Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: CE listed IEC 60898-1 and IEC 60947-2 Curve C breakers in the USA

User: brycenesbitt, Location: United States

Asked on: Saturday, September 21, 2024 at 4:15 am EDT
Answered on: Thursday, March 6, 2025 at 2:44 am EST

Question: I'm looking to learn more about the listing requirements for breakers under the NEC.CE listed IEC 60898-1 and IEC 60947-2 mini DIN rail breakers are ubiquitous in Europe, and seen in a lot of imported equipment in the US and Canada.The breakers seem to use mostly Curve C. While NEMA AB-1 is identical to UL489, UL489 differs slightly from the ICE standards.-What NEC concerns does this bring up? NEC Section 240.2 and 90.7 and 110.3 don't seem to be very specific."equipment has been listed by a qualified electrical testing laboratory in accordance with 110.3(C)." So do these CE marked breakers count?

You've hit upon a common and important issue when dealing with imported equipment in the US governed by the National Electrical Code (NEC). Let's break down the NEC concerns related to using CE-marked IEC breakers.

Key Concerns and NEC Sections1. Listing and Suitability (NEC 110.2, 110.3(A), 110.3(B), 110.3(C), 90.7)

This is the primary concern. The NEC generally requires equipment used in electrical installations to be listed.

110.2 Approval

Equipment shall be
approved. "Approved" is defined in Article 100 and effectively requires approval by the Authority Having Jurisdiction (AHJ). This approval is often based on listing.

110.3(A) Examination

Equipment must be suitable for the voltage, current, and use for which it's intended.

110.3(B) Installation and Use

Equipment must be installed and used in accordance with any instructions included in the listing or labeling.


110.3(C) Listing

This is the crucial section. "Listed" means equipment that has been included in a list published by a qualified electrical testing laboratory (QETL) that maintains periodic inspection of production of listed equipment, and whose listing states that the equipment meets appropriate designated standards or has been tested and found suitable for a specified purpose.

90.7 Examination of Equipment for Safety

It is the intent of the NEC that factory-installed internal wiring or the construction of equipment need not be inspected at the time of installation of the equipment, except to detect alterations or damage, if the equipment has been listed by a qualified electrical testing laboratory in accordance with 110.3(C).

Do CE Marked Breakers Count? Generally, NO.
CE marking itself is a declaration by the manufacturer that the product meets applicable European directives. It is NOT equivalent to a listing by a recognized US-based QETL. While some European test labs may be recognized by OSHA as NRTLs, simply having a CE mark doesn't guarantee it meets US electrical safety standards. Why not? Different Standards

IEC standards (like 60898-1 and 60947-2) are different from UL standards (like UL 489). While there might be some overlap in certain requirements, they are not identical. The testing methods and specific performance requirements differ.


Testing Laboratory Recognition

The testing laboratory must be a QETL recognized in the US. CE marking doesn't automatically imply this recognition.

Curve Characteristics

While you mention Curve C, even the same "curve" designation might have subtle differences in tripping characteristics between IEC and UL breakers. This can impact selective coordination in a circuit.2.

Interrupting Rating (NEC 110.9, 240.86, 240.60, 110.10)

This is a
major concern. Circuit breakers must have an adequate interrupting rating to safely clear a fault.

110.9 Interrupting Rating

Equipment intended to interrupt current at fault levels shall have an interrupting rating sufficient for the nominal circuit voltage and the current that is available at the line terminals of the equipment. Equipment intended to interrupt current at other than fault levels shall have an interrupting rating sufficient for the nominal circuit voltage and the current that must be interrupted.

110.10 Circuit Impedance, Short-Circuit Current Ratings, and Other Characteristics

The overcurrent protective devices, the total impedance, the component short-circuit current ratings, and other characteristics of the circuit to be protected shall be so selected and coordinated as to permit the circuit-protective devices to clear a fault to do so without extensive damage to the electrical components of the circuit. This fault shall be cleared in accordance with all of the following:
(1) The available fault current at the line terminals of each component is not greater than the short-circuit current rating of the component. (2) The available fault current at the line terminals of each component is not greater than the interrupting rating of the interrupting device installed in the circuit ahead of the component. (3) The maximum let-through energy of the overcurrent protective device shall not exceed the thermal withstand rating of the electrical components.

Importance

If a breaker's interrupting rating is too low for the available fault current at its location, it can fail catastrophically during a fault, potentially causing fire, explosion, and injury.


IEC vs. UL Interrupting Ratings

IEC interrupting ratings are often determined using different test methods than UL. A breaker rated for a certain kA under IEC standards may not have the same performance as a UL-listed breaker with the same kA rating.3.

Overcurrent Protection Characteristics (NEC Article 240)

The NEC specifies requirements for overcurrent protection, including sizing and type.

240.1 Scope

This article provides the general requirements for overcurrent protection and details for specific installations.


240.2 Definition of Overcurrent

Overcurrent is any current in excess of the rated current of equipment or the ampacity of a conductor. It may result from overload, short circuit, or ground fault.

Concern

IEC "Curve C" breakers might not provide the same level of protection or have the same tripping characteristics as UL-listed breakers commonly used in the US. This could lead to nuisance tripping or inadequate protection.4.

Selective Coordination (NEC 700.27, 701.18, 702.16)

In some applications (e.g., emergency systems, legally required standby systems), selective coordination is required. This means that only the overcurrent device closest to the fault should trip, minimizing the impact of the fault.


IEC vs. UL Coordination

Achieving selective coordination with a mix of IEC and UL breakers can be very difficult due to differences in tripping characteristics.

What Can You Do?
1. Look for Dual Listings

The ideal situation is to find a breaker that is both CE marked and UL listed. This means it has been tested and certified to both standards. Look for the UL mark (or other QETL mark) on the breaker itself.2.

Contact the Manufacturer

Ask the manufacturer for documentation showing that the breaker meets relevant UL standards and is listed by a recognized US QETL.3.

NRTL Evaluation and Field Labeling

If you must use a CE-marked breaker that is not UL listed, you might be able to have it evaluated and field-labeled by a recognized US Nationally Recognized Testing Laboratory (NRTL). This is an expensive and time-consuming process, but it could be an option in some cases. The NRTL will perform testing to US standards to determine if the breaker is safe and suitable for its intended use.4.

AHJ Approval

Ultimately, the AHJ has the final say on whether equipment is acceptable. Present the AHJ with documentation (test reports, listing information, etc.) and explain why you believe the breaker is safe and suitable. Be prepared for them to reject the use of non-listed equipment. This is particularly important for critical applications.5.

Documentation

Maintain thorough documentation, including: Manufacturer's specifications for the breakers. Test reports (if available). Available fault current calculations for the installation location. Any evaluation reports from NRTLs. AHJ approvals (if obtained).

In Summary


Using CE-marked IEC breakers in US electrical installations governed by the NEC presents significant challenges.
Generally, CE marking alone is not sufficient to meet the NEC's listing requirements*. You must demonstrate that the breakers meet relevant UL standards and are listed by a recognized US QETL, or obtain AHJ approval through other means (like NRTL field labeling). The interrupting rating is a crucial safety factor that must be carefully considered. When in doubt, consult with a qualified electrical engineer or inspector. Flag for review

Previous Question Next Question