User: jes25, Location: Midwest
Asked on: Friday, September 20, 2024 at 10:43 am EDT
Answered on: Thursday, March 6, 2025 at 2:41 am EST
Question: So USE wire can not be ran inside per article 338. But I see the cable offered by Southwire has a dual rating as RHH. So I can run it inside after all. Agree?
You're touching on a common point of confusion regarding USE (Underground Service Entrance) cable and its dual ratings. Let's break it down: USE Cable (General)
Typically, USE cable is not allowed for general interior wiring per Article 338 of the NEC. It's designed and listed primarily for direct burial or installation in underground raceways. Its insulation is suited for wet environments and direct contact with the earth.
Dual-Rated USE/RHH/RHW-2 Cable
Many manufacturers, like Southwire, offer USE cable with a dual or triple rating, often including RHH and/or RHW-2. This is the key.
RHH/RHW-2
These are general-purpose building wires suitable for installation in conduit, raceways, or other approved wiring methods, and often allow for the higher temperature ratings than THHN.
The Crucial Point: The Listing and Markings You CAN use it inside IF
The cable is clearly and legibly marked with BOTH USE and RHH/RHW-2 (or other appropriate interior wiring type). This marking is your proof that it meets the standards for both applications.
You MUST comply with the rules associated with that inner rating, so RHH/RHW.Therefore, your statement is potentially correct, BUT with a critical caveat
You CAN run Southwire dual-rated USE/RHH/RHW-2 cable inside a building, provided it is clearly marked with BOTH USE and RHH/RHW-2 (or appropriate interior wiring type). You must also follow the installation requirements for RHH/RHW-2 wiring within the building (appropriate conduit, support, terminations, etc.). You CANNOT run USE cable inside a building if it ONLY carries the USE marking.Important Considerations
NEC Article 338
Always refer to the latest version of the National Electrical Code (NEC) Article 338 and any applicable local codes for specific requirements in your jurisdiction. Local codes can be stricter than the NEC.
Manufacturer's Instructions
Always follow the manufacturer's instructions for installation, as they can provide additional guidance and limitations.
Inspection
The final authority on whether an installation is compliant rests with the local electrical inspector. They will verify that the cable is properly listed, marked, and installed according to code.
In summary: Don't rely solely on the "USE" designation. Look for the dual listing (USE and* RHH/RHW-2) on the cable itself. If it has both, and you install it according to the requirements for RHH/RHW-2, you're generally good to go (pending inspector approval, of course). If it only says USE, then the answer is no. Flag for review