Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Conduit Fill Discrepancy: Southwire vs NEC

User: viaPipeline, Location: Utah

Asked on: Sunday, September 22, 2024 at 5:42 pm EDT
Answered on: Thursday, March 6, 2025 at 2:47 am EST

Question: So have a bit of an issue at the job I'm on. There are 8, 4" EMT runs entering a box.However, there are only 3, 4" EMT exiting it at the back (opposite the cover) and going up through the ceiling about 2.5ft to another box, then to the switchgear. These holes were drilled in the concrete (x-rayed for PT cables) months ago.In each of the 8 incoming 4" conduits are 4 350kcmil aluminum THHN conductors and a #2 (I think) ground.The individual who had the holes drilled saw the table in NEC that said 4" EMT could hold 11 350kcmil conductors and assumed because 11 x 3 = 33, this should be enough.Since 11 isn't a multiple of 4, however, that means that not all of the circuits will be able to stay together.My Southwire Conduit Fill app says 4" EMT can hold 12 conductors before hitting 40% Fill.1) Why the discrepancy between NEC and Southern and who go believe?2) How screwed are we? What other problems might there be? The feeders have been pulled and if we have to remove the box, we have to pull them out.

Okay, let's break down this situation. You've got a complex conduit fill problem compounded by pre-drilled holes in concrete.1. Discrepancy Between NEC and Southwire Conduit Fill App



NEC (National Electrical Code)

The NEC is the
minimum safety standard. It's the law in most jurisdictions. It provides tables (like Table C.1 in Chapter 9 for EMT) based on conductor size and conduit type. These tables usually provide the maximum number of conductors allowed.

Southwire Conduit Fill App (and similar apps)

These apps calculate conduit fill based on conductor dimensions (including insulation) and conduit inside diameter. They often use the actual conductor dimensions provided by the manufacturer, which can vary slightly. These apps can be more precise and sometimes allow for more conductors than the tables.

Why the Difference?
The NEC tables are simplified and designed for ease of use. They often use conservative assumptions. Conduit fill apps use a more detailed calculation, potentially allowing for more conductors if the specific conductors used have slightly smaller dimensions. Who to Believe? First, always follow the NEC. It's the law. Second, if the app allows MORE conductors than the NEC table, you MUST still comply with the NEC. The app can only reduce the maximum allowed by the NEC. The app is a guide, but compliance with the NEC is paramount. Third, if the app allows the required conductors and complies with the NEC fill requirements, make sure to document how you came to that conclusion.2. How Screwed Are You? (And What to Do About It)

This is a
significant problem, but not necessarily an insurmountable one. Here's a breakdown of the issues and potential solutions: Overfilled Conduits (Likely)

The individual did not calculate the fills correctly. While 4" EMT may be able to hold the conductors in a straight pull, the concern is that once the conductors are bent inside the box it can put enough pressure on the connections that they come loose and are then more likely to arc, which can lead to a fire.

NEC Violation

Overfilled conduits violate NEC Article 314.16 (Conduit and Tubing Fill). This can lead to rejection by inspectors, fines, and potential liability issues.


Difficult Pulling

Overfilled conduits make pulling conductors extremely difficult, potentially damaging the insulation.

Heat Buildup

Overfilled conduits restrict airflow, leading to increased heat buildup. This can degrade insulation, reduce ampacity, and potentially cause a fire.


Voltage Drop

While less likely to be a direct result of overfilling (but indirectly possible due to heat degrading insulation), overfilled conduits can exacerbate voltage drop issues.

Future Problems

Adding or modifying circuits in the future will be difficult or impossible without further rework.


Parallel Circuits

The #2 ground may not be compliant with 250.122(B) if the overcurrent protection device requires a larger ground.

What To Do Next


Verify Conductor Size & Type

Confirm the exact size and type of conductors used (e.g., 350 kcmil aluminum THHN, and confirm the EXACT grounding conductor size). Check the insulation type.2.

Calculate Fill Carefully

Use the Southwire app (or a similar, reputable app) with the exact conductor data. Document your calculations. This will confirm exactly how overfilled the conduits are.3.

Consider Parallel Circuits

If the NEC tables have been violated, see if the circuits can be split into parallel configurations.4.

Consult with an Electrical Engineer

Given the complexity and potential code violations, consult with a licensed electrical engineer ASAP. They can perform a thorough review, calculate conduit fill, analyze the system, and recommend solutions that meet code requirements. This is especially important because of the pre-existing concrete penetrations.5.

Discuss with the Inspector

Be upfront with the electrical inspector. Explain the situation and the steps you're taking to correct it. They will likely have specific requirements.6.

Explore Solutions

Depending on the extent of the overfill and the recommendations from the engineer and inspector, consider the following:

Pulling Conductors and Increasing Conduit Size

If possible, this is the ideal solution. You would need to enlarge the holes in the concrete (if feasible) and replace the 4" EMT with larger conduit. This is the most expensive and time-consuming, but it ensures compliance and provides future flexibility.


Reducing Conductor Size (if possible)

If the load calculations allow, consider using smaller conductors (e.g., 300 kcmil) if this would bring the conduit fill within acceptable limits and if it's permitted by the NEC based on the load requirements. This is often difficult as 350 kcmil conductors were probably chosen to meet a specific load requirement. Consult with an engineer.

Adding a Box (if feasible)

Adding a junction box to divide the conduits and allow for a more reasonable fill. This is usually done when dealing with a long run of conduit.

Important Considerations



Safety First

Ensure all work is performed by qualified electricians and in accordance with safety regulations.

Documentation

Keep meticulous records of all calculations, decisions, and modifications.


Communication

Communicate clearly with the owner, contractor, engineer, and inspector throughout the process.*

Long-Term Planning

Consider future load growth when selecting conductors and conduit sizes.

In summary, you have a significant problem that requires careful evaluation, consultation with experts, and a well-thought-out solution. Don't try to "fudge" the numbers or cut corners. Address the issue head-on to ensure safety and compliance.
Flag for review

Previous Question Next Question