User: solarken, Location: Hudson, OH, USA
Asked on: Sunday, September 22, 2024 at 8:08 pm EDT
Answered on: Thursday, March 6, 2025 at 2:48 am EST
Question: I could use some feedback on three options I put together for a Sol-Ark system design. 2023 NEC applies here. Attached is simple 1-line of each. I don't think option A is feasible because our utilities generally require an external accessible and lockable PV System disconnect. It is not clear to me that Option A does not meet NEC 690.13 requirement for PV System disconnecting means, as this option does provide a means to disconnect the PV system by turning off the Service breaker and moving the Bypass switch to the bottom position, albeit that also cuts power to the home as well.Option C provide the most extensive capabilities and avoids a supply side connection, but it requires two breaker enclosures and the bypass switch, so a lot of wall space outside the house and extra expense.Option B seems to meet requirements to me with only one breaker enclosure, but is a supply side connectionThe other detail I need to work out is where to run a neutral with the L1 and L2 between all this equipment. It seems I will need to leave a neutral out of one run in the triangle formed by the Inverter having connections to the breaker enclosure and the bypass switch, or there will be a loop in neutral path.Any thoughts or suggestions are welcomed
Okay, let's break down these Sol-Ark system options, considering NEC 2023, and address your concerns. Your assessment of each option is a good starting point. I'll provide feedback on each, focusing on code compliance, practicality, and cost.
General Considerations for All Options (and NEC 2023) Rapid Shutdown (RSD)
This is a big one for NEC 2023. You
must have a method for rapid shutdown of the PV system. The Sol-Ark likely has integrated RSD, but you need to ensure your system design supports this. This typically involves compatible RSD devices at the panel level (e.g., Tigo TS4-A-F or similar) that communicate with the inverter. Check the Sol-Ark manual and your chosen RSD devices for compatibility and wiring requirements. Grounding/Bonding
Pay very close attention to grounding and bonding requirements. This includes equipment grounding conductors (EGCs) from the PV array, combiner box (if applicable), disconnects, and the inverter back to the service entrance. Follow the Sol-Ark instructions and NEC Article 690 meticulously. Consider using listed grounding lugs and ensuring proper torque specifications.
Overcurrent Protection
Ensure all breakers and fuses are properly sized for the conductors and equipment they are protecting. Conduct ampacity calculations for all wiring runs.
Conductor Sizing
Correct conductor sizing based on the NEC for continuous and non-continuous loads.
Labeling
NEC 690.56 has specific labeling requirements for PV systems, including warnings about voltage, disconnect locations, and rapid shutdown. Don't skip this!
Working Space
Remember the working space requirements around electrical equipment as per NEC 110.26. Make sure there's adequate space for maintenance and troubleshooting.
Arc-Fault Circuit Interrupter (AFCI) Protection
2023 NEC is likely to require AFCI protection for new PV systems in many jurisdictions. The Sol-Ark inverter needs to be compatible with any AFCI devices you use.
AHJ (Authority Having Jurisdiction)
Crucially, check with your local permitting authority (AHJ) about their specific interpretation and enforcement of NEC 2023 and any local amendments. This is essential to avoid surprises during inspection.
AC Combiner Panel
If you are combining more than one inverter output, you'll need to use an AC combiner panel.
Option A: Service Disconnect & Bypass (Potentially Problematic) Utility Disconnect Requirement
You're likely correct that this won't fly with your utility. Most require an external, accessible, and lockable disconnect specifically for the PV system. This is for their safety and to allow them to isolate the PV system during grid outages or maintenance.
NEC 690.13 Adequacy
While technically you can disconnect the PV system by turning off the service breaker and using the bypass, this is not the intent of 690.13. The disconnect needs to be readily accessible and clearly labeled as a PV disconnect. Imagine a firefighter needing to shut down the PV system quickly – they're not going to want to hunt for the main service disconnect.
Limited Functionality
This option offers the least flexibility. You can't easily isolate the PV system for maintenance without killing power to the entire house.
