Topic: Load center lugs are too big

User: Hehehe, Location: Las Vegas NV

Asked on: Monday, September 23, 2024 at 8:10 pm EDT
Answered on: Thursday, March 6, 2025 at 2:51 am EST

Question: Hi all,I currently have a 4-space subpanel on the side of my house and need 6 spaces.So I went and bought the next size Siemens 8-space panel thinking everything would match.Turns out I the A,B,N lugs are rated for #4 - 2/0, unlike my smaller panel that supports #14.My feeder wire is only #10 and was compatible with the smaller 4-space panel.How can I attach the #10 feeder?Also, code apparently says more than 6 disconnects requires a main breaker?I’ll end up having 2x 2-pole, 1x tandem, and 1x regular. Is that 5? I don’t necessarily need a main right?This panel supports a back feed main breaker too, should I use that to get around the wire size requirement? Will any Siemens breaker work? I know about the hold down kit, but the compatibility stuff is confusing me.

Okay, you've got a few questions here, let's break them down one by one, addressing safety and code considerations along the way. Remember, electrical work is dangerous. If you are not comfortable and knowledgeable, hire a qualified electrician.1. Connecting #10 Feeder to Lugs Rated for #4 - 2/0

This is a common problem when upgrading panels. Here are the acceptable solutions, ranked in order of preference:

Use a Listed Reducer/Adapter

This is the best and safest method. Look for something specifically designed for this purpose. Search online for "wire reducer lug adapter #10 to #4" or similar. These will look like small adapters that clamp onto the #10 wire, and have a larger lug that fits into the panel's lug. Make sure they are
UL listed and rated for the voltage and current you're dealing with. Follow the manufacturer's instructions.

Pig-tail with the correct wire gauge

In this case, the pig tail would need to be rated for the same amperage as the circuit. For 30 amps (using #10 wire), you would use the lug rated for your desired amperage.

Important Notes Regarding Wire Size and Ampacity



#10 Copper Wire Ampacity

#10 copper wire is
typically rated for 30 amps (check your local code, this may vary and also depends on the insulation rating – THHN, THWN, etc.). Don't exceed this ampacity.

Circuit Breaker Size

Your circuit breaker protecting this subpanel must be sized appropriately for the #10 wire, meaning you should probably use a 30 amp breaker to avoid overloading the feeder.

2. Number of Disconnects and Main Breaker



"Six Handle Rule"

The NEC (National Electrical Code) generally allows up to six circuit breakers to serve as the main disconnect for a panel
unless the local jurisdiction has specifically changed it. Your breaker count: 2 x 2-pole breakers = 2 handles (Each 2-pole breaker counts as two disconnects because it simultaneously disconnects two circuits) 1 x Tandem breaker = 1 handle (Even though it controls two circuits) 1 x Regular breaker = 1 handle

Total: 4 handles
You are fine by code. When a Main Breaker is Recommended (Even if Not Required)

A main breaker is strongly recommended if: You want a single point of disconnect for the entire subpanel. This is useful for maintenance and emergencies. You want to limit the subpanel's load to a specific amperage. You are running a long feeder and want the added protection of a main breaker tripping before the main panel breaker.

3. Using a Backfed Main Breaker to Circumvent Wire Size Requirement



NO. Absolutely NOT.
This is dangerous and violates code. You cannot use a backfed breaker to make the lugs suitable for a smaller wire size. The lugs are rated for a range of wire sizes to handle the potential maximum current the panel is designed for. You cannot bypass this. Code Violation and Safety Hazard

The lugs and bus bars are designed to handle the heat and current associated with larger wires. Using a backfed breaker doesn't magically change that. You'll create a fire hazard.


Backfeeding is for Generators/Solar

Backfed breakers are intended to supply power into the panel from a generator or solar system, not to bypass wiring limitations.

4. Compatibility of Siemens Breakers and Hold Down Kit



Siemens Breaker Compatibility

You generally need to use Siemens breakers specifically designed for
that particular Siemens panel. Check the panel's label; it will list compatible breaker types. Different series of Siemens panels use different breakers. Don't assume they are all interchangeable.



Backfed Breaker Hold-Down Kit

The purpose of the hold-down kit is to prevent the backfed breaker from accidentally being removed from the bus bars while energized. This is a crucial safety feature. The hold-down kit must be compatible with both the breaker and the panel. Again, consult the panel's labeling and Siemens documentation. The purpose of the Hold Down Kit is to keep the backfeed breaker from being pulled out by vibrations (generators) or being pulled by well meaning people.

Here's a summary of the key points and recommendations



Prioritize Safety

Electrical work is dangerous. If you are not confident, hire a qualified electrician.


Use the Correct Lug Adapters

Get the correct UL-listed lug adapters to connect your #10 wire to the larger lugs in the panel.

Don't Exceed #10 Wire Ampacity

Protect the feeder wire with a properly sized breaker (likely 30A).


You Don't Need a Main Breaker (Based on Handle Count)

You have 4 handles. However, consider the convenience and added safety a main breaker provides.

Do NOT Use Backfed Breaker to Bypass Wire Size

This is dangerous and violates code.


Ensure Breaker and Hold-Down Kit Compatibility: Use Siemens breakers specifically designed for your panel, and use the correct hold-down kit if installing a backfed breaker.Before you proceed, consider the following questions for yourself: Why do you need the extra spaces in the subpanel? Is it just for a couple of extra circuits, or are you significantly increasing the load on this subpanel? Have you calculated the total load on the subpanel to ensure that the #10 feeder wire is sufficient? If you are exceeding 30 Amps, you will need to run a larger gauge wire between the main and sub panel.* Are you certain that the breaker protecting the #10 feeder in the main panel is properly sized?Good luck, and remember safety first! Flag for review

Previous Question Next Question