Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Service Disconnect Sizing

User: Aistobasbistoc9, Location: Texas

Asked on: Tuesday, September 24, 2024 at 10:54 pm EDT
Answered on: Thursday, March 6, 2025 at 2:54 am EST

Question: I've got 6 panels each serving a different tenant suite being fed from a single bussed gutter. There is a main fused 800A disconnect for the bussed gutter. Each panel load is calculated per NEC with continuous, lighting, etc. loads at 1.25 of the kVA, and non continuous, receptacle, etc. loads (receptacles under 10kVA to keep this example simple)at 1.00 of the kVA. Each panel load is calculated individually and then for the load summary are added together for a total of 780A. Does the fused disconnect need to be sized at 1.25*780 amps and upsized to a 1000A (closest to the resulting 975 amps), or will the 800A fused disconnect suffice?Please provide with all NEC reference where possible and I appreciate all the help.Thank you

Okay, let's break down this load calculation scenario and address the NEC requirements for sizing the main disconnect for your multi-tenant service. This is a common situation, and understanding the rules is crucial.

The Short Answer

In your specific scenario, assuming the individual tenant panel calculations are accurate and follow NEC guidelines, your 800A fused disconnect is likely sufficient,

provided that the 780A calculated load represents the
maximum demand on the bussed gutter and adheres to all applicable demand factors and diversity factors allowed by the NEC.
You do not automatically apply a 1.25 multiplier to the sum of all individual panel loads.

Explanation with NEC References

The core issue here revolves around the application of the 125% rule (often misconstrued), demand factors, and diversity. You're right to question whether a blanket 1.25 multiplier needs to be applied to the total calculated load of 780A. It likely does not.
1. Understanding the 125% Rule (Continuous Loads) NEC 215.3 states for feeders supplying continuous loads "Feeder conductors shall have an ampacity not less than 125 percent of the continuous load." NEC 215.2(A)(1) states for feeders supplying continuous loads "Feeders shall have sufficient ampacity to supply the load calculated in accordance with Article 220." NEC 215.2(A)(1) informs to refer back to article 220 for load calculation. NEC 220.18 clearly defines a continuous load as "A load where the maximum current is expected to continue for 3 hours or more." NEC 215.2(A)(1) states for feeders supplying continuous loads "Feeder conductors shall have an ampacity not less than 125 percent of the continuous load." NEC 240.4(B) states to protect conductors in accordance with the 125% rule in 215.
3.The 125% rule is primarily about the conductors and overcurrent protection for specific continuous loads. You've already applied this 125% factor correctly within each individual panel calculation. You've taken the continuous portion of each panel's load and multiplied it by 1.25. This fulfills the intent of the code for those loads. The code does not state anywhere that once the initial calculation of the panel loads are determined that all the added values must be multiplied by 1.25 for sizing of the main disconnect.
2. Diversity and Demand Factors (Crucial Concept) This is where things get interesting and where you can potentially avoid upsizing unnecessarily. NEC Article 220 is your main guide for load calculations. Read it thoroughly! NEC 220.3, 220.11, 220.12, 220.14, 220.15, 220.16, 220.17 and 220.42 cover the appropriate demand factors to be used for specific occupancies. The key question: Are all six tenant suites simultaneously drawing their maximum calculated load? Almost certainly not. There's inherent diversity in how tenants use their spaces. Demand factors allow you to account for this. NEC 220.60 Noncoincident Loads. This is very important in multi-tenant situations. "Where it is unlikely that two or more noncoincident loads will be in use simultaneously, it shall be permissible to consider only the largest load(s) that will be used at one time, in calculating the total load to be supplied." Example: If one tenant suite is primarily an office and another is a restaurant, their peak loads likely occur at different times of day. Tenant Load Diversity

The NEC allows for considering diversity in multi-tenant buildings.3.

Applying Demand Factors
Carefully review NEC Article 220 and the specific sections relevant to the types of tenancies you have. For example, if you have dwelling units, NEC 220.82, 220.83, and Table 220.84 provide guidance on demand factors for ranges, dryers, and entire dwelling unit loads. After applying applicable demand factors to individual tenant loads, then sum the resulting demand loads. This is the value you compare to the feeder/disconnect ampacity.4. Sizing the Disconnect NEC 220.4(A). "The feeder or service load shall be determined in accordance with Parts III, IV, or V of this article." NEC 220.5(A) "Ampere loads shall be calculated to at least the nearest ampere." NEC 240.6(A) "Standard ampere ratings for fuses and inverse time circuit breakers shall be considered the standard ratings listed in Table 240.6(A). NEC 240.4(B) "Conductor Overcurrent Protection. Conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.14, 310.15, and as permitted in 240.4(C) through (G). NEC 240.4(B) "If the overcurrent protection device rating is not marked, rated, or listed, the overcurrent protection shall be sized per 240.4(D)" After applying all appropriate demand factors and diversity, if the resulting load is less than or equal to 800A, your 800A disconnect is sufficient. If it is greater than 800A, you will need to upsize to the next standard size (e.g., 1000A).

Steps to Take1. Thorough Load Calculation Review

Double-check your individual tenant panel calculations to ensure you haven't missed any loads or underestimated anything.2.

Apply Demand Factors

Identify the appropriate demand factors for each type of tenant (office, retail, restaurant, etc.) using NEC Article 220. Apply these factors to the individual tenant loads.
3.


Consider Noncoincident Loads

Are there tenant loads that are unlikely to operate simultaneously (e.g., a heavy manufacturing process that only runs during certain hours)? Apply NEC 220.60 if applicable.
4.


Sum the Demand Loads

Add the individual tenant loads
after applying demand factors.5.

Compare to Disconnect Rating

Compare the resulting total demand load to the 800A rating of your disconnect. If the demand load is 800A or less, you are likely fine. If it is greater, you must upsize.

Important Considerations



Future Expansion

If you anticipate adding more tenants or increased loads in the future, it might be wise to upsize the disconnect now, even if not strictly required.

AHJ (Authority Having Jurisdiction)

Always consult with your local building department or electrical inspector. They have the final say and may have specific interpretations or requirements.


Documentation

Keep detailed documentation of your load calculations, including all demand factors used. This is essential for inspections and future reference.

Example Scenario

Let's say, after applying demand factors, the individual tenant loads become: Tenant 1: 150A Tenant 2: 100A Tenant 3: 120A Tenant 4: 110A Tenant 5: 90A Tenant 6: 80AThe total demand load is now 650A. In this case, the 800A disconnect would be sufficient.

Disclaimer:
Consult with a qualified and licensed electrical engineer for your specific project. This information is for educational purposes only. Adherence to the NEC and local codes is your responsibility. Flag for review

Previous Question Next Question