Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Current Limiting OCPD's

User: Grouch1980, Location: New York, NY

Asked on: Tuesday, September 24, 2024 at 5:08 pm EDT
Answered on: Thursday, March 6, 2025 at 2:53 am EST

Question: I understand that if it is decided to use current limiting fuses / circuit breakers to protect a downstream circuit breaker, that combination has to be series rated, due to the presence of dynamic impedance. If the downstream equipment is an appliance with passive impedance, then there is no need for the series rating, and you can freely use the current limiting OCPD.Is there any concern with a current limiting OCPD feeding a downstream control panel, or a downstream EV charging cabinet? Control panels and charging cabinets have integral fuses and circuit breakers. Is there any concern with dynamic impedance? Or can one specify a current limiting OCPD without worrying about any series ratings with the integral fuses / breakers in the control panel or charging cabinet.I'm asking since I have an available short circuit current at the line side terminals of several items that is higher than their SCCR ratings.

You've touched on a nuanced area of electrical protection. Let's break down the considerations for using current-limiting OCPDs upstream of control panels and EV charging cabinets

Understanding the Core Issue: Dynamic Impedance and Series Ratings
Dynamic Impedance

This is the crux of the series rating requirement. When a circuit breaker (or other active OCPD) trips under a fault, its impedance
changes drastically and rapidly as it attempts to interrupt the current. This dynamic impedance interaction between two breakers in series can lead to unexpected behavior, and potentially, both devices failing to clear the fault effectively. Series ratings are established through rigorous testing to ensure coordinated interruption and protection.

Passive Impedance

Passive impedance, like that of a simple load (resistor, capacitor, inductor), is static. It doesn't change dramatically during a fault event. This is why you correctly pointed out that current-limiting devices upstream of simple passive loads usually don't necessitate the same stringent series rating considerations.

Control Panels and EV Charging Cabinets: A Hybrid Case


Control panels and EV charging cabinets are not purely passive loads. They contain: Active Components

Circuit breakers, fuses, contactors, relays, and potentially electronic components (PLCs, monitors, etc.). These introduce the possibility of dynamic impedance, although less pronounced than with two main breakers in series.


Passive Components

Wiring, transformers (in some cases), resistors, capacitors.

The Concern: Coordination and SCCR


The primary concern is whether the combination of the upstream current-limiting OCPD and the downstream OCPDs within the panel or cabinet can withstand and interrupt a fault current up to the available short-circuit current (ASCC).Here's a breakdown of the critical issues:1. SCCR (Short-Circuit Current Rating) of the Downstream Equipment

This is paramount. You correctly identify that your ASCC exceeds the SCCR of some equipment. A current-limiting device can be used to reduce the prospective fault current to a level below the SCCR of the downstream equipment. However, it needs to be done correctly.2.

Series Rating (or Lack Thereof)

If the downstream equipment's SCCR is lower than the ASCC, you must use a current-limiting device and verify that the combination is adequately protected through series ratings. If you choose a current limiting OCPD and do NOT have a series rating with the downstream OCPD, then you are expecting the current limiting OCPD to limit the let through current to a value lower than the SCCR rating of the downstream equipment.3.

Coordination

Even if the ASCC is reduced below the downstream equipment's SCCR, consider coordination. Does the upstream current-limiting device trip before the downstream breaker/fuse in the panel/cabinet for common overload or fault conditions? Poor coordination can lead to unnecessary tripping of the upstream device.4.

Let-Through Current/Energy

Current-limiting devices don't just limit current; they also limit the energy (I2t) that passes through during a fault. Check the manufacturer's let-through current and energy curves for the current-limiting device and ensure that the downstream components (especially sensitive electronics) can withstand that level of energy.

Specific Considerations
Control Panels

Control panels often have branch circuit protection (fuses or breakers) for individual components. The concern is that if a fault occurs in a branch circuit, the downstream branch protection device within the control panel may not clear the fault before the upstream current-limiting device trips, causing a larger outage.


EV Charging Cabinets

EV charging cabinets contain breakers and other components. Some models incorporate complex control and monitoring systems. Again, SCCR and coordination are vital. EV chargers also have specific safety standards that might dictate how fault protection is implemented.

Recommendations
1. Consult Manufacturers

The most crucial step. Contact the manufacturers of the control panels and EV charging cabinets. Ask them: If they have tested specific series ratings with current-limiting devices. What are the recommended upstream OCPDs to achieve the desired SCCR and coordination? What are the let through current limitations of their product, for various available fault currents? Do they have any specific requirements or recommendations for fault protection?2.

Series Rating Tables

Look for series rating tables provided by breaker manufacturers. These tables list tested combinations of upstream and downstream breakers that meet specific SCCR requirements.3.

Engineering Analysis

If no readily available series ratings exist, consult a qualified electrical engineer to perform a detailed short-circuit study, coordination study, and let-through energy analysis. This analysis will determine if the proposed combination provides adequate protection.4.

Upstream Fuse Coordination

Fuses are typically the best approach to use in a series rating or coordination scenario, because their clearing time is much faster than a breaker.

In summary:
You cannot assume you can freely use a current-limiting device upstream of a control panel or EV charging cabinet without considering the downstream OCPDs. Series ratings are preferred, where available, particularly if the downstream equipment's SCCR is less than the ASCC. If no series rating is available, a thorough engineering analysis is essential to ensure that the combination meets the required protection levels. Consulting manufacturers and a qualified electrical engineer are highly recommended.It's generally safer and more reliable to design for a tested and listed series combination rather than relying on assumptions. Flag for review

Previous Question Next Question