Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Class I Div 2 Suitability and Exceptions Around General-Purpose Equipment /General-Purpose Enclosures

User: Kedward, Location: San Jose, CA

Asked on: Tuesday, September 24, 2024 at 4:11 pm EDT
Answered on: Thursday, March 6, 2025 at 2:52 am EST

Question: Hello,I've been working with designs in Class I Division 2 Group B areas for some time, and I've heard a myriad of conflicting information for component selection and requirements. I'm focusing on general-purpose equipment/enclosures.Let's say I have a random instrument as shown in this link: https://dwyer-inst.com/en/products/pressure/single-pressure/transmitters/series3200g.htmlIf I needed this device to be explosionproof, I think the installation is pretty straight-forward. However, since it's in a Class I Division 2 Group B area, explosionproof is not required. My past experience with this is that since the device is specifically using the Explosionproof protection technique however, I have to pretty much follow the explosionproof installation outlined in the code. Reviewing some of this and trying to understand General-Purpose Equipment and General-Purpose Enclosures lead me down a different path and I'm hoping I can know if I'm off-base or not.I start with 501.105(B)(3) and can confirm that the equipment does not have "make-and break or sliding contacts" by removing the mag switches for calibration. Now it's able to be used in a general-purpose enclosure. Then with 500.8(C)(6)(a) the equipment doesn't need to be marked for class, division, group, temperature class, or ambient temperature range.Now I wire up the components in the provision 501.10(B) with much more freedom because my enclosure is not required to be explosionproof.My concerns at this point is that I'm not interpreting 500.8(A) appropriately for suitability. I feel like with the mindset that this is a piece of general-purpose equipment that is still approved for it's purpose it can fall under 500.8(A)(1). I also feel like I'm not using a specific protection method listed in 500.7. Maybe it falls under nonincendive equipment, but that doesn't feel like an intentional design decision and I'm unsure if that satisfies the code or not. I compare this to things like RMC/IMC in 501.10(B)(1) or specific motors in 501.125(B)(3) which made me start questioning past rigidity I've experienced in Class I Division 2 areas.

You've touched on a very nuanced area of hazardous location electrical design, and your questions are valid. Let's break down your thinking process and address your concerns.

Your Reasoning: General Purpose Equipment and Enclosures in Class I, Div 2, Group B

Your interpretation of the NEC, starting with 501.105(B)(3) and progressing through 500.8(C)(6)(a), and 501.10(B) is generally correct in outlining a permissible path to use general-purpose equipment in a general-purpose enclosure in a Class I, Division 2, Group B environment. However, you need to carefully consider the implications and confirm it's suitable for your application.

Addressing your concerns



500.8(A) Suitability

This is the
most critical section you're wrestling with, and rightfully so. 500.8(A) states, "Equipment shall be acceptable only if of a type and design adequate for the ignition and flammability properties of the specific flammable gas, flammable liquid–produced vapor, or combustible dust that will be present, and for the environmental conditions." This is where engineering judgment and documentation are paramount.

Your Argument

You're arguing that since you've removed the make-and-break contact for calibration (the potential ignition source) and are confident that under normal and abnormal conditions the equipment won't create an ignition source, then it falls under 500.8(A)(1) as suitable for its intended use. This is where your argument needs strong support.



Weak Points

Your argument rests heavily on the assumption that
nothing else within the instrument can become an ignition source under any foreseeable normal or abnormal operating condition. Consider:

Component Failure

What happens if a component (resistor, capacitor, etc.) within the transmitter fails? Could it overheat and spark?

Overvoltage/Overcurrent

How robust is the input circuitry against voltage spikes or current surges?


Internal Arcing

Are there any other components inside the device (other than the removed switch) that could arc under fault conditions?

Temperature Rating

Can the device, even without sparking, exceed the auto-ignition temperature of the Group B gas in question (Hydrogen or manufactured gas)?


Specific application: While Group B is defined by Hydrogen (and manufactured gases), your specific application might be more susceptible to a different gas within that group.If any of these are plausible (even with very low probability), then a general-purpose enclosure might not be suitable under 500.8(A).

Strengthening Your Argument



Manufacturer Documentation

Does the manufacturer have any documentation that supports the use of the transmitter in a Division 2 environment, even without being specifically rated for it? This could be in the form of testing data, failure mode analysis, or statements about the design that make ignition unlikely.

Failure Mode Analysis

Perform (or have a qualified engineer perform) a detailed failure mode analysis on the transmitter, specifically looking for potential ignition sources.


Temperature Rise Testing

Under worst-case operating conditions, measure the surface temperature of the transmitter. Ensure it stays well below the auto-ignition temperature of the gases involved.

Third-Party Evaluation

Consider having a qualified third-party testing lab evaluate the transmitter for suitability in your specific application. This would add significant weight to your argument.


Engineering Stamp

Have an experienced Professional Engineer (PE) review your design and the associated documentation and stamp the drawings/calculations.

Using Protection Methods listed in 500.7

You are right, you are not intentionally using a listed protection method in 500.7 if you rely only on removing the switch.


Nonincendive Equipment

Although you're removing the switch, the remainder of the device needs to meet the definition of nonincendive for the intended use in Group B gases in order to qualify.

Other Protection Methods

While not necessarily applicable to the
device itself, consider if other system-level protection methods are relevant. For instance, if you were to include intrinsically safe barriers on the signal lines, you'd need to verify that this barrier is Group B rated in your area.

RMC/IMC in 501.10(B)(1) or specific motors in 501.125(B)(3)

These are examples of specific components or wiring methods that are permitted in Division 2. They don't automatically make a general-purpose enclosure acceptable. They are, instead, specifically allowed to be used in Division 2 wiring, or in specific conditions.

In Summary


Due Diligence is Key

Don't rely solely on the removal of the mag switches. Conduct a thorough hazard analysis that covers the instrument and installation to confirm suitability.2.

Documentation is Critical

Document everything. This includes the hazard analysis, temperature testing results, manufacturer documentation, and engineering review. This documentation is what will justify your design to inspectors and auditors.3.

Consider Alternatives

While your approach is theoretically possible, it is usually more cost-effective and less risky to use equipment specifically rated for Class I, Division 2, Group B. The additional cost often outweighs the engineering and documentation efforts required to justify a general-purpose solution. The labor involved is often enough to cause explosionproof or otherwise appropriately rated equipment to be preferred.4.

Consult with Experts

Talk to a qualified hazardous location electrical engineer, your insurance underwriter, and the Authority Having Jurisdiction (AHJ) (the inspector) before proceeding.5.

Cost Justification

Analyze your time spent and the time of others to determine if it would be more advantageous to use more appropriate equipment.

Recommendation:While using general-purpose equipment can be done under the right circumstances, it's often a high-risk, high-effort strategy. Unless you have a compelling reason to deviate from using properly rated equipment, it's almost always the safer and more practical approach. The cost of potentially incorrect installations far exceeds the cost of proper installations. Flag for review

Previous Question Next Question