Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Exam questions

User: paivaselectric, Location: Mass

Asked on: Sunday, September 22, 2024 at 11:58 pm EDT
Answered on: Thursday, March 6, 2025 at 2:48 am EST

Question: I have 4 office 20x30 how do I find the size feeder I need for to that service ? This was one of the questions on the master exam I thought I knew how to find it.

Okay, let's break down how to approach this feeder sizing question, common in electrical master exams. This isn't a complete design calculation without more information, but it outlines the typical process.1. Understanding the Basics



Feeder

A feeder is the set of conductors (wires) that carry electricity from the service entrance (where power enters the building) to a panelboard or subpanel that then distributes power to individual circuits within an area.


Office Load

In this case, the load is the electrical demand of the four 20x30 offices.

NEC (National Electrical Code)

Feeder sizing must comply with the NEC. You
must use the current version of the NEC for your jurisdiction. The exact NEC version will influence specific article references.

2. Key NEC Articles (Refer to the actual NEC book)



Article 220: Branch-Circuit, Feeder, and Service Calculations

This is the cornerstone of load calculations.

Article 310: Conductors for General Wiring

Used to determine the ampacity (current-carrying capacity) of conductors based on insulation type, temperature rating, and installation conditions.


Article 215: Feeders

Specific requirements for feeders.

3. Steps to Calculate Feeder Size

A.

Determine the General Lighting Load



NEC 220.12

Specifies general lighting loads based on occupancy type. For offices, it's typically
3.5 volt-amperes per square foot (VA/sq ft).

Total Square Footage

4 offices 20 ft 30 ft = 2400 sq ft

General Lighting Load

2400 sq ft
3.5 VA/sq ft = 8400 VAB.

Determine Small Appliance and General Receptacle Load



NEC 220.14(H)

For non-dwelling occupancies (like offices), you typically calculate receptacles at
180 VA per outlet. However, NEC 220.14(I) requires receptacles in specific areas to be supplied by branch circuits rated 20 amperes. The NEC requires this to be the minimum, but often a larger circuit may be preferred.

Receptacles

The number of receptacles is unknown at this point. You'd either be given this number in the exam question or be instructed to assume a certain number based on a code minimum.

Assume (for this example) 10 Receptacles per Office

4 offices
10 receptacles/office = 40 receptacles

Receptacle Load

40 receptacles
180 VA/receptacle = 7200 VAC.

Determine Dedicated Equipment Load (if any)

Offices often have dedicated equipment like HVAC units, copiers, computers, etc. You need to know the VA or amp rating of each piece of equipment. The problem must provide this information.

Assume (for this example) 1 HVAC unit rated at 240V, 15 Amps per office



HVAC Load per Office

240V
15A = 3600 VA

Total HVAC Load

3600 VA/office
4 offices = 14400 VAD.

Calculate Total Connected Load

Add all the loads together: General Lighting: 8400 VA Receptacles: 7200 VA HVAC: 14400 VA

Total Connected Load = 30000 VA


E. Apply Demand Factors (if applicable)



NEC Article 220

Demand factors are multipliers applied to certain loads because it's unlikely that all loads will operate at 100% of their capacity simultaneously. The NEC provides tables for various occupancies. This is crucial.



General Lighting and Receptacles

Demand factors for general lighting and receptacles in non-dwelling units are often 100%. However, you
must consult the specific NEC section to confirm.

HVAC

Demand factors for HVAC are also usually 100%.

In this example, assume all demand factors are 100%



Calculated Load = 30000 VAF.

Calculate Feeder Current (Amps)



Choose a Voltage

You need to know the voltage of the service. Common voltages are 120/240V single-phase or 120/208V or 277/480V three-phase.
The problem must provide this.

Assume 120/208V Three-Phase



Formula

`Amps = VA / (Voltage
√3)`

Feeder Current

30000 VA / (208V
√3) = 83.2 AmpsG.

Apply Any Continuous Load Factors



NEC 215.3

Feeders supplying continuous loads (loads that operate for 3 hours or more at a time)
must be sized to handle 125% of the continuous load.

