Topic: Wire for Control Panels

User: TwoBlocked, Location: Bradford County, PA

Asked on: Friday, September 20, 2024 at 11:01 am EDT
Answered on: Thursday, March 6, 2025 at 2:42 am EST

Question: You guys that do panel work know how nice some MTW/TFFN is that will lay wherever is is placed, but other MTW/TFFN wire is better than THHN but is still tough to manage. I've notice the nice stuff usually has silver colored markings on it, but besides that, I haven't noticed it as a specific "type" listed on the labelling. Is it brand name thing or what?So how do I ask for "The Right Stuff"?

You're right, that "lay flat" MTW/TFFN is a panel builder's dream! It definitely makes for neater and faster work. Identifying it can be tricky, and you've hit on a key observation about the markings. Here's a breakdown of what's going on and how to increase your chances of getting the good stuff

Why the Difference in Flexibility?

The flexibility comes down to a few factors: Strand Count and Strand Gauge

This is the biggest factor. More strands of thinner gauge wire make for a much more flexible conductor. The "lay flat" wire is typically a
high strand count conductor.

PVC Compound Formulation

Different manufacturers use different formulations of PVC for the insulation. Some are softer and more pliable, while others are stiffer.

Manufacturing Process

Even with similar materials, the way the wire is manufactured (extrusion, annealing, etc.) can affect the final flexibility.

Identifying the "Good Stuff"


Here's how you can increase your chances of getting the flexible MTW/TFFN:1. Focus on Strand Count

This is the most important thing. Look for MTW/TFFN specifically listed as "High Strand Count" or "Extra Flexible".
Example: Instead of just asking for "14 AWG MTW/TFFN", ask for "14 AWG MTW/TFFN High Strand Count" or "14 AWG MTW/TFFN Extra Flexible".

Look at the printed legend on the spool. It will indicate how many strands it has. Compare these numbers when you find something you like.
2. Check the UL Listing

The UL listing might not directly specify flexibility, but you can cross-reference the UL file number (printed on the wire) with UL's online database. This might give you more detailed specs.3.

The Silver Markings (Your Observation)

You're onto something here! While not a guarantee, the silver/white markings
can indicate a higher-quality, more flexible wire. It might be a brand-specific practice, but it's worth paying attention to. This could be a good way to identify wire if the print is worn or dirty.4.

Brand Preference (Personal Experience)

Once you find a brand that consistently delivers the flexibility you want, stick with it. Make a note of the brand and the specific product code. (Note that even the same brand can have different lines of MTW/TFFN, some more flexible than others.)5.

Ask Your Supplier!
This is the most direct approach. Tell them exactly what you're looking for: "I need 14 AWG MTW/TFFN that's very flexible for panel wiring. I need something with a high strand count." A knowledgeable supplier will know which brands and products to recommend.6. Feel It

If possible, before buying a whole spool, ask to see a sample and feel the wire. Bend it, twist it. You'll quickly be able to tell the difference between the stiff and flexible versions.

Specific Phrases to Use

"High Strand Count MTW/TFFN" "Extra Flexible MTW/TFFN" "Fine Stranded MTW/TFFN" (Another term for high strand count) "Panel Shop Grade MTW/TFFN" (Some suppliers might have a product specifically marketed for panel builders) "MTW/TFFN for Control Panel Wiring"

Important Considerations



Cost

Higher strand count and premium PVC compounds can mean a slightly higher price. However, the time savings and improved quality of your work will often offset the difference.


Terminal Compatibility

High strand count wire requires using the correct terminals. Standard screw terminals or back-wired receptacles may not properly grip the fine strands. You'll likely need to use ferrules, crimp-on terminals designed for fine-stranded wire, or spring-cage terminals.

In Summary:


The key is to ask specifically for "High Strand Count" or "Extra Flexible" MTW/TFFN. Combine this with your observation about the silver markings, brand preference, and a good relationship with your supplier, and you'll be well on your way to getting "The Right Stuff" for your panel work. Flag for review