Topic: NEC 208(F)

User: medinajuli, Location: Florida

Asked on: Tuesday, September 24, 2024 at 7:48 pm EDT
Answered on: Thursday, March 6, 2025 at 2:54 am EST

Question: Hi, I have been working on a project in a dwelling unit that has two condenser units of 60 amperes / 240V, and 1 electrical vehicle charger of 60 amperes - 240V-1PH located outside.I'm a little bit confused with the NEC article 208(F).150V and 50A?150V or 50A?Thanks!!!

Let's break down NEC 220.82 (F) and how it applies to your situation. You're on the right track thinking about this section.

NEC 220.82(F): Electric Vehicle Supply Equipment

This section addresses the load calculation for EV chargers in dwelling units when using the optional calculation method. It's important to understand the full context of Article 220 and specifically the optional calculation method. I strongly recommend reading the full section of the NEC if you have access to it.Here's the key point:> 220.82(F) Electric Vehicle Supply Equipment. Add the EVSE load to the total load, but only the larger of the two: (1) calculated load for EVSE or (2) 40% of the nameplate ampere rating(s) of EVSE.

Understanding the Application to Your Project1. Optional Calculation Method

The optional calculation method in Article 220 is used for calculating the service size for a dwelling unit. You would typically use this when you want a potentially smaller service size than the standard method would require. You must follow all the rules within the optional calculation method (220.82) if you choose to use it.
2.


Your Loads

You have the following loads relevant to 220.82(F): Two AC Condenser Units: 60A / 240V each One EV Charger: 60A / 240V3.

EV Charger Load Calculation
Nameplate Rating: The EV charger has a 60A nameplate rating. 40% of Nameplate Rating: 0.40 60A = 24ASo, for the optional calculation method, you would use the larger of the following: Calculated Load for EVSE (likely the full 60A, unless you have control equipment installed to limit demand) 40% of Nameplate Rating (24A)In your case, you would use the full 60A for the optional calculation method.

Addressing Your Original Question ("150V and 50A?" or "150V or 50A?")

I suspect you may have read information pertaining to older editions of the NEC. NEC 220.82(F) does
not include 150V or 50A verbiage in the most recent editions.

Important Considerations & Disclaimer



Local Amendments

Always check with your local Authority Having Jurisdiction (AHJ). They may have amendments to the NEC that affect your installation.

Safety

Electrical work can be dangerous. If you're not a qualified electrician, hire one.


Correct Edition

Make sure you are using the correct edition of the NEC as adopted by your local jurisdiction.*

Completeness

This is a simplified explanation and might not cover all nuances. A full load calculation involves many steps and other applicable NEC sections.

In Summary


NEC 220.82(F) is about calculating the load for EV chargers under the optional calculation method. You'll need to determine whether to use the standard method or the optional method.If you decide to use the optional method, you have to apply all of the requirements within that method. Flag for review