User: charlie b, Location: Lockport, IL
Asked on: Tuesday, September 24, 2024 at 4:23 pm EDT
Answered on: Thursday, March 6, 2025 at 2:53 am EST
Question: MV service switchgear, with a main-tie-tie-main configuration. Utility connects to far left and to far right. Generators connect between the ties. Utility does not include neutral. Generators do. Only loads immediately downstream are step-down transformers (no neutral needed).How are the neutrals to be connected?Disconnect at generators and don't bring to service panel?Add neutral bar to service switchgear, connect generator neutrals there, and connect nothingbelse there?Something else?
Okay, this is a common and important question for MV service switchgear configurations, especially with generators and transformers involved. Here's a breakdown of the best practice for handling the neutrals in your described system and the rationale behind it
The Recommended Approach:
1. Generator Neutrals
Bring the generator neutrals individually into the MV switchgear.2.
Neutral Bus/Bar
Install a dedicated neutral bus (or bar) within the MV switchgear enclosure. This neutral bus should be appropriately sized for the generator neutral current it will carry.3.
Connect Generator Neutrals
Connect each generator neutral conductor securely to this dedicated neutral bus.4.
Isolate from Utility Ground
Crucially, DO NOT CONNECT this generator neutral bus to the utility ground. Keep it floating relative to the utility.5. Ground Fault Protection
Implement sensitive ground fault protection on the generator feeders. This is critical!6.
Transformer Connections
Because your downstream transformers are delta-wye and do not require a direct MV neutral connection, DO NOT connect any wires to the neutral bus other than the generator neutrals.
Why This Approach is Best (Explanation)
Avoiding Circulating Currents
The utility supply is ungrounded (no neutral). If you were to directly connect the generator neutrals (which are grounded) to the utility ground or to a common ground point, you'd create a parallel path for ground fault currents. This can lead to:
Circulating Harmonic Currents
Generators can produce harmonic currents. With a parallel neutral path, these currents can circulate between the utility ground and the generator neutral, potentially overloading the neutral conductors and causing voltage distortion.
Unnecessary Tripping
Ground faults downstream of the transformers could cause unexpected tripping of the generator breakers due to the circulating ground fault current.
Damage to Equipment
Excessive neutral currents can overheat conductors and damage equipment.
Generator Neutral Grounding Benefits
Having a dedicated neutral bus for the generators allows you to:
Provide a Path for Generator Ground Fault Currents
In the event of a ground fault within the generator or on the generator feeder, the current has a defined path back to the generator neutral. This allows the ground fault protection system to operate correctly and quickly isolate the fault.
Allows for High Resistance Grounding
The generator neutral ground can include a resistor, which is the most common approach for generators. With high resistance grounding, ground fault current is limited to a low value, but a path is provided back to the generator. This limits damage to the generators and power system from a ground fault, and allows the equipment to continue running briefly before an automatic transfer.
Allows for Ground Fault Protection
With a defined path for generator ground fault currents, ground fault protection equipment can isolate the faulted equipment, and prevent damage to the rest of the distribution system.
Transformer Requirements
Since your downstream transformers are connected to a delta on the MV side, they are only concerned with phase voltage and current, so don't require a MV neutral connection. The transformer will deal with its own neutral needs, and not affect the generator or utility neutral.
Safety
This configuration ensures that fault currents are properly managed and limited, enhancing the overall safety of the electrical system.
Important Considerations
Ground Fault Protection
Implement sensitive, directional ground fault protection on each generator feeder. This protection should be coordinated with the protection on the downstream transformers.
Generator Grounding Resistor (If Used)
If you choose to use a high-resistance grounding scheme on the generator neutrals (which is a common practice), make sure the resistor is properly sized to limit ground fault currents to a safe level. The resistor should be capable of handling continuous ground fault current.
Neutral Conductor Sizing
The neutral conductors from the generators to the neutral bus must be sized to carry the expected fault current or the maximum neutral current specified by the generator manufacturer.
Documentation
Thoroughly document this neutral grounding configuration in your electrical drawings and procedures. This is critical for future maintenance and troubleshooting.*
Coordination Study
A full coordination study is highly recommended to ensure that all protective devices (circuit breakers, relays, fuses) operate correctly and selectively.
In Summary:
Create a dedicated, isolated neutral bus within the MV switchgear to connect the generator neutrals. DO NOT connect this neutral bus to the utility ground. Implement sensitive ground fault protection on the generator feeders. This approach minimizes circulating currents, ensures proper fault current management, and enhances the overall safety and reliability of the electrical system. Flag for review