Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Residential protector's > 20' from service 800.100(A)(4)

User: gene6, Location: NY

Asked on: Friday, September 20, 2024 at 12:46 pm EDT
Answered on: Thursday, March 6, 2025 at 2:42 am EST

Question: Greetings Mike and grounding engineers and experts.I would like to make sure I am understanding, in plain English, what the NEC is requiring for communications grounding protectors (cable / landline phone / satellite dish / wifi antenna) where the 'primary protector' or DMARC box is located more than 20 feet from the grounding grounding electrode conductor at a two family dwelling.I am on the 2017 NEC if that matters.800.100(A)(4) Says:(4) Length. The primary protector bonding conductor orgrounding electrode conductor shall be as short as practicable.In one- and two-family dwellings, the primary protector bondingconductor or grounding electrode conductor shall be as short aspracticable, not to exceed 6.0 m (20 ft) in length.

Okay, let's break down NEC 800.100(A)(4) in plain English, specifically for your situation with a two-family dwelling and a communications primary protector (like a cable TV box, phone box, or satellite dish connection point) more than 20 feet from your main grounding electrode conductor (GEC).

The Problem

Communications equipment (cable, phone, satellite) is vulnerable to surges and lightning. To protect it, and more importantly your house and family, a "primary protector" is installed where the cable enters your house. This protector needs to be connected to ground. The NEC wants this ground connection to be as direct as possible to your main electrical grounding system.

NEC 800.100(A)(4) Explanation



"The primary protector bonding conductor or grounding electrode conductor shall be as short as practicable."
This is the general rule. You should always aim for the shortest possible path to ground for the protector. Shorter is better because it reduces the impedance (resistance to AC current, like surge energy) and makes the grounding more effective. "In one- and two-family dwellings, the primary protector bonding conductor or grounding electrode conductor shall be as short as practicable, not to exceed 6.0 m (20 ft) in length." This is the key part for you. If you have a one- or two-family house (like a duplex), the wire that connects the communications protector to ground cannot be longer than 20 feet.What happens if the protector is more than 20 feet from the main GEC? This is the critical question. The NEC effectively says you need to establish a supplemental grounding point closer to the communications protector. Here's how to interpret what to do, based on 800.100 and related sections

The Solution (Because Your Protector is Too Far Away):

Since your protector is more than 20 feet from your existing grounding electrode conductor, you must do one of the following:1. Relocate the service

If feasible, relocate the protector to within 20' of the grounding electrode conductor.2.

Supplemental Electrode System

Per NEC 800.100(D), drive a ground rod (or use another approved grounding electrode) near where the protector enters the building. You will then connect the protector to this supplementary electrode with a bonding conductor less than 20' feet in length.
3.


Bonding to the Building's Metallic Water Pipe

This is the best way to resolve the issue. Bond the protector to the nearest metallic water pipe using a conductor less than 20' feet in length. Doing this will allow the water pipe to act as a system electrode.

In Detail - Supplement Electrode Example



Drive a Ground Rod

Drive an 8-foot ground rod (or another approved electrode method, check your local codes) as close as possible to where the cable/phone/satellite line enters your house. Aim for a location within a few feet, if you can.


Size the Grounding Electrode Conductor

The grounding electrode conductor that connects the protector to the ground rod MUST be sized according to NEC table 800.100. Table 800.100 typically directs you to use at least a #14 AWG conductor. Always use NEC table 800.100 as your guide.

Connect to the Protector

Connect the protector's grounding terminal to the newly installed ground rod with the sized conductor. Keep this conductor as straight and short as possible, and it MUST be less than 20 feet.

Important Considerations



Bonding to Other Systems

If you install a supplemental ground rod, you must also bond it to your main grounding system (typically at your service panel) with a bonding jumper (NEC 250.50). This bonding jumper ensures that all grounding electrodes are at the same potential. This conductor needs to be sized in accordance with 250.53(D)(2).

Bonding is Key

The goal is to create a common ground potential. Without proper bonding to your main electrical grounding system, you could create a difference in potential between the communications ground and your electrical ground, which can be dangerous and negate the protection.


Local Codes

Always check with your local electrical inspector. They may have additional requirements or interpretations of the NEC. They have the final say!

Qualified Electrician

If you are not comfortable working with electrical grounding systems, hire a qualified electrician to do the work. This is crucial for safety.

In summary, because your communications protector is more than 20 feet from your main grounding electrode conductor, you
must* install a supplementary grounding electrode near the protector and bond the protector to it with a conductor less than 20 feet long. Then, bond this new grounding electrode back to your main electrical grounding system.


I hope this helps clarify the NEC requirements for your situation. Let me know if you have any more questions! Flag for review

Previous Question Next Question