Question: Hello. There is an existing commercial building that is being fed from a pole mounted transformer. The overhead cabling is going directly over the building with a weather head and vertically penetrates from the roof to the main panel location with a 600AMP main breaker. The meter is on the outside of the building with wiring from the CT on the weather head i believe. I believe that is NEC compliant. Since it has a main breaker disconnect at the panel it enters overhead. Is that correct?In my area i typically see weatherhead to the meter location with a disconnect (exterior) and then it goes inside to a interior panel. Or underground to the meter or even underground to main panel inside with a disconnect. First seeing it directly going inside to building in my area. See attached picture.thank you
You're right to question this. Let's break down the code requirements and discuss the specific situation.
Key NEC Sections to Consider
NEC 230.6(3) Protection Against Physical Damage: Service-entrance conductors must be protected from physical damage. This is a critical consideration for overhead service conductors running across a roof. NEC 230.9 Clearance from Building Openings: Overhead service conductors must maintain specific clearances from windows, doors, porches, fire escapes, etc. Your picture doesn't show these in relation to the building. NEC 230.24(A) Above Roofs: Overhead service conductors must have a minimum clearance above roofs as specified in Table 230.24(A). This clearance varies based on voltage and roof slope. Typically, a fully insulated neutral-supported cable has less stringent clearances. NEC 230.43 Wiring Methods for Services: This section details acceptable wiring methods for service conductors. For overhead services, it commonly involves service-entrance cable (SE cable, like in your picture), or individual conductors in raceway (conduit). NEC 230.70 Location of Service Disconnecting Means: The service disconnecting means (your 600A breaker) must be readily accessible and located either inside or outside at a readily accessible location nearest the point of entrance of the service conductors. NEC 230.71 Maximum Number of Disconnects: This is important. In general, a building or other structure served shall be supplied by only one service. The service disconnecting means must consist of no more than six switches or sets of circuit breakers mounted in a single enclosure or in a group of separate enclosures at each location.
Analysis of the Scenario and the Photo
Main Breaker as Service Disconnect
Yes, a 600A main breaker located inside the building can serve as the service disconnecting means, provided it's located at a readily accessible location nearest the point of entry of the service conductors into the building, as per NEC 230.70. If the panel is immediately inside the wall where the conductors penetrate, this could be compliant. However, if you have to walk a significant distance inside the building from the point of entry to get to the breaker, it would not be compliant.2.
Overhead Run Across the Roof Concerns: THIS is where your biggest concerns lie. Simply having a main breaker inside doesn't automatically make the entire installation compliant. Physical Protection: The service-entrance cable running across the roof MUST be adequately protected from physical damage. Is the cable rated for direct sunlight (UV resistance)? What is the condition of the cable? Clearance Above Roof: The clearance above the roof must meet the requirements of NEC 230.24(A). This is a crucial safety factor. Low voltage lines only require 3 feet of clearance above the roof. Support: Is the cable adequately supported along the roof? NEC specifies how often service entrance cable must be secured.3. Meter Location and CTs: Your description suggests that the meter is located outside, and CTs (current transformers) are located at the weatherhead. This is a common configuration for services larger than 200A. The conductors from the CTs to the meter are considered part of the service.4. Local Practices vs. Code: You're right to note that this installation is different from what you typically see. Local utility requirements and preferences can influence installation practices. However, the NEC is the minimum safety standard.
Is it NEC Compliant?
Based solely on your description, it might be compliant if: The 600A breaker is immediately inside the building at the point of entry. The overhead conductors have the required clearance above the roof. The service-entrance cable is adequately protected from physical damage, including UV degradation. The cable is adequately supported.
However, several red flags are raised by the photo and your description.Recommendations
Inspect Carefully
Visually inspect the entire service entrance: Assess the condition of the cable running across the roof. Look for cracks, brittleness, or UV damage. Measure the clearance above the roof. Check for proper support of the cable. Verify the location of the 600A breaker relative to the point of entry. Ensure everything is properly weather-sealed.2.
Consult with a Licensed Electrical Contractor
The best course of action is to have a qualified and licensed electrical contractor evaluate the installation. They can assess code compliance, identify potential safety hazards, and recommend necessary upgrades.3.
Contact the Local Authority Having Jurisdiction (AHJ)
In your area, this might be the building inspector or electrical inspector. They can provide guidance on local interpretations of the NEC and any specific requirements in your area.
In summary, while the installation could be compliant in certain circumstances, there are significant concerns about the roof penetration, physical protection, and clearances that require a thorough on-site inspection by a qualified professional. Do not assume it's compliant without a professional assessment. Ignoring these issues could lead to safety hazards or code violations. Flag for review