User: Rock86, Location: new york
Asked on: Friday, September 20, 2024 at 12:15 pm EDT
Answered on: Thursday, March 6, 2025 at 2:42 am EST
Question: We have a client with an existing MCC and they are looking to upgrade/modify. The motors run 24/7, and only 2 groups of motors need to have A start before B. All of the motors are 208V and no larger than 10HP. There is an alarm system involved incase one of the motors fails.I have 2 primary questions...1. Is a motor control center necessarily needed for continuous on/ manual off operations, and all of the alarm equipment? (pretend you are the client, would you want one)1.a. If you don't think a MCC is needed, what would you use to trigger an alarm situation? Would you stick with a motor contactor is an aux relay just eliminate the lights and switches?2. If an MCC is need, what manufactures are helpful with equipment selections? I can do all of the calculations of the motor starter and overload device, but our office has not had to design an MCC in a long time, I assume most of you will say Allen Bradly, i am curious if there is anyone else out there.
Okay, let's address your client's MCC situation. I'll put on my client hat and give you my perspective, along with some suggestions for both MCC and alternative approaches.1. Is a motor control center necessarily needed for continuous on/ manual off operations, and all of the alarm equipment? (pretend you are the client, would you want one)
Honestly, as the client, my answer would be: "It depends. Show me the costs and benefits of both an MCC and an alternative approach. Focus on reliability, maintainability, and long-term cost of ownership."
Here's my reasoning as the client: Continuous operation is paramount. Uptime is king. Whatever solution you propose, it MUST be robust and reliable. We cannot afford frequent downtime for maintenance or repairs. Manual On/Off is acceptable. We're okay with manually starting and stopping the motors. Automated or remote control isn't a priority for us right now. Alarm system is crucial. We absolutely need a reliable alarm system to notify us immediately if a motor fails. Space and Aesthetics
How big is this MCC? Is it going to take up a huge amount of space? How about the alternative, will it be aesthetically pleasing?
Why I'm hesitant about an MCC
Cost
MCCs are generally more expensive upfront than individual starters and control components.
Complexity
While you're experienced, MCCs can be more complex to troubleshoot and modify compared to simpler systems, potentially leading to longer downtime for repairs if something goes wrong.
Overkill? If we only have a few motors and the control requirements are relatively basic, an MCC might be overkill.
Why I might be interested in an MCC
Future Expansion
Is this likely? Are we going to add more motors in the future? An MCC offers a centralized and expandable solution, making future additions easier.
Centralized Control and Monitoring
If we anticipate needing more sophisticated monitoring or control in the future (e.g., energy usage tracking, remote monitoring), an MCC could provide a better platform for integrating these features.
Safety and Standardization
MCCs offer a structured and standardized approach to motor control, which can improve safety and maintainability.
Space Savings
Depending on the configuration, an MCC can sometimes save space compared to individually mounting all the components.
1.a. If you don't think a MCC is needed, what would you use to trigger an alarm situation? Would you stick with a motor contactor is an aux relay just eliminate the lights and switches?
If I were leaning toward an alternative to an MCC, here's how I'd approach the alarm system and motor control: Individual Motor Starters with Overload Protection
Each motor would have its own NEMA-rated motor starter with properly sized overload protection (based on motor FLA and service factor). These would be mounted in individual enclosures or on a back panel within a larger enclosure.
Current Transformers (CTs)
This is my preferred method for reliable motor failure detection. Install a CT on each motor's power feed. The CT outputs a signal proportional to the motor current. This signal is fed into a current monitoring relay.
Current Monitoring Relay
This relay continuously monitors the motor current. If the current drops below a set threshold (indicating a motor failure), the relay triggers an alarm. These relays are highly reliable and can be adjusted to avoid nuisance tripping due to temporary load fluctuations.
Auxiliary Contacts on Overload Relay
Use the auxiliary contacts on the motor starter's overload relay to signal a motor trip. This provides redundancy in the alarm system.
Alarm System Interface
Connect the outputs from the current monitoring relays and overload relay auxiliary contacts to a central alarm panel. This panel can trigger audible and visual alarms, as well as send notifications via email, SMS, or other communication methods.
