Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 600ft voltage drop

User: karn, Location: United States

Asked on: Sunday, September 22, 2024 at 3:10 pm EDT
Answered on: Thursday, March 6, 2025 at 2:46 am EST

Question: I'm installing an RV panel with 50, 30, and 20-amp receptacles inside the panel. However, the location of this panel is almost 600 feet from the house panel. I don't think 4 AWG copper will suffice due to voltage drop, and 2 AWG gets pricy fast, so I was considering using a direct burial cable such as UF-B, USE-2, or URD to save the customer some money. I just wanted to get another opinion.

Okay, let's break down your RV panel installation and the considerations for that 600-foot run. You're right to be concerned about voltage drop over that distance. Here's a comprehensive look at your options, factors to consider, and recommendations

Key Considerations:
Voltage Drop

This is your primary concern. Excessive voltage drop can damage appliances, cause them to run inefficiently, or not function at all. The NEC recommends limiting voltage drop to 3% for feeders and 5% total (feeder + branch circuit).


Ampacity

The wire must be sized to handle the maximum load you anticipate.

NEC Compliance

You
must adhere to the National Electrical Code (NEC) and local electrical codes. This is non-negotiable for safety and legality. Your local permitting and inspection authority is the ultimate authority.

Cost

Balancing performance with cost is important.

Safety

Safety is paramount. Improper wiring can lead to fires, shocks, and other hazards.


Future Expansion

Consider if the customer might add more load in the future (e.g., another RV outlet, a small shop).

Analyzing Your Situation


Load Calculation

You must perform a load calculation to determine the actual maximum amperage the RV panel will draw. Don't just assume it's 50A because there's a 50A receptacle. RV loads are diverse, and typically not all outlets will be used at max capacity simultaneously. Factors to consider: Number and type of RVs expected. Common appliances used (air conditioners, heaters, refrigerators, etc.). Usage patterns (full-time RVers vs. occasional weekenders). Diversity factor (the likelihood of all appliances running at once).2.

Voltage Drop Calculation

Once you have an estimated load, you can calculate the voltage drop for various wire sizes. Use a voltage drop calculator (many are available online; Southwire's is a good one: [https://www.southwire.com/calculator-vdrop](https://www.southwire.com/calculator-vdrop)). You'll need: Voltage (240V or 120V depending on the loads). Assume 240V for the calculations. Amperage (from your load calculation). Wire length (600 feet 2 = 1200 feet for a 2-wire circuit). Wire type (copper or aluminum). Wire gauge.3.

Wire Type Considerations



Copper

Excellent conductivity, but expensive for long runs at higher amperages. Your initial instinct about 4 AWG being insufficient is likely correct, given the distance.


Aluminum

More cost-effective for larger gauges. However, you must use appropriately rated connectors and follow specific installation practices to prevent corrosion and overheating. Aluminum expands and contracts more than copper, which can loosen connections over time. Anti-oxidant compound is essential.

UF-B (Underground Feeder)

Can be direct buried. Less expensive than copper. Ampacity is usually 60°C or 75°C, so double check that it meets your requirements. Aluminum is a common option.


USE-2 (Underground Service Entrance)

Can be direct buried. More heat resistant than UF-B (usually rated for 90°C), which can allow you to use a smaller gauge (check ampacity charts and voltage drop). Often used for service entrance cables. Aluminum is a common option.

URD (Underground Residential Distribution)

Typically used by utilities for underground power distribution. It's generally acceptable for your application, but double-check local codes. It's usually aluminum and cost effective.4.

Grounding

Do
not rely on the ground through the neutral conductor (this is illegal for feeders to outbuildings). You must run a separate grounding conductor (copper or aluminum) along with the feeder conductors. Sizing of the grounding conductor must comply with NEC table 250.122 based on the overcurrent protective device size.

Recommendations


Aluminum is Highly Likely the Best Choice

Given the distance and load, aluminum is likely the most cost-effective solution. However, proper installation is absolutely crucial.2.

Load Calculation is Mandatory

Don't skip this step! It determines the correct wire size.3.

Voltage Drop Calculator

Use a reputable voltage drop calculator to ensure you're within acceptable limits. Aim for a maximum of 3% voltage drop on the feeder.4.

Consider These Aluminum Wire Options



1 AWG Aluminum USE-2 or URD

This is a good starting point. Calculate voltage drop and ampacity based on your load calculation. The 90°C rating allows a higher ampacity than UF-B.

2/0 AWG Aluminum USE-2 or URD

If the voltage drop with 1 AWG is excessive, step up to 2/0.


4/0 AWG Aluminum USE-2 or URD

If you anticipate that your customer may need to upgrade their services later on, using 4/0 may be worth it for future load demand.5.

Proper Installation is Key (for Aluminum)



Use dual-rated (AL/CU) connectors

These are specifically designed for aluminum-to-copper connections (if you're connecting to copper in your panels).


Apply anti-oxidant compound

Coat the aluminum conductors with an anti-oxidant joint compound (like Noalox or Penetrox) before making the connections. This prevents corrosion.

Torque to specification

Tighten all connections to the torque specifications provided by the connector manufacturer. Use a torque wrench.


Inspect periodically

Check the connections annually, especially during the first few years, to ensure they remain tight.6.

Grounding Conductor

Size the grounding conductor according to NEC table 250.122 based on the overcurrent protective device feeding the RV panel. Aluminum grounding conductors are acceptable.
7.


Overcurrent Protection



Main Breaker

Install a main breaker in the RV panel to protect the entire panel. Size it according to the ampacity of the feeder cable and your load calculation.


House Panel Breaker

The breaker in your house panel must protect the feeder cable leading to the RV panel.8.

GFCI Protection

Implement proper GFCI protection as required by the NEC for outdoor receptacles.9.

Permitting and Inspection

Obtain the necessary permits and have the installation inspected by a qualified electrical inspector. This is critical for safety and compliance.

Example Scenario (Illustrative)

Let's say your load calculation estimates a continuous load of 40 amps.

Voltage Drop Calculation

Using a voltage drop calculator for 600 feet (1200 feet total wire length), 240V, 40 amps:


1 AWG Aluminum

Voltage drop will likely be outside of a reasonable percentage, potentially in excess of 5%.

2/0 AWG Aluminum

Voltage drop is likely more reasonable, potentially around 2%-3%.


4/0 AWG Aluminum

Even lower, possibly 1%.

Ampacity

Check the ampacity of 2/0 or 4/0 AWG aluminum cable for the given temperature rating (75°C or 90°C). Ensure it's greater than 40 amps.

Important Reminders



Local Codes Prevail

Always check with your local electrical inspector to ensure compliance with local codes. They may have specific requirements.

Qualified Electrician

If you're not comfortable with electrical work, hire a qualified electrician. Electricity is dangerous.


Documentation:
Keep records of all calculations, wire sizes, and materials used.By carefully considering these factors, performing accurate calculations, and adhering to the NEC and local codes, you can ensure a safe and reliable RV panel installation. Good luck! Flag for review

Previous Question Next Question