Determine Continuous Loads

Identify which loads are likely to be continuous. In an office, lighting, some HVAC, and computer equipment could be considered continuous. This is a judgment call based on the specific scenario.

Assume Lighting and HVAC are Continuous (Total Continuous Load = 8400 VA + 14400 VA = 22800 VA)



Continuous Load Current

(22800 VA / (208V √3)) 1.25 = 79.2 Amps

Non-Continuous Load Current

(7200 VA / (208V
√3)) = 20 Amps

Total Adjusted Feeder Current

79.2 A + 20 A = 99.2 AmpsH.

Select Conductor Size



NEC Table 310.16

This table provides the ampacity of conductors based on their insulation type, temperature rating, and installation conditions (e.g., in conduit, free air). You need to know the insulation type and temperature rating (usually given in the problem or you assume the most common, THHN 75°C). Also, consider ambient temperature and any derating factors for multiple conductors in a raceway (NEC 310.15).

Example

Let's assume you're using THHN copper conductors in conduit, rated at 75°C, and no derating is required. You need a conductor with an ampacity of at least 99.2 Amps. According to NEC Table 310.16, you would need at least a #3 AWG copper conductor (rated for 100 Amps at 75°C).I.

Select Overcurrent Protection



NEC 240.4(B)

You generally protect a conductor at its ampacity. You can use the next standard overcurrent device size if the conductor's ampacity doesn't correspond exactly to a standard breaker size (see NEC 240.6 for standard sizes).

In this case

Since you're using #3 AWG (100 Amps), and if the calculated load is 99.2 Amps, you
could use a 100 Amp breaker. However, always double-check with the NEC article.J.

Grounding and Bonding

Don't forget to size the equipment grounding conductor (EGC) based on the size of the ungrounded conductors (from NEC Table 250.122).

Important Considerations and Exam Tips



Read the Question Carefully

Underline key information (voltage, load types, continuous loads, etc.).


Show Your Work

Even if you don't get the final answer perfectly, showing your steps can earn you partial credit.

Know Your Tables

Be very familiar with NEC tables 220.12, 310.16, 250.122 and the relevant sections in Article 220 and 215.


Demand Factors are Critical

Don't skip them! This is where many people make mistakes.

Continuous Loads

Remember the 125% factor for continuous loads.


Voltage Drop

Although not usually the primary focus of a feeder sizing question on the master exam, keep in mind that NEC 215.2(A)(1) advises that feeders be sized to prevent excessive voltage drop. A common recommendation is not more than 3% voltage drop at the furthest outlet.

Example Short-Answer Exam Response

"1.

Lighting Load

2400 sq ft 3.5 VA/sq ft = 8400 VA (NEC 220.12)2.

Receptacle Load

40 receptacles
180 VA/receptacle = 7200 VA (NEC 220.14(H))3.

HVAC Load

4 offices 240V 15A = 14400 VA4.

Total Connected Load

8400 VA + 7200 VA + 14400 VA = 30000 VA5.

Assuming 120/208V 3-phase

I = 30000 VA / (208V √3) = 83.2 Amps6.

Continuous Loads (Lighting and HVAC)

(8400 VA + 14400 VA) / (208V
√3) 1.25 = 79.2 A7.

Non-Continuous Loads (Receptacles)

7200 VA / (208V
√3) = 20 A8.

Total Adjusted Feeder Current

79.2 A + 20 A = 99.2 Amps9.

Conductor Size

Using THHN 75°C copper, #3 AWG (100 Amps) is required per NEC Table 310.16.
10.


Overcurrent Protection

A 100 Amp breaker is suitable (NEC 240.4(B)).
11.


EGC

Size per NEC Table 250.122 based on the size of the ungrounded conductors."

Disclaimer:
This is a general explanation and example. Always refer to the current NEC and consult with a qualified electrical engineer or inspector for actual design and installation. Code requirements can vary by jurisdiction. Good luck with your exam! Flag for review

Previous Question Next Question