Hand-Off-Auto (HOA) Switches (Optional)
If you want local manual control, use HOA switches for each motor. In the "Hand" position, the motor runs regardless of external control signals. In the "Off" position, the motor is stopped. In the "Auto" position, the motor can be controlled by an external control system (if we add one in the future).
Auxiliary Relays
Use auxiliary relays to isolate the control circuitry from the alarm circuitry. This improves safety and prevents a fault in one system from affecting the other.
Interlocking for A then B
Since only two motor groups need interlocking, use a simple relay logic circuit with auxiliary contacts from motor A's starter coil to enable motor B's starter coil. This is a simple and reliable solution.
No Lights and Switches
This would be a good decision if all of the motors will always be in the ON position. This will help save cost.
Why I prefer CTs and current monitoring relays
More Reliable
More reliable than relying solely on auxiliary contacts on the overload relay. Overload relays can sometimes fail to trip, especially with slow overloads. Current monitoring is more sensitive to detecting a wider range of motor failures.
Early Warning
Current monitoring can sometimes detect problems before the overload relay trips, allowing for proactive maintenance.
Flexibility
Current monitoring relays can be adjusted to monitor various parameters, such as undercurrent, overcurrent, and current imbalance.
Important Considerations for either approach
Short-Circuit Protection
Regardless of whether you use an MCC or individual starters, ensure that each motor circuit is properly protected against short circuits with appropriately sized fuses or circuit breakers.
Coordination
Coordinate the motor starters, overload relays, and short-circuit protection devices to ensure proper selective coordination. This means that a fault on a motor circuit should only trip the breaker or blow the fuse for that specific circuit, without affecting other circuits.
Documentation
Provide complete and accurate documentation, including wiring diagrams, component specifications, and troubleshooting procedures.
2. If an MCC is needed, what manufacturers are helpful with equipment selections? I can do all of the calculations of the motor starter and overload device, but our office has not had to design an MCC in a long time, I assume most of you will say Allen Bradley, I am curious if there is anyone else out there.
You're right, Allen-Bradley (Rockwell Automation) is a dominant player in the MCC market, and they are a solid choice. However, here are some other reputable MCC manufacturers to consider: Eaton
Eaton is a major competitor to Allen-Bradley and offers a wide range of MCCs with various features and options. They are known for their quality and reliability. Their Cutler-Hammer line is well-regarded.
Schneider Electric
Schneider Electric offers a comprehensive range of electrical equipment, including MCCs. They are known for their innovative technologies and focus on energy efficiency.
Siemens
Siemens is another global leader in electrical engineering, and their MCCs are known for their quality and advanced features.
Square D (also Schneider Electric)
Square D has a long history in the electrical industry and offers a range of MCCs for various applications.
WEG
WEG is a Brazilian company that has become a significant player in the global electrical market. They offer a range of MCCs that are known for their cost-effectiveness.
Tips for working with MCC manufacturers
Provide a Detailed Specification
The more detailed your specification, the more accurate the quote and the less likely you are to have problems later. Include motor horsepower, voltage, full-load amps, service factor, and any specific control requirements.
Ask for Drawings and Submittals
Review the drawings and submittals carefully to ensure that the MCC meets your requirements.
Consider Future Expansion
If you anticipate adding more motors in the future, specify an MCC with spare capacity.
Visit the Manufacturer's Facility
If possible, visit the manufacturer's facility to see their production process and quality control measures.
Get References
Ask the manufacturer for references from other customers.
Ask about Support
Inquire about the manufacturer's level of support after the sale.
Ease of Service and Parts Availability
Inquire as to the amount of lead time on spares, as well as support after the sale.
In conclusion, as the client, I'd want you to present a clear comparison of the costs and benefits of both an MCC and an alternative approach. Focus on reliability, maintainability, and long-term cost of ownership. A good alternative with CTs and current monitoring relays might be more appropriate given the limited number of motors and relatively simple control requirements. If you are unsure of future growth and possible control systems, the MCC becomes a stronger contender. If the choice is made to go with an MCC, get quotations from at least 2 manufacturers before committing to one. Good luck! Flag for review