Topic: Sub panels for residential

User: Recee, Location: Arizona

Asked on: Sunday, September 22, 2024 at 5:45 pm EDT
Answered on: Thursday, March 6, 2025 at 2:47 am EST

Question: I have a 200 amp service ( residential) going to a 125 amp sub panel. That subpanel feeds another 125amp panel am I already maxed out?

No, you are not necessarily maxed out. Here's why: Service vs. Load

Your 200 amp service is the maximum amount of current the utility company
could supply to your house at any given moment. It does not mean you are drawing 200 amps constantly. Your actual usage depends on the loads (appliances, lights, etc.) you are using.

Panel Ratings vs. Actual Load

The 125 amp rating of the subpanels is the maximum capacity of those panels. Again, it doesn't mean you are drawing 125 amps from them at all times.

Understanding Demand Factors and Load Calculations


Electrical codes (like the NEC in the US) recognize that you don't use all your appliances and lights at the same time. Therefore, they allow for "demand factors" in load calculations. These factors reduce the calculated load to a more realistic value.

Here's what you need to do to determine if you're overloaded


Load Calculation for Each Panel

You need to perform a proper load calculation for each panel (the 125 amp subpanel and the second 125 amp panel it feeds). This involves listing all the circuits in each panel, calculating the expected load for each circuit (lights, outlets, appliances, etc.), and applying the appropriate demand factors as allowed by the electrical code.

General Lighting and Receptacles

For general lighting and receptacles, you'll use a minimum load calculation based on the square footage of the area served by each panel. Then you'll apply demand factors (e.g., the first 3000 VA is calculated at 100%, the next 117,000 VA at 35%, etc.).


Large Appliances

Large appliances (ranges, ovens, water heaters, dryers, AC units, etc.) must be included at their full nameplate rating or using specific load calculations defined in the electrical code (ranges have a special demand factor table, for example).

Motors

Motor loads are also calculated differently, often including a 125% factor for the largest motor.2.

Load Calculation for the Entire Service

Once you have the load calculations for both 125 amp panels, you need to combine those loads (with appropriate demand factors) to determine the total load on your 200 amp service.3.

Compare to Service Capacity

Finally, compare the total calculated load for your entire house to the 200 amp service capacity. If the calculated load is less than 200 amps, you're not overloaded. If it's close to or exceeds 200 amps, you should consult with a qualified electrician.

Example Scenario (Simplified)

Let's say, after performing the calculations:
The first 125 amp subpanel has a calculated load of 90 amps. The second 125 amp panel (fed by the first) has a calculated load of 70 amps.You can't just add 90 amps + 70 amps = 160 amps and assume you're fine. You need to consider the demand on the 200 amp service. If you calculate based on those two panels, plus all the other load in your house to equal 190 amps, you are good to go.

Important Considerations



Future Expansion

If you plan to add more appliances or circuits in the future, you should factor that into your load calculations.

Electric Vehicle Charging

EV chargers are a significant load and must be carefully considered. A Level 2 charger can easily add 30-50 amps of continuous load.


Safety First

If you are unsure how to perform load calculations, hire a qualified electrician. Incorrect calculations can lead to overloaded circuits, overheating, and potential fire hazards.

In summary, while your panel ratings might seem concerning, it's the actual load on your electrical system that matters. Proper load calculations are essential to determine if your 200 amp service is adequate.
Recommendation: Given that you have two subpanels in series, it's highly recommended that you hire a licensed electrician to perform a thorough load calculation. They can accurately assess your electrical needs and ensure your system is safe and compliant with local codes. Flag for review