Topic: Best practice for multiple motors on a branch curcuit

User: cal7212, Location: Florida

Asked on: Monday, September 23, 2024 at 8:19 am EDT
Answered on: Thursday, March 6, 2025 at 2:48 am EST

Question: I have searched the forum and have not come up with a solid answer for my situation so here goes...I work for a hydraulic systems OEM and we are re-designing the control panel that we use for testing our units. We want to be able to run up to 2 motors between 50 and 100HP each. There is a 200A circuit breaker supplying this panel. What is the best method to allow this? The only guidance I have seen is 430.53(C), however I am not sure that this meets the group installation criteria. Am I correct? Is there another reference? For each of the 2 starters how do they need to be rated if a variable range of motor sizes can be run on each?

Okay, let's break down this challenging motor control panel design with a 200A supply and figure out how to handle up to two 50-100HP motors.

Understanding the Core Issues

You're right to be cautious. Designing motor control panels, especially with multiple motors, requires careful adherence to the NEC (National Electrical Code), specifically Article 430. The goal is to ensure: Overload Protection

Protecting the motors from damage due to overloads (excessive current draw for extended periods).


Short-Circuit and Ground-Fault Protection

Quickly interrupting fault currents (short circuits or ground faults) to prevent fires and equipment damage.

Proper Conductor Sizing

Ensuring the wiring can safely carry the required current without overheating.


Safe Installation

Following proper wiring methods, grounding, and disconnect requirements.

Why 430.53(C) Might Not Be Ideal for Your Application


NEC 430.53(C) addresses group motor installations with short-circuit protective devices. While it could be used, it's often cumbersome and requires careful coordination. Here's why it might not be the best fit for your test panel where you want flexibility in motor size: Fixed Motor Sizes

430.53(C) typically assumes you know the exact FLA (Full Load Amperes) of each motor and can select components accordingly. Since you want to test a range of motor sizes (50-100 HP), you'd have to design for the
worst-case scenario (100HP on both motors simultaneously). This leads to larger and more expensive components than you might actually need most of the time.

Coordination Challenges

430.53(C) relies on the overload relays in each motor starter to coordinate with the branch-circuit short-circuit protective device (your breakers). This coordination can be tricky to achieve and requires careful selection of breaker types and overload relay settings.

Limited Flexibility

If you ever need to test a motor that
slightly exceeds the FLA you designed for under 430.53(C), you'd be out of luck.

A More Flexible and Practical Approach: Individual Branch Circuits


Instead of trying to force-fit 430.53(C), consider using individual branch circuits for each motor. This is generally a cleaner, more flexible, and safer approach, especially for your application:1. Separate Motor Starters and Overload Protection

Each motor will have its own dedicated motor starter and overload relay. This allows you to independently protect each motor based on its specific nameplate FLA.2.

Individual Branch Circuit Protection

Each motor starter will be fed from its own dedicated circuit breaker within the panel. This provides individual short-circuit and ground-fault protection for each motor branch.

Steps to Design the Panel (Using Individual Branch Circuits)
1. Determine the FLA of the Motors

You need to determine the Full Load Amperes (FLA) of the 50HP and 100HP motors at your operating voltage (e.g., 460VAC, 3-phase). Use NEC Table 430.250 for typical FLA values.

Example

At 460V:
50 HP ~ 65 Amps 100 HP ~ 124 Amps2.

Motor Starter Selection

Select motor starters that are sized appropriately for the largest motor you intend to run (100HP). The starter must have a horsepower rating equal to or greater than the motor's horsepower. Consider using solid-state or smart starters, especially for larger motors. They offer features like reduced voltage starting, overload protection, and communication capabilities. Choose starters with adjustable overload relays so that you can easily dial in the FLA.3.

Overload Relay Selection

Choose overload relays that are compatible with your chosen starters. The overload relay's adjustable range must cover the FLA of the motors you'll be testing. For instance, an overload relay with a range of 50-130 Amps would likely be suitable for both 50HP and 100HP motors at 460V.

Important

Properly set the overload relay to the motor's nameplate FLA. This is crucial for motor protection.4.

