Topic: 600 amp service (from disconnect back through ct can to panels??)

User: ksandusky86, Location: Pierce county WA

Asked on: Sunday, September 22, 2024 at 3:02 pm EDT
Answered on: Thursday, March 6, 2025 at 2:46 am EST

Question: I am building a 600 amp service. About to install the disconnect. The picture shows a rudimentary sketch of its intended installation. Two 3 inch pvc conduits will run between the CT cabinet and the disconnect housing the feeders that run in and out of the disconnect. (thats the meter in the middle). My question is, after the feeders exit the disconnect can they re_enter the CT cabinet? Then proceed through the back of the CT cabinet to enter the panels??

Okay, let's break down your situation with the 600 amp service and the potential re-entry of the feeders into the CT cabinet. The short answer is YES, you can re-enter the CT cabinet.

Here's a more detailed explanation, incorporating code considerations and best practices


General Feeder Routing



From Disconnect to CT Cabinet to Panels

Yes, it's a common and generally acceptable practice to run feeders from the load side of the disconnect, back into the CT cabinet, and then from the CT cabinet to your distribution panel(s). The CT cabinet becomes essentially a large junction/pull box in this scenario.


Code Compliance

Make sure all work conforms to the current edition of the National Electrical Code (NEC) and any local amendments. The NEC addresses feeder installations extensively.2.

Critical Considerations and NEC References



Working Space (NEC 110.26)

This is
extremely important. The CT cabinet must have sufficient working space in front of it to meet the NEC requirements based on the voltage to ground and the available fault current. Having wires and conduits exiting the back of the CT cabinet makes this especially important, as it can impede access and movement during maintenance or emergencies. Consider the depth, width, and height requirements for working space. The depth is most critical because the rear wall will impact accessibility.

Enclosure Size & Fill (NEC 314)

The CT cabinet must be large enough to accommodate all the conductors, splices (if any), and conduits entering and exiting it
without exceeding the fill limits specified in NEC 314. This includes adequate space for bending radii and heat dissipation. Carefully calculate the conductor fill. Use the conduit fill tables in Chapter 9 of the NEC. Overfilling can lead to overheating and is a code violation. Consider derating factors if there are more than three current-carrying conductors in a raceway (NEC 310.15(B)(3)).

Insulation & Termination Temperature Ratings (NEC 110.14(C))

Ensure the terminals of the disconnect, CT cabinet, and panels are rated for the temperature of the conductors used. This is usually 75°C or 90°C.

Clear Identification and Labeling (NEC 110.21 and Article 408)

Clearly identify all feeders, panels, and the disconnect. This is crucial for safety during maintenance or troubleshooting. Proper labeling helps prevent accidental disconnections.


Secure and Support (NEC 314.23, 300.11)

All conduits and enclosures (CT cabinet, disconnect) must be securely supported and fastened to the building structure. Don't rely on the conduits to support the enclosures.

Bending Radius (NEC 300.34)

Ensure the bending radius of the conductors within the CT cabinet meets the minimum requirements specified in the NEC. Sharp bends can damage the insulation and reduce current carrying capacity.


Grounding and Bonding (NEC Article 250)

Proper grounding and bonding are essential for safety. Make sure the CT cabinet and all other metal enclosures are properly grounded to the service grounding electrode system. Use bonding jumpers around any concentric or eccentric knockouts.3.

Reasons to Choose Alternative Routing



Working Space Constraints

If you're tight on space and routing the feeders directly from the disconnect to the panels simplifies the installation and improves working space, that's a valid consideration.


Cost

Running more conduit can be more expensive, but sometimes simpler routing saves on labor costs.

Complexity

The fewer bends and the shorter the runs, the less voltage drop and potential for problems.4.

Recommendations



Consult a Licensed Electrical Inspector

Before proceeding, discuss your plans with your local electrical inspector. They can provide valuable insights into local codes and best practices.

Load Calculations

Perform a thorough load calculation to ensure the 600 amp service is adequate for the connected loads.


Detailed Drawings

Create detailed drawings of the entire installation, including conduit runs, conductor sizes, enclosure dimensions, and grounding details.

Professional Installation

If you're not a qualified electrician, hire a licensed electrical contractor to perform the installation. This is especially important for large services like a 600 amp service.

In summary, re-entering the CT cabinet is permissible, but you
must* carefully consider working space, fill requirements, bending radii, grounding, and proper identification.
Overlooking these details can result in code violations, safety hazards, and performance problems. Flag for review