User: SgtBOMBULOUS, Location: Eldersburg MD
Asked on: Friday, September 20, 2024 at 11:00 am EDT
Answered on: Thursday, March 6, 2025 at 2:42 am EST
Question: Hello! This will be my first post here. We recently had my house upgraded to a 400 amp service. Outside, from the overhead line, the electrician ran 350 kcmil down conduit and readied it to enter the new meter box. When the BGE contractor came, they set up the box, etc. Everything seemed great (They even replaced the service drop wire!).But then... I overheard the "boss" telling his employee "Yah gotta really dig in when you're stripping these". He removed the outer ring of wires from the 350 in order to fit the end into a 4/0 lug. He called the 350 "overkill", and said he didn't have a lug for the 350.He also left the CL200 meter unit in place. Also curious about opinions on this.So... How concerned about this should I be? When the electric inspector came, he didn't think it was the right way to do it, but said there's nothing he can do about it, and that utilities basically do whatever they want.Thanks!
Welcome to the world of home electrical upgrades! It sounds like you've got a valid concern, and it's good you're digging deeper. Here's a breakdown of the situation and how concerned you should be
The Problem: Reduced Conductor Size
The practice of removing strands from a conductor to make it fit into a smaller lug is absolutely not acceptable and is a code violation in most jurisdictions. Here's why it's bad: Reduced Ampacity
350 kcmil cable is rated for a specific ampacity (current-carrying capacity). By removing strands, you are effectively reducing the cross-sectional area of the conductor, thereby lowering its ampacity. This means the wire could overheat under a full 400A load, potentially leading to insulation damage and fire.
Concentrated Heat
The smaller area of contact between the reduced conductor and the 4/0 lug creates a "bottleneck" for current flow. This bottleneck generates heat due to resistance. This localized heating can damage the lug, the conductor, and even the meter box.
Compromised Connection
Even if the connection initially seems tight, removing strands makes the cable more susceptible to loosening over time due to vibration, temperature changes, and the dissimilar metals of the conductor and lug expanding and contracting at different rates. A loose connection is another significant fire hazard.
Code Violation
This practice almost certainly violates the National Electrical Code (NEC) and likely local electrical codes. The NEC requires connections to be made according to manufacturer's instructions and properly rated for the conductor size.
Why the Inspector's Response is Troubling
While it's true that utilities sometimes operate under different rules than general electrical contractors, this is primarily related to distribution wiring. At the service point (the connection between the utility and your home's electrical system, which includes the meter), the utility generally adheres to the NEC or a similar standard. The inspector's "hands-off" approach is concerning. It could be that they feel they have no jurisdiction over the utility, which may or may not be true depending on local regulations.
The CL200 Meter Base
A CL200 meter base is typically rated for 200 amps. This is a major issue. Your service is 400 amps, and the meter base needs to be rated for the entire service capacity.
What You Need to Do NOW
Document Everything
Take clear photos of the compromised conductor connection at the meter base. Take photos of the meter box.2.
Contact BGE (Again)
Call BGE's customer service and explain the situation calmly and clearly. Emphasize that the conductor was intentionally modified by removing strands to fit a smaller lug, and that the meter base is under-sized. State that you believe this creates a significant safety hazard. Ask to speak to a supervisor or someone in the engineering department. Document the names and dates of everyone you speak with.3.
Contact Your Local Electrical Inspector (Again)
Press the issue with your local electrical inspector. While they may feel they can't directly force the utility's hand, you should emphasize that you are concerned about safety and that the installation does not meet code. Ask them for advice on how to proceed. Show them the photos you took.4.
Consider a Private Electrical Inspector
If you're getting nowhere with the city/county inspector, consider hiring a certified private electrical inspector to evaluate the installation and provide a written report. This report will carry more weight and can be used to pressure the utility to correct the problem.5.
Consider contacting the Public Utilities Commission
This is a government body that regulates utilities. They may be able to investigate and compel the utility to fix the issues.
In summary
The compromised conductor connection is a serious problem and needs to be fixed. The CL200 meter needs to be replaced by a CL400 or higher. The inspector's initial response is inadequate. Don't let this go. This is a significant safety issue that could have dire consequences.
Important Considerations
Don't Touch Anything Yourself
Do not attempt to fix this problem yourself. You could be injured or further compromise the electrical system.
Be Persistent: Dealing with utilities and government agencies can be frustrating. Be polite but persistent in pursuing a resolution.Good luck! This might take some effort, but it's crucial to get this resolved properly. Flag for review