Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Duplex Service load calculations

User: Dengineer, Location: new york

Asked on: Friday, September 20, 2024 at 10:56 pm EDT
Answered on: Thursday, March 6, 2025 at 2:44 am EST

Question: Hello everyone,I’m trying to wrap my head around how to do service and feeder load calculations for duplexes, and I’d appreciate your insights.To my understanding I should calculate the load for each unit using the standard single dwelling unit method to figure out the size for the main panels. Then, I would add both load summaries I calculated from each individual unit to get the service size for the entire building. Does this make sense?Secondly, can I use 220.82 for each dwelling unit and then combine those calculations for the overall service size, assuming the main service and feeders to each unit are all over 100A?Lastly, I know about 220.85, which allows for using 220.84 for duplexes, but my project is based on the 2011 NEC.Thanks you! any help would be appreciated.

You're on the right track! Here's a breakdown, clarifying some points based on the 2011 NEC

Understanding Duplex Load Calculations (2011 NEC)

The general approach is:1. Calculate Individual Dwelling Unit Loads

Determine the load for each unit separately using the standard dwelling unit methods (Article 220 Part III). This includes:

General Lighting and Receptacle Load

Based on square footage at 3VA/sq ft (220.12).


Small Appliance Circuits

Two 20-amp circuits (1500VA each – 220.11(C)(1))

Laundry Circuit

One 20-amp circuit (1500VA – 220.11(C)(2))


Appliance Loads (Fixed Appliances)

Nameplate rating of each appliance (cooktop, oven, dishwasher, water heater, etc.) – 220.53

Electric Ranges/Cooking Equipment

Use Table 220.55 based on the total connected load. Remember the notes to Table 220.55, especially Note 4.


Heating and Air Conditioning

The larger of the heating or cooling load. (220.51) If using heat pumps, add 100% of the compressor's nameplate rating to the HVAC load.
2.


Apply Demand Factors to Individual Unit Loads

After calculating the total VA for each unit, you generally don't apply demand factors within each unit load calculation, except for specific items like ranges (Table 220.55) or similar equipment where demand factors are already built into the code. Calculate the entire load, do not use 220.82 yet.
3.


Sum the Loads

Add the loads calculated for both dwelling units after any demand factors have been applied to specific appliances (ranges, etc.) and after the calculation of each load is complete and all appliances are added for that particular unit.4.

Apply Optional Calculation (220.82 or 220.84/220.85)

Now you can apply either 220.82 (Optional Calculation for Dwelling Unit) to the total combined load, OR if you qualify under 220.85 (the Duplex Exception), you can use the simpler 220.84 method.

Addressing Your Specific Questions



Calculating Load for Each Unit and Adding

Your initial understanding is generally correct,
but be sure you're not applying demand factors prematurely within each individual unit calculation. Calculate each unit's load separately and completely first. Add them after you have a total value for each unit. Then apply 220.82 or 220.84/220.
85.


Using 220.82 Individually and Combining



This is generally incorrect and will likely lead to undersized service.
You cannot apply 220.82 to each dwelling unit separately and then add those reduced loads. 220.82 is intended to be applied to the combined load of all units after it has been calculated fully. It must be applied to the combined total after each unit has been totalled. 220.85 and 220.84

You're correct that 220.85 references 220.
84. It allows you to use the simpler 220.84 calculation for the entire duplex service if
both dwelling units are equipped with electric cooking equipment and electric space heating, or electric space heating and air conditioning. (Essentially, if they're all-electric homes). If you meet the criteria of 220.85, you can use 220.84 for the entire duplex.

Important Considerations for 2011 NEC



Feeder and Service Size

The calculated load is used to determine the minimum size of the service conductors and overcurrent protection. You must also consider voltage drop when selecting conductor sizes.

Neutral Load

Don't forget to calculate the neutral load. 220.61 allows for a demand factor on the neutral conductor.


Diversity

The optional methods (220.82 and 220.84) are based on statistical diversity. They assume that not all loads will be operating at their maximum simultaneously. This is why you can't apply them to each unit individually and add.

Example (Simplified)

Let's say after calculating the load for Unit A, you get 18,000 VA. After calculating the load for Unit B, you get 20,000 VA.1.

Total Combined Load

18,000 VA + 20,000 VA = 38,000 VA2.

Optional Calculation (220.82 Example)

First 3 kVA: 100% = 3,000 VA Next 8 kVA: 35% = 2,800 VA Remainder (27 kVA): 25% = 6,750 VA Total Calculated Load (using 220.82): 3,000 + 2,800 + 6,750 = 12,550 VA3.

Apply Demand factors to individual loads (if any),
and THEN add loads for each unit individually. Apply 220.82 or 220.84 to the total calculated load after summing loads for each individual unit.

Key Takeaway: Don't apply 220.82 to each dwelling unit separately. Calculate each unit's load completely, then sum the loads, then apply 220.82 (or use 220.84 if you qualify under 220.85).I hope this helps clarify the process. Let me know if you have any more questions. Flag for review

Previous Question Next Question