Question: Lets say I wanted to tap a 1600A bus with a 500A fused disconnect within 25'.If I wanted to use 4 runs of 1/0 (3 CCCs in each). Would the EGC need to be 4/0 per conduit or 1/0 per conduit?Basically, does the rule where the EGC does not need to be larger than the feeder tap conductor reduce the EGC size when taking into account parallel runs or should I consider the feeder tap as the circular mils of 4x1/0 and that brings me back to 4/0 being the smallest size EGC?What if I chose to have all of the CCCs in one conduit, like 4 x 2/0 (derated at 70% is still okay at 546A). Would my EGC be a single 2/0 or 4/0?
Okay, let's break down the EGC sizing for these scenarios, addressing the key points in your questions and how the NEC applies.
Scenario 1: 4 Runs of 1/0 Copper (3 CCCs each) to a 500A Fused Disconnect (within 25 feet) Feeder Tap Rules
The fundamental principle here is that the tap conductors must be sized according to NEC 240.21(B) and 240.4(B). Assuming a 25-foot tap rule applies, you need to ensure the tap conductors have an ampacity: Not less than the calculated load [240.21(B)(1)(1)], AND Not less than the rating of the overcurrent device (500A) protecting the tap conductors at the disconnect [240.21(B)(1)(2)], AND Not exceed the ampacity of the feeder [240.21(B)(1)(3)].
Conductor Ampacity
You are proposing 4 runs of 1/0 copper. 1/0 copper THHN has an ampacity of 170A at 75 degrees C. 4 runs of 1/0 equates to 680A. This satisfies the second condition of the tap rule.
EGC Sizing in Parallel
NEC 250.122(F) is the crucial section for parallel conductors. It states the EGC in each raceway must be sized based on the overcurrent device protecting the circuit conductors in the raceway. Then, 250.122(B) tells us the size requirements. You have a 500A OCPD at the disconnect. Referring to Table 250.122, a 500A overcurrent device requires a 1/0 copper EGC. Now we must apply 250.122(F)(1) or (2).
(1) When parallel conductors are run in separate raceways or cables, the equipment grounding conductor shall be installed in each raceway or cable. This says you have to have an EGC in each raceway. (2) Where parallel conductors are run in the same raceway or cable, the equipment grounding conductor shall comply with all of the following
(a) Be of the type specified in 250.118 (b) The size shall be based on the total phase conductor size. (c) Where ground-fault protection of equipment is installed, the equipment grounding conductor shall be installed in the same raceway or cable with the circuit conductors. Therefore, because you are running 4 separate raceways, you need a 1/0 EGC in each.
Answer to your first question
You need a 1/0 EGC in each conduit. Even though the 1/0 is smaller than what is required for the feeder EGC (4/0) it is sufficient for the overcurrent protection on the conductors in each raceway.
Scenario 2: All CCCs in One Conduit (4 x 2/0 Copper, derated at 70%) Conductor Ampacity
2/0 copper THHN has an ampacity of 195A at 75 degrees C. 4 x 2/0 has an ampacity of 780A. Per NEC Table 310.16 note 5 (derating for more than 3 CCCs in a raceway), 4 conductors would be derated to 80%. 780 x 80% = 624A. Since you are at 624A (and per the 75 degree rating in 110.14(C)(1) can only use the 75C rating), it would be in your best interest to bump the 2/0 up to 3/0.
EGC Sizing
The CCCs are in the same conduit, therefore we use 250.122(F)(2). Per Table 250.122, your EGC is dependent on the size of the overcurrent protection device that protects the feeder. In this case, it is the 1600A main OCPD. Therefore, we need a 4/0 AWG EGC.
Answer to your second question
You need a 4/0 EGC because all CCCs are in the same conduit and that EGC must match the feeder size's requirements.
Important Considerations and Clarifications
Engineering Judgement
While the NEC provides minimum requirements, consult with a qualified electrical engineer to ensure the design meets all applicable codes and provides a safe and reliable installation.
Voltage Drop
Don't forget to calculate voltage drop. The length of the run can significantly impact the required conductor size.
Coordination Study
For systems of this size, a coordination study is essential to ensure proper selective coordination of overcurrent devices.
AIC Rating
Ensure that the components used (including the disconnect switch) have an adequate Ampere Interrupting Capacity (AIC) rating for the available fault current at that location.
Material
This assumes copper conductors. Aluminum conductors have different ampacities and EGC sizing requirements.
In summary: The key is to correctly apply the parallel conductor rules in NEC 250.122(F). When in separate raceways, the EGC is sized based on the protection of the conductors in that raceway. When in a single raceway, the EGC is sized based on the size of the feeder's OCPD. Always consult the most current NEC and local amendments with a licensed electrician and/or qualified electrical engineer. Flag for review