User: MisterMoSparky, Location: WV
Asked on: Tuesday, September 24, 2024 at 10:41 am EDT
Answered on: Thursday, March 6, 2025 at 2:51 am EST
Question: Main Disconnect outside G-N bonded, 4-wire going into main panel, Main Panel has G-N bonded also. My customer called me out there to fix their landscape lights and one of their 600W Transformers had burned out. I recommended having their grounds and neutrals separated in the main panel. During a surge event, the over voltage that’s traveling along the ground and neutral bar in the main panel to eventually make it to the ground rod outside will slightly effect the low voltage electronics and lighting around the house over time. Is my thought process wrong?
You've identified a potentially hazardous situation and are thinking about the problem correctly, but there are nuances to your proposed solution. Let's break it down
Your Observations & Concerns:
Main Disconnect Outside, G-N Bonded
This is where your power company's service is separated into your feed.
4-Wire to Main Panel
Suggests you have two hots, a neutral, and a ground wire (equipment grounding conductor).
Main Panel, G-N Bonded
Here is where the issue is.
The Core Problem
You have a neutral-ground bond in both the main disconnect and the main panel. This creates a parallel path for neutral current. Instead of all neutral current flowing back to the utility transformer via the neutral conductor, some will flow back through the grounding conductors and the earth. This is a code violation (NEC 250.24(A)(5)) and can cause a few problems:
Stray Voltage
The current flowing through the grounding system can create small voltage differences between grounded objects. This can be problematic, especially with sensitive electronics.
Increased Risk of Shock
Under fault conditions, the current flowing through the ground can make grounded objects hazardous to touch.
Burned out transformers
This could be the reason the low voltage transformer burned out.
Your Hypothesis About Surge Events
While surges can contribute, the primary issue isn't surge events themselves. It's the constant presence of neutral current flowing through the ground system. Surge events will definitely exacerbate the problem. The parallel neutral path can act as an antenna, making the impact worse.
Your Proposed Solution (Separating G-N in the Main Panel)
This is the correct approach, but it needs to be done properly. Here's the procedure:1.
Remove the Neutral-Ground Bond in the Main Panel
Disconnect the bonding jumper/screw/strap that connects the neutral bar to the metal enclosure and grounding bus in the main panel.2.
Ensure the Main Disconnect Outside Still Has the G-N Bond
Do not remove the neutral-ground bond in the main disconnect. This is the only location the neutral and ground should be bonded. This is where the service is split into your panel feed.
Important Considerations
Verify Bonding at Service Disconnect
Ensure that the main disconnect outside is properly bonded. Check that the neutral conductor is bonded to the grounding electrode system (ground rods, water pipe, etc.) at this location.
Grounding Electrode System
Make sure the grounding electrode system is adequate. This typically involves ground rods, connections to a metal water pipe (supplemented with a ground rod if the water pipe is plastic), and/or a concrete-encased electrode (Ufer ground).
Voltage Drop
If the landscape lighting is a significant distance from the transformer or panel, voltage drop could also be contributing to the transformer failure. Check the wiring gauge and distance.
Surge Protection
Once the G-N separation issue is resolved, consider adding a whole-house surge protector to the main panel. Also, consider surge protection for the low-voltage landscape lighting transformer.
Professional Inspection
Highly recommend a licensed electrician perform a full inspection to ensure all wiring is up to code and safe. Don't just fix the G-N bond; have them check the entire system.
Why This Matters for Low-Voltage Lighting
Sensitive Electronics
Low-voltage lighting transformers and LED drivers are often sensitive to voltage fluctuations and noise. Neutral current flowing through the ground system can introduce noise and voltage fluctuations into the low-voltage circuit, shortening the lifespan of the transformer and/or lights.*
Shared Grounding
If the low-voltage lighting system is connected to the same grounding electrode system as the main electrical system, any voltage on the grounding system will affect the low-voltage system as well.
In summary, your thought process is generally correct. Resolving the double-bonded neutral is crucial for safety and reliability. It will address the root cause of the stray voltage issues that are likely contributing to the landscape lighting transformer failure. Don't forget the additional considerations to ensure a comprehensive fix.
Disclaimer: I am an AI chatbot and cannot provide electrical advice. Always consult a qualified and licensed electrician for any electrical work. Flag for review