Topic: Summer vs Winter Demand

User: dvcraven052256, Location: St. Louis, missouri

Asked on: Tuesday, September 24, 2024 at 8:56 am EDT
Answered on: Thursday, March 6, 2025 at 2:51 am EST

Question: I am working on multifamily dwelling that has house loads. I am try to find a way to reduce some of the demand loading on my house panel. Is it possible to look at the summer and winter loads and take some diversity of the type of load.I thought the NEC had an section where I could take the largest of the two loads and ignore the other.Thanks,Dan Craven

You're on the right track. The NEC does allow for taking diversity and using the larger of summer or winter heating/cooling loads, but it's crucial to apply it correctly. You're thinking of NEC 220.87.Here's a breakdown of how it works and what you need to keep in mind

Understanding NEC 220.87 (Optional Method)
What it allows

This section provides an optional method for calculating the feeder and service load of a dwelling unit or multifamily dwelling where heating and air-conditioning are installed and operated simultaneously.


The key

The NEC recognizes that in most climates, the full heating load and full air-conditioning load don't occur simultaneously. Instead, you typically have one dominating the other.

The Calculation


Calculate the Summer Load

This includes the air-conditioning load (including any heat pumps in cooling mode)
plus all other general loads (lighting, receptacles, appliances, etc.).2.

Calculate the Winter Load

This includes the heating load (including any heat pumps in heating mode)
plus all other general loads (lighting, receptacles, appliances, etc.).3.

Compare the Two

Take the
larger of the two values (summer load or winter load). This is the demand load you use for sizing the service.

Important Considerations



General Loads Included in Both

This is crucial. You must include all the general lighting and receptacle loads, appliance loads (ranges, dishwashers, dryers, etc.), and any other fixed loads in both the summer and winter load calculations. You're only choosing between the heating and air conditioning loads, not omitting other loads entirely.

Heat Pumps

Heat pumps are tricky because they contribute to both heating and cooling. Make sure to factor in the heat pump load appropriately in
both calculations, based on whether it's in heating or cooling mode. Use the nameplate rating for each mode.

Electric Space Heating

For electric space heating, you generally use 100% of the connected load.

Air Conditioning

Similar to heating, you would use 100% of the air conditioning load as per nameplate.


Other Optional Calculations in Article 220

Review other sections in Article 220, as they may provide other load reduction opportunities that, when combined with 220.87, could provide more savings. Examples include demand factors for ranges, dryers, etc.

Local Amendments

Always check with your local building authority or inspector. Some jurisdictions may have amendments to the NEC that modify or restrict the use of 220.87.

Example (Simplified)

Let's say you have:
General Loads (lighting, receptacles, appliances): 100 amps Air Conditioning Load: 40 amps Electric Heating Load: 60 amps

Summer Load

100 amps (General) + 40 amps (A/C) = 140 amps

Winter Load

100 amps (General) + 60 amps (Heating) = 160 ampsIn this case, you would use the winter load of 160 amps for sizing the service, because it's larger.

Why it Helps

This method acknowledges the diversity in seasonal loads, potentially allowing you to use a smaller service entrance and panel, saving on cost and materials.

Critical Advice



Consult with a Qualified Electrical Engineer or Licensed Electrician

Load calculations can be complex, and it's crucial to ensure they are accurate and comply with all applicable codes. An engineer can help you with the load calculations and ensure the design is safe and reliable.


Document Your Calculations

Keep thorough records of all your load calculations and assumptions. This is important for inspections and future reference.

Verify Equipment Ratings

Double-check the nameplate ratings of all your equipment (heating, cooling, appliances) to ensure accurate load calculations.


Be Conservative:
When in doubt, it's always best to err on the side of caution and use a slightly larger service. Undersized services can lead to overloads, nuisance tripping, and potentially dangerous situations.By understanding and applying NEC 220.87 (along with other applicable sections of Article 220) correctly, you can often reduce the demand load on your house panel and optimize the electrical system design. Flag for review