Question: I have never seen this before and question application. "Electrician" installed meter base, new service conductor from weatherhead to line side, 3 wire. From load side of meter, a 4 wire cable was run to a load center. The grounded conductor and grounding electrode were bonded inside the meter base. A grounding lug was screwed to the meter base and then connected to 2-ground rods via a #4 bare copper conductor. I refused the installation based on 250.24(A)(1) and 250.8 of the 2008 NEC. Could this even be considered acceptable?

You are correct to refuse the installation based on the information provided. Your reasoning using the 2008 NEC is sound. Here's a breakdown of why and what specific code sections are relevant, expanded on the reasons you stated

Why It's Unacceptable and Code Violations:

1. Multiple Points of Grounding the Neutral (Grounded Conductor)

The primary issue is bonding the neutral (grounded conductor) at both the meter base and the load center. This creates parallel paths for neutral current, which is a dangerous and code-violating situation.

250.24(A)(5) 2008 NEC - Load-Side Grounding.
Specifically states the grounded conductor can not be connected to equipment grounding conductors on the load side of the service disconnecting means.2. Improper Bonding Location

Bonding the grounded conductor and grounding electrode conductor
inside the meter base is problematic if it's also bonded at the load center. The Code specifies where this bonding is permitted. Generally, the neutral-ground bond happens at the service disconnecting means.3.

Service Equipment Requirements

The meter base
might not be considered service equipment unless it also houses the service disconnect. Typically, the service disconnect is the main breaker in the load center. If the load center is the service disconnect, the grounding and bonding needs to occur there.

Breakdown of Relevant 2008 NEC Sections



250.24(A)(1) Grounding Service-Supplied Alternating-Current Systems

This section requires the grounded conductor (neutral) to be grounded. However, it doesn't dictate where that grounding must occur. It's the subsequent subsections that define the location.

250.24(A)(5) 2008 NEC - Load-Side Grounding.
Specifically states the grounded conductor can not be connected to equipment grounding conductors on the load side of the service disconnecting means. 250.8 Connection of Grounding and Bonding Equipment

This section covers the methods for making proper grounding and bonding connections (e.g., using listed connectors, exothermic welding, etc.). While your description doesn't necessarily indicate a violation of how the connections were made, the location of the connections is incorrect, rendering the installation unacceptable.

Why Parallel Neutral Paths Are Dangerous



Overheating

Neutral current will divide between the neutral conductor and the equipment grounding conductor (and any other metallic paths). This can overload the grounding conductor, causing it to overheat and potentially create a fire hazard.


Stray Voltage

Stray voltage can appear on grounded metal parts of equipment, creating a shock hazard.

Improper Operation of Protective Devices

The intended current path for fault current can be altered, preventing overcurrent protection devices (breakers/fuses) from operating correctly.

Correct Installation (General)


Neutral-Ground Bond at
One Location

Typically, the neutral (grounded conductor) and the equipment grounding conductors are bonded at the
service disconnecting means (usually the main breaker panel).2.

Four-Wire Feed to Load Center

The four-wire feed (hot-hot-neutral-ground) from the meter base to the load center is correct
only if the neutral-ground bond is not made at the meter base.3.

Grounding Electrode Conductor

A grounding electrode conductor (the #4 copper to the ground rods) must connect to the grounded conductor
at the service disconnecting means*.4.

Meter Base Grounding

The meter base itself should be grounded, but this is typically achieved through the equipment grounding conductor from the load center, and/or through the metallic raceway connecting the meter base to the service equipment.

In summary, the installation you described is incorrect because it likely creates multiple points of neutral-to-ground bonding, leading to parallel neutral paths and potentially dangerous conditions.
The neutral-ground bond should only occur at the service disconnecting means. You were correct to refuse the installation and cite the relevant sections of the NEC. Flag for review