User: Mmares179, Location: Michigan
Asked on: Wednesday, September 25, 2024 at 7:49 am EDT
Answered on: Thursday, March 6, 2025 at 2:54 am EST
Question: Not sure how many people on here are familiar with National Time & Signal systems but I am at a loss on how to fix the issue I am having.I am getting a trouble on one of the NAC panels whenever the system is in alarm condition, system is normal otherwise. The NAC Panel is showing a short on one of the two output circuits. I originally thought it was one of the devices that was causing the issue, but could not locate any. I then removed the wires from the troubled circuit and fired the system again, the NAC circuit still showed up as having a short. I ordered a new panel thinking the issue was within the panel itself. I just finished swapping all the parts from within the panel and I am getting the same issue. Any thoughts?
Okay, this is a tricky situation and likely points to a grounding issue or a very subtle fault. Here's a systematic breakdown of things to consider and try, based on your description
Understanding the Problem
Short in Alarm Only
The key thing is that the short appears only when the system is in alarm. This means the higher voltage/current being applied during alarm is somehow triggering the fault, or that the system is more sensitive to it in the alarm state.
New Panel, Same Issue
Replacing the panel eliminates a hardware failure within the main unit. This is a significant step.
Circuit Isolation
Disconnecting field wiring and the fault persists points to a fault close to the panel itself.
Troubleshooting Steps
Here's a detailed approach. Go through these in order:1. Verify Basic Wiring at the Panel (Again!) Polarity
Double-check the polarity of the NAC wiring. Even a small reversal or a stray wire can cause issues. Ensure the wires are in the correct terminal block locations.
Wire Gauge
Confirm you are using the correct wire gauge.
Wire Security
Verify that the field wiring connections are secure and properly seated within their terminal blocks. Even a slightly loose connection can cause intermittent problems.
Visual Inspection
Closely inspect the wiring for any nicks, cuts, or damaged insulation, especially near the panel. These could be the source of a short when voltage is applied.
Grounding
Ensure that the panel's grounding wire is connected securely to a known good ground. This is crucial for proper operation and fault detection.2.
Investigate Ground Faults VERY Carefully The Most Likely Culprit
Because the problem occurs only during alarm, a ground fault is now your prime suspect. During normal operation, the voltage is low, and the fault might not be detectable. During alarm, the higher voltage allows current to flow to ground, triggering the short.
Use a Multimeter (Very Important)
With the system powered down and the NAC circuit disconnected
Measure the resistance between each NAC output wire (positive and negative) and ground (the panel chassis is a good ground point). You are looking for low resistance readings (close to 0 ohms), which would indicate a ground fault.
Check with the panel powered up AND in alarm
Carefully measure the AC voltage between each NAC output wire and ground. You should see close to 0v AC. If you see a substantial voltage (more than a few volts AC), you likely have a ground fault.
Ground Fault Location
If you find a ground fault, you'll need to isolate it. Since you've eliminated field devices, focus on the wiring close to the panel, the panel enclosure, and any conduit runs.3.
Inspect the End-of-Line Resistor (EOLR) Circuit Value of the EOLR
Confirm that you are using the correct value of end-of-line resistor for the NAC panel. The wrong value can sometimes cause strange behavior. The resistor should be factory matched to the panel.
Placement of the EOLR
The EOLR should be located at the very end of the circuit, past the last device. Verify its location.
EOLR Wiring
Ensure the EOLR is wired correctly and that its leads are not touching anything else.4.
Check All Jumpers and Dip Switches in the Panel (Again!) Correct Settings
Review the panel's manual and verify that all jumpers and dip switches are set correctly for your specific installation and device types. It's easy to overlook a setting.
Specifically, look for NAC output type. Some panels require you to specify whether the NAC output is a Class A or Class B circuit.5. Internal Wiring within the Panel Enclosure Carefully inspect all the internal wiring within the panel enclosure itself. Look for any wires that may be pinched, frayed, or rubbing against metal parts of the enclosure. Make sure any splices within the panel enclosure are properly insulated and secured.6. Power Supply Issues (Less Likely, but Possible) Voltage Fluctuations
Check the voltage of the power supply, both during normal and alarm conditions. A significant voltage drop during alarm could cause unexpected behavior.
Battery Test
Perform a battery test to ensure the batteries can supply the necessary current during an alarm. A weak battery can cause the system to act erratically.7.
Review the sequence of operations Review the sequence of operations within the panel to confirm that everything is firing as expected.
Important Considerations
Safety First
Always disconnect power to the system before working on any wiring.
Documentation
Refer to the manufacturer's documentation for the specific NAC panel you are using.
Professional Help
If you've exhausted all these steps and still can't find the problem, it's time to call a qualified fire alarm technician. They have specialized tools and experience to diagnose complex problems.*
False Alarms
Be aware that troubleshooting a fire alarm system can sometimes trigger false alarms. Notify the monitoring company and the fire department (if required by local regulations) before you begin testing.
In Summary:
The fact that the short only occurs during alarm points very strongly to a ground fault or a subtle wiring issue that only becomes apparent when the voltage is higher. Focus your efforts on finding a path to ground from the NAC circuit.Let me know what you find after going through these steps. I'm here to help you narrow it down further if needed. Good luck! Flag for review