In summary, Option A is likely not compliant and impractical.Option B: Supply-Side Tap (Potentially Compliant, But Requires Careful Execution) Supply-Side Connection Concerns
Supply-side taps (connections before the main service disconnect) are permitted by the NEC (705.11 and 230.82), but they have strict requirements.
Overcurrent Protection
The tap conductor needs to be protected by an overcurrent device sized appropriately for its ampacity. This often means a breaker in the service panel before the main breaker or a fused disconnect.
Tap Conductor Length
The tap conductor length is often limited (e.g., to 10 feet) unless specific conditions are met (like being in conduit). Check NEC 240.21(B).
Breaker Size Limitations
Breaker must meet 120% rule (Article 705.12)
Cost
Typically lower costs than other options since you are only buying one breaker enclosure.
Neutral
If a neutral is needed for the Sol-Ark, you can pick it up in the panel, but it could cause a loop as you described if you need to run it to the bypass switch and the Inverter separately. Be sure to follow the manufacturer's instructions to prevent ground loops.
Overall, Option B is potentially viable, but requires very careful attention to the supply-side tap rules, conductor sizing, and overcurrent protection. Also, you might run into neutral loop issues.Option C: Load-Side Connection with Critical Loads Panel (Generally Best, Most Flexible, But Most Expensive) Advantages
This is often the preferred method for grid-tied with backup systems. It provides the most flexibility and avoids the complexities of a supply-side connection.
Critical Loads Panel
You create a subpanel (critical loads panel) fed from the Sol-Ark. This panel powers essential circuits during a grid outage.
Backfeed Protection
The main service panel needs to be protected from backfeed from the Sol-Ark. This is usually accomplished with a breaker interlock or an automatic transfer switch (ATS).
Bypass Switch
Allows you to bypass the Sol-Ark and power the critical loads panel directly from the grid in case of inverter failure.
Cost
More expensive due to the extra panel, ATS/interlock, and bypass switch.
Wall Space
Requires more wall space.
Neutral
You could still encounter the neutral loop issues in the triangle described if you need to connect the neutral to both the critical loads panel and the bypass switch. Be sure to follow the manufacturer's instructions to prevent ground loops.
Option C provides the most robust and code-compliant solution, but it comes at a higher cost.Addressing the Neutral Loop Concern
You're right to be concerned about potential neutral loops. This is a common issue with interconnected systems. Here's how to approach it:1.
Consult the Sol-Ark Manual
The absolute first step is to carefully review the Sol-Ark installation manual. It should provide specific guidance on neutral connections and ground loop prevention.2.
Understand the Grounding System
Is your system bonded at the service entrance, the inverter, or both? The bonding location affects how you handle the neutral.3.
Single Point Grounding
The goal is generally to have a single point where the neutral is bonded to ground. Multiple bonding points can create circulating currents.4.
Neutral Disconnect/Switching
In some cases, the bypass switch may need to switch the neutral conductor as well as the hots. This depends on the specific configuration and the Sol-Ark's requirements.5.
Test for Voltage Between Neutrals
After installation, before connecting to the grid, use a voltmeter to check for any voltage difference between the neutral conductors at different points in the system. A significant voltage (more than a few volts) indicates a potential ground loop issue.6.
Consult with a Qualified Electrician
If you are not experienced with electrical systems and grounding, hire a qualified electrician who is familiar with PV systems and NEC 2023. This is not the area to cut corners.
Recommendations
Start with Option C as your baseline. It's the most code-compliant and flexible.2. Thoroughly research the Sol-Ark manual and local codes.3. Focus on grounding/bonding and overcurrent protection.4. Consult with your AHJ (building inspector/permitting office) early in the design process. Get their feedback on your proposed design.5. Consider a site visit from a qualified solar installer or electrician. They can assess your specific situation and provide tailored recommendations.6. If cost is a major constraint, investigate Option B, but be extremely* diligent about compliance with the supply-side tap requirements. Don't compromise on safety or code compliance.By following these steps, you can design a Sol-Ark system that is safe, reliable, and meets all applicable codes. Remember, the devil is in the details, so pay close attention to every aspect of the design and installation. Flag for review