Topic: Current carrying conductors

User: Preacher84, Location: Hagerstown MD U.S.

Asked on: Monday, September 23, 2024 at 9:15 am EDT
Answered on: Thursday, March 6, 2025 at 2:49 am EST

Question: How many current carrying conductors can go inside a 1” EMT pipe, with 20 amp breakers? And does it make a difference if the conductors are stranded as opposed to solid?

Let's break down how to determine the number of current-carrying conductors (CCCs) allowed in a 1" EMT (Electrical Metallic Tubing) conduit, taking into account the 20-amp breakers and whether the conductors are stranded or solid.1. Conduit Fill Calculation: The Basics Code Requirement

The National Electrical Code (NEC) limits the percentage of a conduit's cross-sectional area that can be occupied by conductors. For three or more conductors, the maximum fill is generally

40%
.
Conduit Area

You need the internal area of a 1" EMT conduit. You can find this in NEC Chapter 9, Table 4, or in most electrical reference materials. The internal area of a 1" EMT conduit is approximately

0.864 square inches
. Conductor Area

You need the cross-sectional area of the conductors you plan to use. This is where the conductor size and stranding come into play.

2. Conductor Size and Stranding



Wire Size and Ampacity

A 20-amp breaker typically requires

12 AWG
copper conductors (check NEC 310.16 and the temperature rating of the terminals). Aluminum is not permitted for 15/20 amp branch circuits. Stranded vs. Solid



Yes, it absolutely makes a difference!
Stranded conductors, while more flexible, have a slightly larger overall diameter (and therefore area) than solid conductors of the same AWG size because of the air gaps between the strands.3. Finding Conductor Areas (NEC Chapter 9, Table 5A)

Here are the approximate areas for conductors typically used with 20A breakers (check NEC Chapter 9, Table 5A to confirm):


12 AWG THHN/THWN-2 Solid Copper

Around 0.0133 sq in.

12 AWG THHN/THWN-2 Stranded Copper

Around 0.0172 sq in.
NEC 310.16 dictates that for 20 amp breakers we must have conductors with an ampacity of at least 20 amps. 14 AWG copper is rated for 15 amps, 12 AWG copper is rated for 20 amps, and 10 AWG copper is rated for 30 amps.

4. Calculation


Calculate Allowable Fill Area

0.864 sq in (conduit area) 0.40 (40% fill limit) =

0.3456 sq in
(usable area inside the conduit).2. Determine Number of Conductors



Solid 12 AWG

0.3456 sq in / 0.0133 sq in/conductor ≈

26 conductors
Stranded 12 AWG

0.3456 sq in / 0.0172 sq in/conductor ≈

20 conductors
5. Derating

NEC 310.15(B)(3)(a) requires you to adjust the ampacity of conductors if there are more than three current-carrying conductors in a conduit. This is called "derating." 4-6 CCCs: 80% of ampacity 7-9 CCCs: 70% of ampacity

6. Putting It All Together - Practical Application and Example

Let's say you have a 120V circuit with a neutral (so 3 current carrying conductors), running 12 AWG stranded copper. You can fit many more conductors into the pipe, but the practical question becomes:

How many
circuits can you run?
Each circuit typically requires 3 conductors (Hot, Neutral, Ground – ground wires generally don't count as current-carrying for derating purposes) or 2 conductors in a 240v circuit. Example

You want to run three 120V circuits (each with Hot, Neutral, Ground; 3 current-carrying conductors per circuit) through the conduit. That's 9 current-carrying conductors. According to NEC 310.15(B)(3)(a), you must derate the ampacity to 70%. This means your 20 amp breaker must use 12 AWG conductors rated to 28.5 amps.

Important Considerations



Grounding Conductors

Grounding conductors (equipment grounding conductors – EGCs) do count toward conduit fill calculations but do not typically count towards derating. This is because they are not normally carrying current.

Neutral Conductors

In many cases, the neutral conductor in a standard residential circuit is considered a current-carrying conductor and
does count toward derating. However, there are exceptions (e.g., if the load is primarily non-linear). Consult the NEC for specific requirements.

Box Fill

Don't forget to calculate box fill as well! The number of conductors in the conduit must also be accommodated in the electrical boxes at either end.

Local Codes

Always check your local electrical codes and regulations, as they may have stricter requirements than the NEC.

In summary

A 1" EMT conduit can hold a significant number of conductors. Stranded conductors take up more space than solid conductors. Derating significantly impacts how many circuits you can safely run in a conduit.* Consult the NEC and local codes for the most accurate and up-to-date information.

Disclaimer:
I am an AI chatbot and cannot provide electrical advice. This information is for general guidance only. Consult with a qualified electrician for any electrical work to ensure safety and compliance with applicable codes. Incorrect electrical work can be dangerous and potentially fatal. Flag for review