Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Large box sizing help

User: nickelec, Location: US

Asked on: Monday, September 23, 2024 at 3:04 pm EDT
Answered on: Thursday, March 6, 2025 at 2:50 am EST

Question: Have an unusual set up. Were installing a 3000A service and having an issue sourcing a switch in time. Utility is ok with me installing a "pull box" with terminal blocks to accommodate until the switch comes inWe will be installing 8 sets of 4 inch pvc with 4 750 mcm conductors in each, i need to size a big enough pull box to house the conductors and terminal blocksAny help is greatly apricated

Okay, this is a unique temporary setup, but we can definitely figure out the pull box sizing based on the code requirements and physical constraints. Let's break down the calculations and considerations

Understanding the Requirements
NEC Article 314 (Outlet, Device, Pull and Junction Boxes; Conduit Bodies; Fittings; and Handhole Enclosures)

This is the governing article for sizing pull boxes. We'll focus on 314.28, which deals with conductors of size 4 AWG or larger.


Straight Pulls (314.28(A)(1))

The minimum length of the pull box in a straight pull situation is

8 times the trade diameter of the largest raceway
entering the box. Angle or U Pulls (314.28(A)(2))

The distance from the raceway entry point to the opposite wall must be at least

6 times the trade diameter of the largest raceway
, plus the sum of the diameters of all other raceways on the same wall and row.
Terminal Blocks

These add to the required space inside the box. We need to estimate their size and allow for conductor bending space leading to and from them.

Conductor Bending Radius

750 MCM conductors have a significant bending radius. You need to provide enough depth in the box to accommodate this bending without damaging the conductors.

Calculations
1. Raceway Diameter

4-inch PVC conduit has an outside diameter (OD) of approximately 4.5 inches. We will use 4 inches for the NEC calculation since it uses trade size.
2.


Straight Pull Calculation

If the conduits enter and exit the box on opposite sides in a straight line, the minimum length of the pull box is: 8 4 inches = 32 inches3.

Angle or U Pull Calculation

This is more likely given the 8 conduits entering and exiting. Let's assume all 8 conduits enter on one side and exit on the opposite side (a U-pull). Minimum distance from raceway entry to opposite wall: 6 (trade size of the largest raceway) + sum of the trade size of remaining raceways on same wall 6 4 inches + (7 4 inches) = 24 inches + 28 inches = 52 inches4.

Terminal Block Consideration

This is the trickiest part without knowing the exact terminal blocks. Let's make some assumptions and then you need to confirm with the actual hardware.

Arrangement

You will likely arrange the terminal blocks in two rows of 4 (or similar). This saves width and depth, but increases length.

Dimensions per Block

A large terminal block capable of handling 750 MCM will be substantial. Let's
estimate (and you MUST confirm this) a size of: Length: 6 inches Width: 4 inches Height: 8 inches (includes mounting hardware/insulators)

Overall Terminal Block Area

Two rows of 4 blocks would have a length of (4 blocks 6 inches/block) + space between blocks ≈ 28 inches (approximately). This could add to the length previously calculated above. Width: 4 inches per block + space between blocks ≈ 18-20 inches. Height: 8 inches5.

Bending Radius and Depth Calculation

NEC Table 312.6(B)(2) provides minimum bending space at terminals based on one wire per terminal. For a 750 MCM conductor, the minimum bending space is

12 inches
. Since you're using terminal blocks, this bending space must be factored into the depth of the pull box. If the conductors enter the box and immediately bend upwards to the terminal blocks, you'll need at least 12 inches of depth above the conduit entry point. If they are going to wrap around from the back of the box, or the sides, you will need to take that into account.

Pull Box Sizing Recommendations (Based on the Assumptions)



Length

At least 52 inches (based on the U pull) + the length of the terminal block array on each side of the conduits (28 inches) =

Approximately 80 inches minimum
. Width

At least 18-20 inches to accommodate the terminal blocks. The conduits also need space, and you need working room.

Minimum 36 inches wide is recommended
.
Depth

This is critical. 12 inches minimum to accommodate the bending radius, plus the height of the terminal block is 8 inches. So that is approximately

20 inches in depth
.

So, a pull box size of approximately 80" (Length) x 36" (Width) x 20" (Depth) would be a starting point based on these conservative estimates.Important Considerations and Next Steps


Confirm Terminal Block Dimensions

Absolutely critical. Get the exact dimensions of the terminal blocks you are using, including the mounting hardware.2.

Layout

Create a detailed layout of how the conduits will enter the box, where the terminal blocks will be positioned, and how the conductors will be routed. This is best done with a scaled drawing.3.

Conductor Support

The conductors will need support within the pull box to prevent strain on the terminal blocks. Consider using cable cleats or other approved methods. Consult with a qualified electrician or engineer to ensure proper design.4.

Working Clearance

Ensure you have adequate working clearance around the pull box as per NEC Article 110.5.

Local AHJ

Discuss this temporary setup and pull box sizing with your local Authority Having Jurisdiction (AHJ). They may have specific requirements or preferences.6.

Vendor Consultation

Work with a pull box manufacturer. They can help you select a standard size box that meets your needs and provide guidance on conductor support and other details.7.

Material

Ensure the pull box is NEMA rated for the environment. Also ensure the conductors are compatible with the terminal blocks.

Disclaimer:
I am an AI Chatbot. This information is for general guidance only and should not be considered a substitute for professional engineering or electrical design advice. The NEC is a complex document, and it is essential to consult with qualified professionals to ensure compliance with all applicable codes and regulations. You MUST work with a licensed electrician and engineer to ensure the design is safe and code-compliant. Good luck with your project! Flag for review

Previous Question Next Question