Topic: Indoor spa and bonding

User: bobped, Location: Medford, OR

Asked on: Monday, September 23, 2024 at 1:12 pm EDT
Answered on: Thursday, March 6, 2025 at 2:50 am EST

Question: Working on a two story new construction home with a walkout basement, slab on grade. The home is in Oregon, which recently adopted NEC '23. Sometime in the future a spa will be installed inside this basement. I'm not usually involved in concrete pours, and in fact slab on grade is not very common in our area, so this may just be a stupid question. But I'm trying to understand if there is anything I or the concrete sub need to do above and beyond normal practice regarding bonding of the slab that will be the base for the spa. Since the spa will not be installed until well after construction is complete if we don't take this into consideration now I fear trouble down the line.The spa manufacturer says this about reinforcement and bonding, no mention of any differences for interior vs exterior locations.Concrete foundations should be a minimum of 4” (10.16cm) thick and should be reinforced with either rebar or mesh. For electrical grounding purposes, the rebar or mesh should be attached to a bond wire.The home has a foundation surrounding the slab, with UFER ground that was inspected. The slab will have either WWM or rebar (not sure) and will be poured next week. I will be speaking with the concrete sub later this week, but wanted to be sure I'm straight on what is needed before that chat.My question - is there any way that slab will pass inspection but leave the slab in a state where it is not suitable for the spa, in terms of bonding? Or will the concrete sub be required to bond the slab to the existing UFER anyway, so we won't need to do anything else after the slab is poured?

This is a great question, and definitely worth addressing now rather than scrambling later. Here's a breakdown of considerations and what you need to discuss with your concrete sub, based on NEC '23 and best practices for spas

Key Concerns & Code Requirements (NEC '23):
680.26(B)(2) - Interior Installations

This section of the code is where things get tricky. It specifically states that for indoor spa installations, you
must have a structural conductive grid, or a similar method approved by the AHJ, in the concrete. This grid MUST be bonded to the equipment grounding conductor (EGC) of the spa.

(1) Structural Reinforcing Steel.
Structural reinforcing steel that is bonded in accordance with 680.26(C). (2) Common Bonding Grid. A common bonding grid constructed in accordance with 680.26(C). (3) Solid Metal Sheathing. A solid metal sheathing that is bonded in accordance with 680.26(C). (4) Conductive Coating. A conductive coating applied to the interior surface of the pool or spa shell, or to the perimeter surface within 3 ft horizontally of the interior wall of the pool or spa, that is bonded in accordance with 680.26(C). (5) Perimeter Surface Bonded to Structural Reinforcing Steel.

A perimeter surface that is bonded in accordance with 680.26(C) to structural reinforcing steel. 680.26(C) - Bonding to the Equipmemnt Grounding Conductor. Means that the grid (rebar or mesh in the slab, in your case) has to be connected to the spa equipment grounding conductor. UFER Ground Isn't Enough

While the UFER ground in the foundation is critical for the service entrance grounding, it

doesn't automatically satisfy the requirements for bonding around the spa
. You need a separate, dedicated bonding connection to the slab reinforcement. Future Spa Installation

The fact that the spa is a future installation is exactly why you need to plan now. Retrofitting a proper grid and bonding connection after the slab is poured is significantly more difficult and costly.

Potential Problems if Not Addressed Now



Failed Inspection Later

The electrical inspector for the spa installation will likely require proof of the bonding grid within the slab, connected to the spa's EGC. If it's not there, the spa won't pass inspection.

Safety Hazard

Improper bonding can create a shock hazard around the spa.


Concrete Sawing & Jackhammering

To retrofit a proper connection, you'd likely need to cut into the concrete to expose the rebar/mesh and install a bonding lug. This is messy, expensive, and can compromise the integrity of the slab.

Steps to Take NOW (Talk to your Concrete Sub)


Confirm Rebar vs. WWM

Find out exactly what the concrete sub plans to use for reinforcement:

Rebar

This is generally easier to bond to.


WWM (Welded Wire Mesh)

Still acceptable, but may require multiple bonding points for optimal conductivity.2.

Ensure Continuous Reinforcement

Make sure the rebar or mesh is continuous throughout the entire slab area that will be under and around the spa. Overlapping is fine, but there shouldn't be any significant gaps.3.

Bonding Lug Placement

This is the MOST important part. You need to specify the installation of a bonding lug within the slab, accessible after the concrete is poured. Here's how:

Location

Choose a location close to where the spa equipment will be located (e.g., near the planned pump and control panel location). This minimizes the length of the bonding conductor. Make sure it is somewhere it won't get stepped on or driven over, and will be accessible after the spa is installed.


Embedment

The concrete sub needs to securely attach a listed bonding lug (designed for concrete embedment) to the rebar or mesh before the pour. The lug should be positioned so that the connection point is just below the finished surface of the slab, or protruding slightly. You can then cap this off until needed. This is often done with a pre-made bonding plate.

Connection Method

The lug should allow for a reliable mechanical connection to the spa's EGC (typically a screw-type lug for a solid copper conductor).4.

Bonding Jumper (Optional but Recommended)

While not explicitly required, it's a good practice to have the concrete sub run a bonding jumper from the rebar/mesh to the UFER ground system. This provides an extra layer of grounding protection.

What to Communicate to the Concrete Sub

"We need to ensure this slab will be suitable for a future indoor spa installation, in accordance with NEC '23, 680.26(B)(2)." "The slab reinforcement (rebar or mesh) needs to be continuous throughout the spa area." "We need you to embed a listed bonding lug into the slab reinforcement, in this location [point to the spot]. The lug needs to be accessible after the pour, to allow us to connect the spa's equipment grounding conductor." "We'd also like you to run a bonding jumper from the rebar/mesh to the existing UFER ground, if possible."

During Inspection

Take pictures during the concrete pour showing the bonding lug attached to the rebar/mesh. When the spa is eventually installed, your electrical inspector will want to see the connection between the bonding lug in the slab and the spa's EGC.

In Summary:


While the UFER ground is a good starting point, it's not enough to satisfy the specific bonding requirements for an indoor spa. You
must* plan for a dedicated bonding connection to the slab reinforcement now, by embedding a suitable bonding lug during the concrete pour. Communicate clearly with your concrete sub to ensure they understand the requirements and can properly install the lug. Flag for review