Question: My NEW local authority member Electrical inspector has required US to drive grounding electrodes for SAW POLES. AKA construction temporary power. In my location we have used a butt ground for over 20 years due to someone driving a rod through a primary cable. Are most jurisdictions requiring ground rods on temporary saw poles?
This is a tricky question because the NEC (National Electrical Code) doesn't explicitly mandate grounding electrodes for every temporary power pole. However, it does require a grounding electrode system for a separately derived system (SDS).Here's a breakdown of the factors involved and why your inspector might be requiring this, despite your past practices
Understanding the Code & Rationale:
NEC 590.6(A): Grounding
Temporary power installations must be grounded in accordance with Article 250. This is the key provision.
NEC 250.30 Separately Derived Systems
If your temporary power is derived from a generator (which often it is on construction sites) or a transformer providing power exclusively to the temporary setup, then it's very likely considered a Separately Derived System (SDS). If so, NEC 250.30 mandates a grounding electrode system.
Why Grounding is Important
Fault Current Path
Grounding electrodes provide a low-impedance path for fault current to flow back to the source (transformer or generator). This helps overcurrent protective devices (breakers) trip quickly and clear a fault, preventing shocks and fires.
Voltage Stabilization
Grounding helps stabilize the voltage to ground, reducing the risk of voltage spikes and transients that can damage equipment.
"Butt Ground" (Neutral-to-Ground Connection at the Transformer)
This is likely what you've been doing. Connecting the neutral to ground at the transformer is necessary for an SDS, but it's not always sufficient on its own. The NEC generally requires an additional grounding electrode system.
NEC 250.30(A)(7) Grounding Electrode Conductor for Separately Derived System
Requires a grounding electrode conductor to be connected to the grounding electrode. (ground rods)
Why the Inspector is Likely Correct (But Communication is Key)
Based on the above, here's why the inspector's requirement is likely valid, assuming your temporary power is an SDS:1.
Code Compliance
The inspector is likely interpreting the NEC 590.6(A) in conjunction with Article 250, particularly 250.30, which requires a grounding electrode system (ground rod(s) or other approved means) for SDSs.
2.
Safety
The inspector's priority is safety. While you've had a long history of using a butt ground, the NEC's grounding electrode system requirements are designed to provide a more robust and reliable grounding path.3.
Local Interpretation
While the NEC is widely adopted, local authorities (AHJs - Authorities Having Jurisdiction) have the final say in how it's interpreted and enforced. Your inspector is likely following the local interpretation of the code.
Addressing the Issue and Finding Solutions
Clarify the Source of Power
The most important step is to clarify exactly how your temporary power is supplied.
If it's a dedicated transformer or generator
It's highly likely an SDS, and the inspector is likely correct.
If it's simply a tap off of the building's existing service
It might not be considered an SDS, but the inspector might still require grounding for safety reasons.2.
Talk to the Inspector
Politely discuss the situation with the inspector. Explain your past practices and the reasoning behind them. Ask for clarification on why they're requiring ground rods in your specific situation. They might be willing to discuss alternative solutions that meet the code and address your concerns about the primary cable.3.
Alternative Grounding Methods (Consult with Inspector)
Concrete Encased Electrode (Ufer Ground)
If a Ufer ground exists on the site, you might be able to use it as part of your grounding electrode system (NEC 250.52(A)(3)).
Ground Ring
A ground ring encircling the temporary power setup is another option (NEC 250.52(A)(4)).
Existing Building Steel
If the temporary power is very close to an existing building with a properly grounded steel frame, you might be able to bond to that steel.4.
Documentation
Keep meticulous records of your grounding system, including any tests performed to verify its effectiveness.5.
Address the "Rod Through Primary Cable" Issue
Call Before You Dig (811)
This is crucial every single time you drive a ground rod. Make sure all underground utilities are clearly marked.
Ground Penetrating Radar (GPR)
Consider using GPR to scan the area before driving rods, especially if you're concerned about unmarked utilities.
Manual Installation
In areas where underground utilities are a significant concern, consider manually installing the ground rods or using a less invasive method.
In summary, while you have a long history of doing it one way, code changes, interpretations, and safety concerns often lead to new requirements. Communication with your inspector is paramount. Understand the source of your power, and if it is a Separately Derived System, then he is most likely correct. Discuss your concerns and explore possible alternative grounding solutions to meet the code and ensure safety.* Flag for review