I should bid it as designed.

Okay, let's break down how to handle this situation and make an informed decision about pricing and bidding. You're right to investigate aluminum as a potential cost-saving alternative to copper, but it needs to be done correctly and safely.1. Understand the Situation & Gather Information Original Design

Document everything about the original design using copper conductors. This is your baseline. Note the following:


Feeder Size(s)

The exact copper conductor size(s) specified (e.g., #4/0 Cu, 250 kcmil Cu).

Conduit Size(s)

The conduit size(s) associated with each feeder.


Feeder Length(s)

Accurate measurements of the feeder run distances. This is crucial for voltage drop calculations.

Load(s)

The ampacity requirements of the loads being served by each feeder. This will drive the minimum conductor size you can use. Ideally, you have the actual connected load. If not, use the designed or calculated load from the electrical drawings.


Voltage

The system voltage (e.g., 480V, 208V).

Number of Conductors

Number of current carrying conductors and grounds.


Installation Method

Note what type of conduit is to be used (PVC, RMC, EMT).

Specifications

Carefully review the project specifications for any restrictions or requirements related to:


Aluminum Conductors

Are they permitted at all? Some projects explicitly forbid aluminum.

Conductor Type

Is there a specific type of aluminum conductor required (e.g., AA-8000 series aluminum)?


Terminations

Are there any specific requirements for termination methods or materials used with aluminum conductors?

Voltage Drop Limits

What's the maximum allowable voltage drop specified for the feeders? (Typically 3% for the feeder plus 2% for the branch circuit.)


Grounding

Grounding requirements for Aluminum conductors may differ from copper.

AHJ Approval

Is pre-approval from the Authority Having Jurisdiction (AHJ) required for substitutions?


Equal or Better

Understand any "equal or better" clauses. You'll need to prove your proposed aluminum system meets or exceeds the copper system's performance and safety.

2. Aluminum Upsizing Calculations
Ampacity

Use the NEC (National Electrical Code) Table 310.16 (and associated correction/adjustment factors) to determine the
minimum aluminum conductor size that has an ampacity equal to or greater than the original copper conductor. Remember to apply derating factors for:

Ambient Temperature

If the installation environment has an ambient temperature above 30°C (86°F), you'll need to derate the conductor's ampacity.

Number of Conductors in Conduit

If you have more than three current-carrying conductors in a raceway, you'll need to apply a derating factor.


Other Derating Factors

Consider any other derating factors that might apply based on the installation conditions.

Voltage Drop

This is critical! Use a voltage drop calculator (many are available online for free) or the NEC voltage drop formula to calculate the voltage drop for the proposed aluminum conductor size
at the full load. Make sure it's below the specified limit (or, if no limit is specified, use a reasonable guideline like 3%). You'll likely need to iterate – starting with the ampacity-equivalent size and increasing it until the voltage drop is acceptable. The online calculators require the conductor length, load (Amps), voltage, conductor type, and power factor.

Aluminum has higher resistance than copper.
You WILL need to upsize more for voltage drop. Grounding Conductor

Check NEC 250.122 to ensure the equipment grounding conductor is properly sized. Aluminum grounding conductors are often smaller than the phase conductors, but follow the NEC table.


NEC Table 8

Check the AC Resistance and Reactance tables in Chapter 9 to get accurate values to use in voltage drop calculations.

3. Conduit Sizing
NEC Chapter 9, Table 4

Once you have the aluminum conductor size(s), use this table to determine the
minimum conduit size required for the number and type of conductors you'll be pulling. You must adhere to conduit fill limitations.

Consider Future Expansion

If there's a possibility of adding circuits in the future, it might be wise to slightly oversize the conduit now.

Conduit Body Sizing

When upsizing conduit, remember to also upsize conduit bodies.

4. Cost Analysis
Material Costs

Get accurate pricing for: Aluminum conductors (compare pricing from multiple suppliers). Larger conduit sizes. Connectors and termination lugs (specifically those rated for aluminum). These are different and more expensive than copper lugs. Anti-oxidant compound (required for aluminum terminations).

Labor Costs

Consider the labor impact of:
Pulling larger conductors and conduit. This takes more time and effort. Terminating larger conductors (especially aluminum). Potential increased difficulty in maneuvering larger conduit in tight spaces.

Compare the Total Cost

Carefully compare the total cost of the aluminum alternative (materials + labor) to the cost of the original copper design.

5. Termination Considerations
Aluminum-Rated Lugs

Crucially, you must use connectors and lugs that are specifically rated for use with aluminum conductors. Look for markings like "AL9CU" or "AL9CU7."

Anti-Oxidant Compound

Always apply an approved anti-oxidant joint compound to aluminum conductors before making terminations. This helps prevent oxidation and ensures a good electrical connection.


Torqueing

Proper torqueing of connections is especially important with aluminum conductors. Use a calibrated torque wrench and follow the manufacturer's torque specifications. Re-torqueing after a period of time may be required (check manufacturer instructions).

Dissimilar Metals

Be aware of corrosion issues where aluminum conductors terminate to copper bus bars or equipment terminals. Use properly rated connectors and anti-oxidant compound to minimize this.

6. Presentation to the Client
Transparency

If you decide to bid based on the aluminum alternative, clearly state this in your bid. Don't hide it.

Value Engineering Proposal

Frame it as a "value engineering" proposal, highlighting the potential cost savings while emphasizing that the aluminum system will meet or exceed all performance and safety requirements.


Technical Justification

Provide detailed calculations and supporting documentation to back up your claims about ampacity, voltage drop, and code compliance.

Warranty

Clearly state your warranty terms for the aluminum system.

When to Bid as Designed (Copper)
Small Cost Savings

If the cost savings from using aluminum are marginal after considering all factors (materials, labor, potential risks), it might not be worth the effort.

Tight Deadlines

If you're under a tight deadline and don't have time to thoroughly investigate and calculate the aluminum alternative, it's safer to bid based on the original design.


Client Preference

If you know the client has a strong preference for copper (e.g., due to past experiences or concerns about aluminum), it might be best to stick with the original design.*

Specific Requirements

If the specifications strongly favor copper or make it difficult to use aluminum, it's probably not worth the effort.

Example


Let's say the original design calls for #3/0 Cu in a feeder. The load is 175 amps, the voltage is 480V, and the feeder length is 250 feet. You check the AL wire ratings and see #4/0 AL is rated at 180 amps, which meets the minimum ampacity requirements. Then you run a voltage drop calculation with #4/0 AL. If the voltage drop exceeds 3%, you increase to 250 kcmil AL and calculate voltage drop. Repeat as needed until the voltage drop is within limits. Next, you check table 310.15(B)(3)(a) and apply the appropriate adjustment factors for the numbers of current carrying conductors in a raceway. You would then determine the conduit size required for these conductors. Finally, you would compare the cost of this design versus the original design to see if bidding using AL is worthwhile.

In summary: Thorough investigation and accurate calculations are essential before bidding an aluminum alternative. Don't cut corners. If you do it right, it can potentially save you (and the client) money, but if you do it wrong, it can lead to safety problems, code violations, and costly rework. Flag for review