Branch Circuit Conductor Sizing (Wiring)

Size the branch circuit conductors (the wires feeding each motor starter) according to NEC 430.22. In general, the conductors must have an ampacity of at least 125% of the motor's FLA.

Example (100HP at 460V)

FLA = 124 Amps Conductor Ampacity Required = 124 Amps 1.25 = 155 Amps. You'd likely need at least a #1 AWG copper conductor (check ampacity tables in the NEC – Table 310.16 for ampacity in free air, or Table 310.15 for ampacity in conduit). Adjust based on temperature rating. Remember to consider voltage drop, especially for longer wire runs.5.

Branch Circuit Short-Circuit and Ground-Fault Protection (Breakers)

Size the branch circuit breakers according to NEC 430.52. This is where it gets a little more nuanced. The breaker's instantaneous trip setting (or, in some cases, the inverse-time breaker rating) needs to be high enough to allow the motor's inrush current during starting, but low enough to provide adequate short-circuit protection. Typically, you can use an inverse time circuit breaker sized no greater than 250% of the motor's FLA (for motors with Code letters F through V). This is just a general guideline. You may need to adjust depending on the breaker type and motor characteristics. The values on 430.52 can also be used.

Example (100HP at 460V)

FLA = 124 Amps Maximum Breaker Size = 124 Amps 2.5 = 310 Amps. Since you don't want to exceed your 200A main breaker, this means you will have to size down. A smaller branch breaker can be used if it allows the motor to start without nuisance tripping.

Important Considerations for Breaker Selection



Motor Starting Characteristics

Motors draw a significant inrush current (6-8 times FLA) when starting. The breaker must be able to withstand this inrush without tripping.


Breaker Type

Different breaker types have different tripping characteristics. "Inverse time" breakers are generally preferred for motor circuits because they allow for short-duration overloads (like inrush current) without tripping.

Coordination

You'll need to ensure that the branch circuit breakers coordinate with the main 200A breaker. This means that the branch breakers should trip
before the main breaker in the event of a fault.

Testing

Test your breaker under load to make sure it can withstand the inrush current without nuisance tripping.6.

Main Disconnect and Overcurrent Protection

You have a 200A circuit breaker. This will be your main overcurrent protection device and your disconnect.

Calculate Total Load

The combined FLA of both motors (assuming you could run them simultaneously) plus any other loads on the panel must not exceed 80% of the 200A breaker's rating (NEC 210.20(A)). 200A 0.8 = 160A. This means you need to choose breakers that are low enough that they will be coordinated for the main breaker. Check your main breaker trip curve against your potential branch breakers.7.

Panel Enclosure and Wiring

Choose an enclosure that is large enough to house all the components and provide adequate space for wiring. Use appropriate wiring methods (conduit, wire type, etc.) according to the NEC and local codes. Properly ground the enclosure and all equipment.8.

Safety Considerations

Clearly label all components and wiring. Provide a prominent warning label stating the maximum motor HP and FLA ratings for each branch circuit. Consider including safety interlocks to prevent accidental starting or operation of the motors during maintenance. Add emergency stop buttons (E-Stops) to the panel for quick shutdown in case of a problem.

Important Notes



Consult the NEC

This is just a general guide. You must refer to the latest edition of the National Electrical Code (NEC) for detailed requirements.

Local Codes

Be aware of any local electrical codes or regulations that may be more stringent than the NEC.


Qualified Electrician/Engineer

This is a complex design. It's highly recommended that you have a qualified licensed electrician or electrical engineer review your design and perform the installation. They can ensure compliance with all applicable codes and safety standards.

Coordination Study

For larger motor installations, a coordination study may be required to ensure that the overcurrent protective devices (breakers and fuses) are properly coordinated to minimize downtime and prevent cascading failures.


Motor Nameplate Data

ALWAYS use the actual nameplate FLA of the motors you are testing, not just the typical values from NEC tables.

In Summary


Using individual branch circuits with properly sized motor starters, overload relays, and breakers is the most flexible and practical approach for your motor testing panel. This allows you to safely test a range of motor sizes without being constrained by the limitations of group motor installation rules. Just make sure all equipment chosen is coordinated for your maximum load. Remember to consult the NEC, local codes, and a qualified electrician or engineer for a safe and compliant installation. Flag for review